[Nut-upsdev] new ups for database?

Peter Selinger selinger at mathstat.dal.ca
Sun Sep 24 04:16:20 UTC 2006


I just made a change to the newhidups driver, and there is a small
chance that it might help with your "Broken pipe" problem. Could you
update to the newest version ("svn up"), and try this again:

./newhidups -DD -u root -x generic -x vendorid=0001 auto

-- Peter

spamwhole at gmail.com wrote:
> 
> Sorry, I think I was trying to run before I could walk.  Here's the 
> requested output.  It looks a little on the short side... 
> 
> 
> # upsc belkin at localhost 
> 
> driver.name: newhidups
> driver.parameter.port: auto
> driver.parameter.vendorid: 0001
> driver.version: 2.1.0
> ups.mfr: MEC
> ups.model: MEC0002 
> 
> thanks 
> 
> Rob 
> 
> Peter Selinger writes: 
> 
> > Hi Rob, 
> > 
> > thanks for trying this. The patch I sent contained only a "stub"
> > driver. Its purpose is to see if you can read any of the device's
> > variables with upsc. Please post the output of "upsc
> > belkin at localhost".  It should list a number of variables whose names
> > start with the word "unmapped". 
> > 
> > Before this driver will be actually useful, we need to change the
> > names of these variables so that NUT can understand them. This is
> > particularly important for the status variables (online, on battery,
> > etc). Also, we should try and map a few instant commands - at minimum,
> > we need an instant command to kill the power.  
> > 
> > -- Peter 
> > 
> > 
> > spamwhole at gmail.com wrote:
> >> 
> >> Forgot to CC the list  
> >> 
> >> spamwhole at gmail.com writes:  
> >> 
> >> > Thanks for your help.  The program now works and connects as expected.  
> >> > 
> >> > Just one quick question though, upslog doesn't seem to have any output.  
> >> > Is this expected or should I have some details here?  
> >> > 
> >> > thanks  
> >> > 
> >> > Rob  
> >> > 
> >> > rmk bin # upslog -s belkin at localhost -l -
> >> > Network UPS Tools upslog 2.1.0
> >> > logging status of belkin at localhost to - (30s intervals)
> >> > 20060923 235602 NA NA NA [NA] NA NA
> >> > 20060923 235632 NA NA NA [NA] NA NA
> >> > 20060923 235702 NA NA NA [NA] NA NA  
> >> > 
> >> > 
> >> > Peter Selinger writes:  
> >> > 
> >> >> P.S. you may have to start the driver with "-a belkin" or "belkin"
> >> >> instead of "auto", or start the driver with "upsdrvctl", to make sure
> >> >> that the socket is named correctly. -- Peter  
> >> >> 
> >> >> spamwhole at gmail.com wrote:
> >> >>> 
> >> >>> Hi,   
> >> >>> 
> >> >>> I've checked all the permissions and they are all ok for root & nobody.  
> >> >>> I've even tried compiling it --with-user=root, but that doesn't make 
> >> >>> much different.  Running an strace on it doesn't bring up anything 
> >> >>> useful either.   
> >> >>> 
> >> >>> I've tried running it as root and using -u root. But I still get the 
> >> >>> same problem. I'm not sure if the 'Can't connect to UPS [belkin]' is the 
> >> >>> program trying to connect to a socket of some description, or if it's 
> >> >>> actually trying to connect to the UPS.   
