[Nut-upsdev] snmp-ups shutdowns

Tim Rice tim at multitalents.net
Sat Mar 1 00:45:09 UTC 2014


On Thu, 27 Feb 2014, Charles Lepple wrote:

| On Feb 27, 2014, at 9:43 AM, Jim Klimov wrote:
| 
| >>>>> # turn off UP gracefully (APC) (stays off even if power is restored)
| >>>>> #UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.1.0 integer 3"
| >> 
| >> This should map to the "shutdown.stayoff" instant command.
| > 
| > And this means that the current code in the repository would not work
| > as expected, without fixing the above discrepancies first? Right?
| 
| I wasn't very clear there: .1.3.6.1.4.1.318.1.1.1.6.2.1.0 *does* currently map to "shutdown.stayoff".
| 
| (We should probably fix the other OID to map to "shutdown.return", if that is indeed what it does.)

I you are refering to
	# reboot gracefully (APC) (stays off until utility power is restored)
	MT_UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.2.0 integer 3"
I have tested it and id does what it says.

Latest (i think) APC mib here.
ftp://ftp.apc.com/apc/public/software/pnetmib/mib/409/powernet409.mib


-- 
Tim Rice				Multitalents	(707) 456-1146
tim at multitalents.net