d tbsky tbskyd at gmail.com
Wed Sep 13 14:26:16 BST 2023


jim Klimov <jimklimov+nut at gmail.com>
>
> Hello all,
>
>   Had another hard look at the PR for QX device voltage/charge/runtime fixes for some broken use-cases (AND hoping to not introduce problems for cases that were not broken), and hopefully found and rolled back the change which in fact introduced the strangeness found in our winter round of tests. Then the year was busy...
>
>   As before, the context for this is:
> * issue https://github.com/networkupstools/nut/issues/1279
> * PR https://github.com/networkupstools/nut/pull/1652
> * PR source git branch (code to build for tests) https://github.com/jimklimov/nut/tree/issue-1279
> * https://github.com/networkupstools/nut/wiki/Building-NUT-for-in%E2%80%90place-upgrades-or-non%E2%80%90disruptive-tests suggests how to quickly build and

Hi:
   one of our voltronic ups caught fire last year. so we abandoned
them and bought APC.  now I have only one 10KV ups to test. It's sad
because I like nutdrv_qx driver. APC microlink is too bad since nut
doesn't support it. there is only modbus with apcupsd driver.

   BTW I saw an APC ups discussion at nut-upsdev about "SRVS1KI"(can
not reply, not subscribed to that list) . I have that easy-ups series.
nut can support them well with apcsmart driver. normally we should
attach it via serial cable. if you attach the ups with usb cable, you
will see "XR21V1410" which is a usb-serial converter. linux kernel
5.15 seems include the driver. or you will need to compile the
driver(xr_usb_serial_common) yourself and get "/dev/ttyXRUSB0" to use
as an serial port. I do that because we lost serial cable at a remote
site and forced to use the usb cable.

> ./nutdrv_qx -a ftups -u root -DDDDDD -d1
Network UPS Tools - Generic Q* USB/Serial driver 0.35 (2.8.0-2359-g6c0032e52)
USB communication driver (libusb 1.0) 0.45
   0.000000     [D1] Network UPS Tools version 2.8.0-2359-g6c0032e52
(release/snapshot of 2.8.0.1) built with gcc (GCC) 11.3.1 20221121
(Red Hat 11.3.1-4) and configured with flags: --enable-Wcolor
--enable-keep_nut_report_featu
re --with-all=auto --with-cgi=auto
--with-serial=auto --with-dev=auto --with-doc=skip
--with-nut_monitor=auto --with-pynut=auto
--disable-force-nut-version-header --enable-check-NIT
--enable-maintainer-mode
   0.000011     [D1] debug level is '6'
   0.000014     [D5] send_to_all: SETINFO driver.debug "6"
   0.000018     [D5] send_to_all: SETFLAGS driver.debug RW NUMBER
   0.000815     [D1] Succeeded to become_user(root): now UID=0 GID=0
   0.000822     [D5] send_to_all: SETINFO device.type "ups"
   0.000825     [D5] send_to_all: SETINFO driver.state "init.device"
   0.000827     [D1] upsdrv_initups...
   0.003147     [D2] Checking device 1 of 11 (8087/8000)
   0.057855     [D2] - VendorID: 8087
   0.057861     [D2] - ProductID: 8000
   0.057862     [D2] - Manufacturer: unknown
   0.057864     [D2] - Product: unknown
   0.057865     [D2] - Serial Number: unknown
   0.057867     [D2] - Bus: 002
   0.057868     [D2] - Device: 002
   0.057870     [D2] - Device release number: 0005
   0.057873     [D2] Trying to match device
   0.057875     [D3] match_function_regex: matching a device...
   0.057888     [D2] Device does not match - skipping
   0.071830     [D2] Checking device 2 of 11 (1D6B/0002)
   0.078881     [D2] - VendorID: 1d6b
   0.078885     [D2] - ProductID: 0002
   0.078887     [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64 ehci_hcd
   0.078888     [D2] - Product: EHCI Host Controller
   0.078890     [D2] - Serial Number: 0000:00:1d.0
   0.078891     [D2] - Bus: 002
   0.078893     [D2] - Device: 001
   0.078894     [D2] - Device release number: 0514
   0.078897     [D2] Trying to match device
   0.078898     [D3] match_function_regex: matching a device...