> >> >>> 
> >> >>> thanks   
> >> >>> 
> >> >>> Rob   
> >> >>> 
> >> >>> rmk trunk # upsd -DD -u root
> >> >>> Network UPS Tools upsd 2.1.0
> >> >>> Can't connect to UPS [belkin] (belkin): No such file or directory
> >> >>> Synchronizing.................. giving up   
> >> >>> 
> >> >>> rmk trunk # strace upsd -DD -u root
> >> >>> munmap(0x2b0d2b273000, 4096)            = 0
> >> >>> socket(PF_FILE, SOCK_STREAM, 0)         = 5
> >> >>> connect(5, {sa_family=AF_FILE, path="newhidups"}, 110) = -1 ENOENT (No 
> >> >>> such file or directory)
> >> >>> close(5)                                = 0
> >> >>> write(2, "Can\'t connect to UPS [newhidups]"..., 72Can't connect to UPS 
> >> >>> [newhidups] (newhidups): No such file or directory   
> >> >>> 
> >> >>> 
> >> >>> Peter Selinger writes:   
> >> >>> 
> >> >>> > spamwhole at gmail.com wrote:
> >> >>> >> >> Hi,  >> >> Thanks for the very very quick patch. But, I can't seem 
> >> >>> to get things to >> work, unfortunately I'm not sure if the error is 
> >> >>> user induced ;-).  I get >> the following error:  >> >> ups # upsd
> >> >>> >> Network UPS Tools upsd 2.1.0
> >> >>> >> /var/state/ups is world readable
> >> >>> >> /usr/local/ups/etc/upsd.conf is world readable
> >> >>> >> Can't connect to UPS [belkin] (belkin): No such file or directory
> >> >>> >> /usr/local/ups/etc/upsd.users is world readable
> >> >>> >> Synchronizing.................. giving up > > This is probably a 
> >> >>> permissions problem. Try running upsd with "-u
> >> >>> > root".  > > Also make sure that upsd and newhidups are from the same 
> >> >>> NUT version.  > >> Here's my ups.conf:  >> >> [belkin]
> >> >>> >> port = /dev/usb/hiddev0             I've tried auto
> >> >>> >> driver = newhidups
> >> >>> >> vendorid = 0001 > > The "port" value is ignored; it can be any 
> >> >>> non-empty string. > >> Here's an strace of 'upsd':  >> >> [snip] >> >> 
> >> >>> Also, as a side note the make fell over when building the driver.  There 
> >> >>> was >> a normal 'gcc' line but with no source code to compile.  When I 
> >> >>> added >> mec-hid.c I I was able to continue/finish the compile. > > You 
> >> >>> could have also done "make depend" in drivers/. > > -- Peter > >> thanks 
> >> >>> >> >> Rob  >> >> >> Peter Selinger writes:  >> >> > Thanks for the info. 
> >> >>> Attached is the patch for an MEC subdriver stub.
> >> >>> >> > Plesae see if you can get this to work and read any info from the
> >> >>> >> > device via "upsd" and "upsc". Thanks, -- Peter >> > >> > 
> >> >>> spamwhole at gmail.com wrote:
> >> >>> >> >> >> >> Peter,  >> >> >> >> Please see below.  I've left the extra 
> >> >>> USB devices in there too, just in >> >> case.  >> >> >> >> thanks  >> >> 
> >> >>> >> >> Rob  >> >> >> >> rmk drivers # ./newhidups -DD -u root -x generic 
> >> >>> -x vendorid=0001 auto
> >> >>> >> >> Network UPS Tools: 0.28 USB communication driver 0.28 - core 0.30 
> >> >>> (2.1.0)  >> >> >> >> debug level is '2'
> >> >>> >> >> Checking device (0000/0000) (003/001)
> >> >>> >> >>  - VendorID: 0000
> >> >>> >> >>  - ProductID: 0000
> >> >>> >> >>  - Manufacturer: Linux 2.6.18-1 ohci_hcd
> >> >>> >> >>  - Product: OHCI Host Controller
> >> >>> >> >>  - Serial Number: 0000:00:02.0
> >> >>> >> >>  - Bus: 003
> >> >>> >> >> Trying to match device
> >> >>> >> >> Device does not match - skipping
> >> >>> >> >> Checking device (14AA/022B) (002/011)
> >> >>> >> >>  - VendorID: 14aa
> >> >>> >> >>  - ProductID: 022b
> >> >>> >> >>  - Manufacturer: Digital TV Receiver
> >> >>> >> >>  - Product: Digital TV Receiver
> >> >>> >> >>  - Serial Number: unknown
> >> >>> >> >>  - Bus: 002
> >> >>> >> >> Trying to match device
> >> >>> >> >> Device does not match - skipping
> >> >>> >> >> Checking device (0000/0000) (002/001)
> >> >>> >> >>  - VendorID: 0000
> >> >>> >> >>  - ProductID: 0000
> >> >>> >> >>  - Manufacturer: Linux 2.6.18-1 ehci_hcd
> >> >>> >> >>  - Product: EHCI Host Controller
> >> >>> >> >>  - Serial Number: 0000:05:06.2
> >> >>> >> >>  - Bus: 002
> >> >>> >> >> Trying to match device
> >> >>> >> >> Device does not match - skipping
> >> >>> >> >> Checking device (0000/0000) (004/001)
> >> >>> >> >>  - VendorID: 0000
> >> >>> >> >>  - ProductID: 0000
> >> >>> >> >>  - Manufacturer: Linux 2.6.18-1 uhci_hcd
> >> >>> >> >>  - Product: UHCI Host Controller
> >> >>> >> >>  - Serial Number: 0000:05:06.0
> >> >>> >> >>  - Bus: 004
> >> >>> >> >> Trying to match device
> >> >>> >> >> Device does not match - skipping
> >> >>> >> >> Checking device (0D3D/0001) (004/002)
> >> >>> >> >>  - VendorID: 0d3d
> >> >>> >> >>  - ProductID: 0001
> >> >>> >> >>  - Manufacturer: unknown
> >> >>> >> >>  - Product: USBPS2
> >> >>> >> >>  - Serial Number: unknown
> >> >>> >> >>  - Bus: 004
> >> >>> >> >> Trying to match device
> >> >>> >> >> Device does not match - skipping
> >> >>> >> >> Checking device (0000/0000) (001/001)
> >> >>> >> >>  - VendorID: 0000
> >> >>> >> >>  - ProductID: 0000
> >> >>> >> >>  - Manufacturer: Linux 2.6.18-1 ehci_hcd