   0.078912     [D2] Device does not match - skipping
   0.091359     [D2] Checking device 3 of 11 (8087/8008)
   0.145626     [D2] - VendorID: 8087
   0.145635     [D2] - ProductID: 8008
   0.145637     [D2] - Manufacturer: unknown
   0.145638     [D2] - Product: unknown
   0.145640     [D2] - Serial Number: unknown
   0.145641     [D2] - Bus: 001
   0.145643     [D2] - Device: 002
   0.145645     [D2] - Device release number: 0005
   0.145648     [D2] Trying to match device
   0.145661     [D3] match_function_regex: matching a device...
   0.145664     [D2] Device does not match - skipping
   0.159837     [D2] Checking device 4 of 11 (1D6B/0002)
   0.166862     [D2] - VendorID: 1d6b
   0.166867     [D2] - ProductID: 0002
   0.166868     [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64 ehci_hcd
   0.166870     [D2] - Product: EHCI Host Controller
   0.166871     [D2] - Serial Number: 0000:00:1a.0
   0.166873     [D2] - Bus: 001
   0.166874     [D2] - Device: 001
   0.166876     [D2] - Device release number: 0514
   0.166878     [D2] Trying to match device
   0.166880     [D3] match_function_regex: matching a device...
   0.166894     [D2] Device does not match - skipping
   0.179366     [D2] Checking device 5 of 11 (1D6B/0003)
   0.200847     [D2] - VendorID: 1d6b
   0.200851     [D2] - ProductID: 0003
   0.200853     [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64 xhci-hcd
   0.200854     [D2] - Product: xHCI Host Controller
   0.200856     [D2] - Serial Number: 0000:00:14.0
   0.200857     [D2] - Bus: 004
   0.200858     [D2] - Device: 001
   0.200860     [D2] - Device release number: 0514
   0.200862     [D2] Trying to match device
   0.200864     [D3] match_function_regex: matching a device...
   0.200877     [D2] Device does not match - skipping
   0.200931     [D2] Checking device 6 of 11 (9966/0202)
   0.202237     [D2] - VendorID: 9966
   0.202254     [D2] - ProductID: 0202
   0.202256     [D2] - Manufacturer: PSTEK
   0.202268     [D2] - Product: PSTEK Combo KVM 8/16 V:2.00
   0.202269     [D2] - Serial Number: unknown
   0.202271     [D2] - Bus: 003
   0.202272     [D2] - Device: 003
   0.202274     [D2] - Device release number: 0000
   0.202275     [D2] Trying to match device
   0.202276     [D3] match_function_regex: matching a device...
   0.202279     [D2] Device does not match - skipping
   0.202300     [D2] Checking device 7 of 11 (0557/2419)
   0.202309     [D2] - VendorID: 0557
   0.202327     [D2] - ProductID: 2419
   0.202329     [D2] - Manufacturer: unknown
   0.202331     [D2] - Product: unknown
   0.202334     [D2] - Serial Number: unknown
   0.202346     [D2] - Bus: 003
   0.202348     [D2] - Device: 004
   0.202350     [D2] - Device release number: 0100
   0.202353     [D2] Trying to match device
   0.202365     [D3] match_function_regex: matching a device...
   0.202367     [D2] Device does not match - skipping
   0.202371     [D2] Checking device 8 of 11 (0557/7000)
   0.202377     [D2] - VendorID: 0557
   0.202379     [D2] - ProductID: 7000
   0.202380     [D2] - Manufacturer: unknown
   0.202382     [D2] - Product: unknown
   0.202384     [D2] - Serial Number: unknown
   0.202386     [D2] - Bus: 003
   0.202389     [D2] - Device: 002
   0.202391     [D2] - Device release number: 0000
   0.202393     [D2] Trying to match device
   0.202395     [D3] match_function_regex: matching a device...
   0.202398     [D2] Device does not match - skipping
   0.202402     [D2] Checking device 9 of 11 (0665/5161)
   0.204923     [D1] nut_libusb_open get iManufacturer failed, retrying...
   0.207280     [D1] nut_libusb_open get iManufacturer failed, retrying...