> >> >>> >> >>  - Product: EHCI Host Controller
> >> >>> >> >>  - Serial Number: 0000:00:02.1
> >> >>> >> >>  - Bus: 001
> >> >>> >> >> Trying to match device
> >> >>> >> >> Device does not match - skipping
> >> >>> >> >> Checking device (0001/0000) (005/004)
> >> >>> >> >>  - VendorID: 0001
> >> >>> >> >>  - ProductID: 0000
> >> >>> >> >>  - Manufacturer: MEC
> >> >>> >> >>  - Product: MEC0002
> >> >>> >> >>  - Serial Number: unknown
> >> >>> >> >>  - Bus: 005
> >> >>> >> >> Trying to match device
> >> >>> >> >> Device matches
> >> >>> >> >> failed to claim USB device, trying 2 more time(s)...
> >> >>> >> >> detaching kernel driver from USB device...
> >> >>> >> >> trying again to claim USB device...
> >> >>> >> >> HID descriptor retrieved (Reportlen = 624)
> >> >>> >> >> Report descriptor retrieved (Reportlen = 624)
> >> >>> >> >> Found HID device
> >> >>> >> >> Report Descriptor size = 624
> >> >>> >> >> Detected a UPS: MEC/MEC0002
> >> >>> >> >> Using subdriver: GENERIC HID 0.1
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.FlowID, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.ConfigVoltage, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.ConfigFrequency, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.LowVoltageTransfer, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.HighVoltageTransfer, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.iManufacturer, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.iProduct, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.iSerialNumber, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.FlowID, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.ConfigVoltage, Type: Feature
> >> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.ConfigFrequency, Type: Feature
> >> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.ConfigApparentPower, Type: Feature
> >> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.ConfigActivePower, Type: Feature
> >> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.DelayBeforeStartup, Type: Feature
> >> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.Flow.DelayBeforeShutdown, Type: Feature
> >> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.BatterySystem.BatterySystemID, Type: Feature
> >> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.BatterySystem.PresentStatus.Used, Type: Feature
> >> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.BatterySystem.PresentStatus.Good, Type: Feature
> >> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.BatterySystem.Voltage, Type: Feature
> >> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.BatterySystem.Temperature, Type: Feature
> >> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.BatterySystem.Test, Type: Input
> >> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >> >>> >> >> Path: 00860004.BatterySystem.Test, Type: Feature
> >> >>> >> >> Can't find object 00860004.PowerConverter.PowerConverterID
> >> >>> >> >> Path: 00860004.PowerConverter.PowerConverterID, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Input.InputID
> >> >>> >> >> Path: 00860004.PowerConverter.Input.InputID, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Input.FlowID
> >> >>> >> >> Path: 00860004.PowerConverter.Input.FlowID, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Input.PresentStatus.Good
> >> >>> >> >> Path: 00860004.PowerConverter.Input.PresentStatus.Good, Type: 
> >> >>> Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Input.Voltage
> >> >>> >> >> Path: 00860004.PowerConverter.Input.Voltage, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Input.Frequency
> >> >>> >> >> Path: 00860004.PowerConverter.Input.Frequency, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Output.OutputID
> >> >>> >> >> Path: 00860004.PowerConverter.Output.OutputID, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Output.FlowID
> >> >>> >> >> Path: 00860004.PowerConverter.Output.FlowID, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Output.Voltage
> >> >>> >> >> Path: 00860004.PowerConverter.Output.Voltage, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Output.Frequency
> >> >>> >> >> Path: 00860004.PowerConverter.Output.Frequency, Type: Input
> >> >>> >> >> Can't find object 00860004.PowerConverter.Output.PercentLoad
> >> >>> >> >> Path: 00860004.PowerConverter.Output.PercentLoad, Type: Input
> >> >>> >> >> Can't find object 
> >> >>> 00860004.PowerConverter.Output.PresentStatus.Overload
> >> >>> >> >> Path: 00860004.PowerConverter.Output.PresentStatus.Overload, Type: 
> >> >>> Input
> >> >>> >> >> Can't find object 
> >> >>> 00860004.PowerConverter.Output.PresentStatus.Boost
> >> >>> >> >> Path: 00860004.PowerConverter.Output.PresentStatus.Boost, Type: 
> >> >>> Input
> >> >>> >> >> Can't find object 
> >> >>> 00860004.PowerConverter.Output.PresentStatus.Buck
> >> >>> >> >> Path: 00860004.PowerConverter.Output.PresentStatus.Buck, Type: 
> >> >>> Input
> >> >>> >> >> upsdrv_updateinfo...
> >> >>> >> >> dstate_init: sock /var/state/ups/newhidups-auto open on fd 5
> >> >>> >> >> upsdrv_updateinfo...
> >> >>> >> >> Waiting for notifications...
> >> >>> >> >> upsdrv_updateinfo...
> >> >>> >> >> Waiting for notifications...
> >> >>> >> >> Signal 2: exiting
> >> >>> >> >> Closing device
> >> >>> >> >> rmk drivers #  >> >> >> >> >> >> Peter Selinger writes:  >> >> >> 
> >> >>> >> > Rob and Dave, >> >> > >> >> > that device looks like it is using an 
> >> >>> illegal vendor id, "0001". It
> >> >>> >> >> > also looks like it is made by MEC, not Belkin (probably sold 
> >> >>> under
> >> >>> >> >> > license).  >> >> > >> >> > We might be able to support its USB 
> >> >>> interface. To find out more,
> >> >>> >> >> > please do the following: >> >> > >> >> > * get the latest 
> >> >>> development version of NUT from SVN. You can follow
> >> >>> >> >> >   the instructions at http://www.networkupstools.org/source.html 
> >> >>> under
> >> >>> >> >> >   "Development tree" to get it. >> >> > >> >> > * post the 
> >> >>> output of >> >> > >> >> >    drivers/newhidups -DD -u root -x generic -x 
> >> >>> vendorid=0001 auto >> >> > >> >> >   from this newest NUT version. >> >> 
> >> >>> > >> >> > This should output a bunch of debugging data, and then go into 
> >> >>> an
> >> >>> >> >> > infinite loop waiting for data. You can do "Ctrl-C" to kill the 
> >> >>> driver
> >> >>> >> >> > (it will not do anything useful at this point). >> >> > >> >> > 
> >> >>> -- Peter >> >> > >> >> > spamwhole at gmail.com wrote:
> >> >>> >> >> >> >> >> >> Hi,  >> >> >> >> >> >> I have the same device, a 
> >> >>> F6H500ukUNV, it has both RS-232 and USB.  >> >> >> >> >> >> url:
> >> >>> >> >> >> 
> >> >>> http://catalog.belkin.com/IWCatProductPage.process?Product_Id=201050  >> 
> >> >>> >> >> >> >> >> >> >> >> The details I have from my system are below.  If 
> >> >>> you would like further >> >> >> informatinon, or a more verbose lsusb 
> >> >>> please let me know.  >> >> >> >> >> >> thanks  >> >> >> >> >> >> Rob  >> 
> >> >>> >> >> >> >> >> dmesg:
> >> >>> >> >> >> hiddev96: USB HID v1.00 Device [MEC MEC0002] on 
> >> >>> usb-0000:05:06.1-2  >> >> >> >> >> >> lsusb:
> >> >>> >> >> >> Bus 005 Device 004: ID 0001:0000 Fry's Electronics  >> >> >> >> 
> >> >>> >> >> cat /proc/bus/usb/device:
> >> >>> >> >> >> T:  Bus=05 Lev=01 Prnt=01 Port=01 Cnt=01 Dev#=  4 Spd=1.5 MxCh= 
> >> >>> 0
> >> >>> >> >> >> D:  Ver= 1.00 Cls=00(>ifc ) Sub=00 Prot=00 MxPS= 8 #Cfgs=  1
> >> >>> >> >> >> P:  Vendor=0001 ProdID=0000 Rev= 1.00
> >> >>> >> >> >> S:  Manufacturer=MEC
> >> >>> >> >> >> S:  Product=MEC0002
> >> >>> >> >> >> C:* #Ifs= 1 Cfg#= 1 Atr=80 MxPwr=100mA
> >> >>> >> >> >> I:  If#= 0 Alt= 0 #EPs= 1 Cls=03(HID  ) Sub=00 Prot=00 
> >> >>> Driver=usbhid
> >> >>> >> >> >> E:  Ad=81(I) Atr=03(Int.) MxPS=   8 Ivl=10ms  >> >> >> >> >> >> 
> >> >>> >
> >> >>> >> >> >> >Hi Dave, >> >> >> >
> >> >>> >> >> >> >nothing in the outputs you sent looks like any Belkin device 
> >> >>> is
> >> >>> >> >> >> >present. Are you sure it is attached to your computer? You 
> >> >>> should have