   0.209669     [D1] nut_libusb_open get iManufacturer failed, retrying...
   0.212022     [D1] nut_libusb_open get iProduct failed, retrying...
   0.214338     [D1] nut_libusb_open get iProduct failed, retrying...
   0.216830     [D1] nut_libusb_open get iProduct failed, retrying...
   0.216846     [D2] - VendorID: 0665
   0.216847     [D2] - ProductID: 5161
   0.216849     [D2] - Manufacturer: unknown
   0.216850     [D2] - Product: unknown
   0.216852     [D2] - Serial Number: unknown
   0.216864     [D2] - Bus: 003
   0.216866     [D2] - Device: 006
   0.216868     [D2] - Device release number: 0001
   0.216870     [D2] Trying to match device
   0.216872     [D3] match_function_regex: matching a device...
   0.216885     [D2] Device matches
   0.216886     [D2] Reading first configuration descriptor
   0.216896     [D3] libusb_kernel_driver_active() returned 0: Success
   0.216926     [D2] Claimed interface 0 successfully
   0.216929     [D3] nut_usb_set_altinterface: skipped
libusb_set_interface_alt_setting(udev, 0, 0)
   0.216946     [D5] send_to_all: SETINFO ups.vendorid "0665"
   0.216950     [D5] send_to_all: SETINFO ups.productid "5161"
   0.218318     [D3] send: QGS
   0.278886     [D5] read [  0]: (8 bytes) => 28 32 32 31 2e 33 20 35
   0.310887     [D5] read [  8]: (8 bytes) => 39 2e 39 20 32 31 39 2e
   0.342884     [D5] read [ 16]: (8 bytes) => 35 20 35 39 2e 39 20 30
   0.382879     [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
   0.414887     [D5] read [ 32]: (8 bytes) => 20 33 36 32 2e 33 20 33
   0.454888     [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
   0.486869     [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
   0.518892     [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
   0.558896     [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
   0.574889     [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
   0.574909     [D3] read: (221.3 59.9 219.5 59.9 002.8 007 362.3
361.8 272.9 ---.- 022.9 100000000010
   0.574928     [D5] send_to_all: SETINFO input.voltage "221.3"
   0.576176     [D3] send: QPI
   0.622874     [D5] read [  0]: (8 bytes) => 28 50 49 30 32 0d 00 00
   0.622880     [D3] read: (PI02
   0.622937     [D5] send_to_all: SETINFO ups.firmware.aux "P02"
   0.622940     Using protocol: Voltronic 0.08
   0.622942     [D5] send_to_all: SETINFO driver.state "init.quiet"
   0.622956     [D5] send_to_all: SETINFO driver.version "2.8.0-2359-g6c0032e52"
   0.622959     [D5] send_to_all: SETINFO driver.version.internal "0.35"
   0.622963     [D5] send_to_all: SETINFO driver.name "nutdrv_qx"
   0.622965     [D5] send_to_all: SETINFO driver.state "init.info"
   0.622967     [D1] upsdrv_initinfo...
   0.622980     [D5] send_to_all: SETINFO driver.version.data "Voltronic 0.08"
   0.624104     [D3] send: QRI
   0.678874     [D5] read [  0]: (8 bytes) => 28 32 32 30 2e 30 20 30
   0.718855     [D5] read [  8]: (8 bytes) => 34 35 20 32 34 30 2e 30
   0.742898     [D5] read [ 16]: (8 bytes) => 20 36 30 2e 30 0d 00 00
   0.742910     [D3] read: (220.0 045 240.0 60.0
   0.742946     [D5] send_to_all: SETINFO output.voltage.nominal "220.0"
   0.742952     [D5] send_to_all: SETINFO output.current.nominal "45"
   0.742958     [D5] send_to_all: SETINFO battery.voltage.nominal "240.0"
   0.742964     [D5] send_to_all: SETINFO output.frequency.nominal "60.0"
   0.744242     [D3] send: QMD
   0.798887     [D5] read [  0]: (8 bytes) => 28 23 23 23 23 23 23 23
   0.838882     [D5] read [  8]: (8 bytes) => 23 23 23 23 47 31 30 4b
   0.870886     [D5] read [ 16]: (8 bytes) => 20 23 23 31 30 30 30 30
   0.910884     [D5] read [ 24]: (8 bytes) => 20 38 30 20 31 2f 31 20
   0.942903     [D5] read [ 32]: (8 bytes) => 32 33 30 20 32 33 30 20
   0.974868     [D5] read [ 40]: (8 bytes) => 32 30 20 31 32 2e 30 0d
   0.974873     [D3] read: (###########G10K ##10000 80 1/1 230 230 20 12.0
   0.974882     [D5] send_to_all: SETINFO device.model "G10K"
   0.974887     [D5] send_to_all: SETINFO ups.power.nominal "10000"
   0.974893     [D5] send_to_all: SETINFO output.powerfactor "0.8"
   0.974903     [D5] send_to_all: SETINFO input.phases "1"
   0.974907     [D5] send_to_all: SETINFO output.phases "1"
   0.974911     [D5] send_to_all: SETINFO input.voltage.nominal "230.0"
   0.976111     [D3] send: F
   1.022870     [D5] read [  0]: (8 bytes) => 23 32 32 30 2e 30 20 30
   1.062876     [D5] read [  8]: (8 bytes) => 34 35 20 32 34 30 2e 30
   1.086867     [D5] read [ 16]: (8 bytes) => 20 36 30 2e 30 0d 00 00
   1.086872     [D3] read: #220.0 045 240.0 60.0
   1.086881     [D5] send_to_all: SETINFO input.current.nominal "45.0"
   1.086901     [D5] send_to_all: SETINFO input.frequency.nominal "60.0"
   1.088234     [D3] send: QMF
   1.134884     [D5] read [  0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
   1.134903     [D3] read: (NAK
   1.134905     [D2] qx_process_answer: query rejected by the UPS (device.mfr)
   1.136185     [D3] send: QVFW
   1.198873     [D5] read [  0]: (8 bytes) => 28 56 45 52 46 57 3a 30
   1.230865     [D5] read [  8]: (8 bytes) => 30 30 37 37 2e 31 33 0d
   1.230870     [D3] read: (VERFW:00077.13
   1.230874     [D5] send_to_all: SETINFO ups.firmware "00077.13"
   1.232171     [D3] send: QID
   1.278886     [D5] read [  0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
   1.278896     [D3] read: (NAK
   1.278909     [D2] qx_process_answer: query rejected by the UPS
(device.serial)
   1.280047     [D3] send: I
   1.326866     [D5] read [  0]: (8 bytes) => 20 20 20 20 20 20 20 20
   1.334901     [D5] read [  8]: (8 bytes) => 0d 00 00 00 00 00 00 00
   1.334906     [D3] read:
   1.334908     [D2] qx_process_answer: short reply (device.mfr)
   1.336115     [D3] send: QGS
   1.390871     [D5] read [  0]: (8 bytes) => 28 32 31 39 2e 35 20 35
   1.430868     [D5] read [  8]: (8 bytes) => 39 2e 39 20 32 32 30 2e
   1.462877     [D5] read [ 16]: (8 bytes) => 34 20 36 30 2e 30 20 30
   1.502865     [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
   1.534867     [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
   1.566867     [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
   1.606862     [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
   1.638861     [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
   1.678883     [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