> >> >>> >> >> >> >something like this in /proc/bus/usb/devices: >> >> >> >
> >> >>> >> >> >> >T:  Bus=04 Lev=01 Prnt=01 Port=00 Cnt=01 Dev#=  3 Spd=1.5 
> >> >>> MxCh= 0
> >> >>> >> >> >> >D:  Ver= 1.10 Cls=00(>ifc ) Sub=00 Prot=00 MxPS= 8 #Cfgs=  1
> >> >>> >> >> >> >P:  Vendor=050d ProdID=0980 Rev= 0.06
> >> >>> >> >> >> >S:  Manufacturer=       >> >> >> >S:  Product=UPS
> >> >>> >> >> >> >C:* #Ifs= 1 Cfg#= 1 Atr=c0 MxPwr= 20mA
> >> >>> >> >> >> >I:  If#= 0 Alt= 0 #EPs= 1 Cls=03(HID  ) Sub=00 Prot=00 
> >> >>> Driver=usbhid
> >> >>> >> >> >> >E:  Ad=81(I) Atr=03(Int.) MxPS=   8 Ivl=248ms >> >> >> >
> >> >>> >> >> >> >Note "Vendor=050d", which is Belkin's vendor ID.  >> >> >> >
> >> >>> >> >> >> >The output from newhidups does not show a 050d/XXXX device 
> >> >>> either.  >> >> >> >
> >> >>> >> >> >> >-- Peter >> >> >> >
> >> >>> >> >> >> >meherenow at darkglobe.org wrote:
> >> >>> >> >> >> >> >> >> >> >> I have a Belkin F6H500ukUNV ups that I am 
> >> >>> attempting to get working =20
> >> >>> >> >> >> >> under nut, however it
> >> >>> >> >> >> >> does not appear to be detected by nut, I'm assuming that I 
> >> >>> need to =20
> >> >>> >> >> >> >> feed some information
> >> >>> >> >> >> >> back to you guys to get it included in the database 
> >> >>> somwhere. >> >> >> >> >> >> >> >> I've included (what I can think might 
> >> >>> be) the relivant outputs. Please >=20
> >> >>> >> >> >> >> let me know if you
> >> >>> >> >> >> >> require anything else. >> >> >> >> >> >> >> >> dmesg output
> >> >>> >> >> >> >> /sbin/newhidsups output
> >> >>> >> >> >> >> ll /dev/usb*
> >> >>> >> >> >> >> cat /proc/bus/usb/devices >> >> >> >> >> >> >> >> p.s. I 
> >> >>> tried chmodding /dev/usb<blah> 777 just incase it was a =20
> >> >>> >> >> >> >> permissions problem, but
> >> >>> >> >> >> >> that didn't help either. >> >> >> >> >> >> >> >> Many 
> >> >>> thanks. >> >> >> >> >> >> >> >> 
> >> >>> ###########################################################
> >> >>> >> >> >> >> dmesg output when connecting the ups >> >> >> >> >> >> >> >> 
> >> >>> usb 2-1: new low speed USB device using uhci_hcd and address 2
> >> >>> >> >> >> >> PM: Adding info for usb:2-1
> >> >>> >> >> >> >> PM: Adding info for No Bus:usbdev2.2_ep00
> >> >>> >> >> >> >> usb 2-1: configuration #1 chosen from 1 choice
> >> >>> >> >> >> >> PM: Adding info for usb:2-1:1.0
> >> >>> >> >> >> >> hiddev96: USB HID v1.00 Device [MEC MEC0002] on 
> >> >>> usb-0000:00:10.1-1
> >> >>> >> >> >> >> PM: Adding info for No Bus:usbdev2.2_ep81 >> >> >> >> >> >> 
> >> >>> _______________________________________________
> >> >>> >> >> >> Nut-upsdev mailing list
> >> >>> >> >> >> Nut-upsdev at lists.alioth.debian.org
> >> >>> >> >> >> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev >> 
> >> >>> >> >> >> >> >  >> >> >> >  >> >   
> >> >>> 
> >> >>  
> >> 
> >> _______________________________________________
> >> Nut-upsdev mailing list
> >> Nut-upsdev at lists.alioth.debian.org
> >> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev 
> >> 
> > 
> 




More information about the Nut-upsdev mailing list