   1.694864     [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
   1.694884     [D3] read: (219.5 59.9 220.4 60.0 002.8 007 361.8
361.8 272.9 ---.- 022.9 100000000010
   1.694914     [D5] send_to_all: SETINFO input.frequency "59.9"
   1.694921     [D5] send_to_all: SETINFO output.voltage "220.4"
   1.694926     [D5] send_to_all: SETINFO output.frequency "60.0"
   1.694932     [D5] send_to_all: SETINFO output.current "2.8"
   1.694936     [D5] send_to_all: SETINFO ups.load "7"
   1.694940     [D5] send_to_all: SETINFO battery.voltage "272.9"
   1.694945     [D5] send_to_all: SETINFO ups.temperature "22.9"
   1.694962     [D5] send_to_all: SETINFO ups.type "online"
   1.694967     [D5] update_status: OL
   1.694970     [D5] update_status: !LB
   1.694988     [D5] update_status: !CAL
   1.695003     [D5] update_status: !FSD
   1.695007     [D5] send_to_all: SETINFO ups.beeper.status "enabled"
   1.696295     [D3] send: QMOD
   1.734859     [D5] read [  0]: (8 bytes) => 28 4c 0d 00 00 00 00 00
   1.734878     [D3] read: (L
   1.734891     [D5] update_status: OL
   1.736229     [D3] send: QWS
   1.790912     [D5] read [  0]: (8 bytes) => 28 30 30 30 30 30 30 30
   1.830878     [D5] read [  8]: (8 bytes) => 30 30 30 30 30 30 30 30
   1.862874     [D5] read [ 16]: (8 bytes) => 30 30 30 30 30 30 30 30
   1.894869     [D5] read [ 24]: (8 bytes) => 30 30 30 30 30 30 30 30
   1.934865     [D5] read [ 32]: (8 bytes) => 30 30 30 30 30 30 30 30
   1.966853     [D5] read [ 40]: (8 bytes) => 30 30 30 30 30 30 30 30
   2.006871     [D5] read [ 48]: (8 bytes) => 30 30 30 30 30 30 30 30
   2.038858     [D5] read [ 56]: (8 bytes) => 30 30 30 30 30 30 30 30
   2.046851     [D5] read [ 64]: (8 bytes) => 30 0d 30 30 30 30 30 30
   2.046870     [D3] read:
(0000000000000000000000000000000000000000000000000000000000000000
   2.048166     [D3] send: QBV
   2.102862     [D5] read [  0]: (8 bytes) => 28 32 37 33 2e 32 20 32
   2.142871     [D5] read [  8]: (8 bytes) => 30 20 30 31 20 31 30 30
   2.158875     [D5] read [ 16]: (8 bytes) => 20 30 31 30 0d 00 00 00
   2.158880     [D3] read: (273.2 20 01 100 010
   2.158886     battery_number: 20
   2.158895     battery_number, settable range: 1..9
   2.158904     [D5] send_to_all: SETINFO battery.packs "1"
   2.158907     [D5] send_to_all: SETFLAGS battery.packs RW
   2.158911     [D5] send_to_all: ADDRANGE battery.packs 1 99
   2.158914     [D5] send_to_all: SETFLAGS battery.packs RW NUMBER
   2.158919     [D5] send_to_all: SETINFO battery.charge "100"
   2.158924     [D5] send_to_all: SETINFO battery.runtime "600"
   2.160228     [D3] send: QLDL
   2.206859     [D5] read [  0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
   2.206874     [D3] read: (NAK
   2.206880     [D2] qx_process_answer: query rejected by the UPS
(output.power.minimum.percent)
   2.206894     [D2] qx_process_answer: query rejected by the UPS
(output.power.maximum.percent)
   2.208167     [D3] send: QFLAG
   2.270872     [D5] read [  0]: (8 bytes) => 28 45 70 62 72 61 73 64
   2.310890     [D5] read [  8]: (8 bytes) => 74 69 44 6f 76 65 66 6a
   2.318849     [D5] read [ 16]: (8 bytes) => 6d 0d 00 00 00 00 00 00
   2.318867     [D3] read: (EpbrasdtiDovefjm
   2.318910     [D5] send_to_all: SETINFO ups.start.auto "yes"
   2.318915     [D5] send_to_all: SETFLAGS ups.start.auto RW
   2.318928     [D5] send_to_all: ADDENUM ups.start.auto "no"
   2.318930     [D5] send_to_all: ADDENUM ups.start.auto "yes"
   2.318945     [D5] send_to_all: SETINFO battery.protection "yes"
   2.318948     [D5] send_to_all: SETFLAGS battery.protection RW
   2.318951     [D5] send_to_all: ADDENUM battery.protection "no"
   2.318964     [D5] send_to_all: ADDENUM battery.protection "yes"
   2.318969     [D4] ups_infoval_set: failed to preprocess value
[battery.energysave: EpbrasdtiDovefjm]
   2.318973     [D4] ups_infoval_set: failed to preprocess value
[ups.start.battery: EpbrasdtiDovefjm]
   2.318989     [D5] send_to_all: SETINFO outlet.0.switchable "no"
   2.318992     [D5] send_to_all: SETFLAGS outlet.0.switchable RW
   2.318994     [D5] send_to_all: ADDENUM outlet.0.switchable "no"
   2.318996     [D5] send_to_all: ADDENUM outlet.0.switchable "yes"
   2.319001     bypass_alarm: enabled
   2.319020     battery_alarm: enabled
   2.319036     bypass_when_off: disabled
   2.319055     alarm_control: enabled
   2.319060     converter_mode: disabled
   2.319072     eco_mode: disabled
   2.319075     battery_open_status_check: enabled
   2.319078     bypass_forbidding: disabled
   2.319083     [D4] ups_infoval_set: failed to preprocess value
[site_fault_detection: EpbrasdtiDovefjm]
   2.319087     [D4] ups_infoval_set: failed to preprocess value
[advanced_eco_mode: EpbrasdtiDovefjm]
   2.319091     [D4] ups_infoval_set: failed to preprocess value
[constant_phase_angle: EpbrasdtiDovefjm]
   2.319096     [D4] ups_infoval_set: failed to preprocess value
[limited_runtime_on_battery: EpbrasdtiDovefjm]
   2.319101     setvar(bypass_when_off, disabled)
   2.319104     bypass_when_off is already disabled
   2.319106     setvar: FAILED
   2.320434     [D3] send: QHE
   2.374864     [D5] read [  0]: (8 bytes) => 28 32 33 31 20 32 30 39
   2.382868     [D5] read [  8]: (8 bytes) => 20 0d 00 00 00 00 00 00
   2.382883     [D3] read: (231 209
   2.382916     [D5] send_to_all: SETINFO input.transfer.high "231"
   2.382929     [D5] send_to_all: SETFLAGS input.transfer.high RW
   2.382932     [D5] send_to_all: ADDRANGE input.transfer.high 231 244
   2.382934     [D5] send_to_all: SETFLAGS input.transfer.high RW NUMBER
   2.382950     [D5] send_to_all: SETINFO input.transfer.low "209"
   2.382953     [D5] send_to_all: SETFLAGS input.transfer.low RW
   2.382955     [D5] send_to_all: ADDRANGE input.transfer.low 196 209
   2.382957     [D5] send_to_all: SETFLAGS input.transfer.low RW NUMBER
   2.382962     [D5] send_to_all: SETINFO input.transfer.low.min "196"
   2.382966     [D5] send_to_all: SETINFO input.transfer.low.max "209"
   2.382970     [D5] send_to_all: SETINFO input.transfer.high.min "231"
   2.382975     [D5] send_to_all: SETINFO input.transfer.high.max "244"
   2.384206     [D3] send: QFRE
   2.430854     [D5] read [  0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
   2.430859     [D3] read: (NAK
   2.430861     [D2] qx_process_answer: query rejected by the UPS
(input.frequency.high)
   2.430864     [D2] qx_process_answer: query rejected by the UPS
(input.frequency.low)
   2.432092     [D3] send: QBYV
   2.494864     [D5] read [  0]: (8 bytes) => 28 32 36 34 20 31 31 30
   2.502857     [D5] read [  8]: (8 bytes) => 0d 00 00 00 00 00 00 00
   2.502875     [D3] read: (264 110
   2.502891     max_bypass_volt: 264
   2.502896     max_bypass_volt, settable range: 231..276
   2.502899     min_bypass_volt: 110
   2.502903     min_bypass_volt, settable range: 110..209
   2.504103     [D3] send: QBYF
   2.566858     [D5] read [  0]: (8 bytes) => 28 36 34 2e 30 20 35 36
   2.574855     [D5] read [  8]: (8 bytes) => 2e 30 0d 00 00 00 00 00
   2.574870     [D3] read: (64.0 56.0
   2.574876     max_bypass_freq: 64.0
   2.574891     max_bypass_freq, settable range: 61.0..64.0
   2.574895     min_bypass_freq: 56.0
   2.574909     min_bypass_freq, settable range: 56.0..59.0
   2.574915     [D2] setvar: nothing to do... [battery_number]
   2.576110     [D3] send: RE0
   2.798865     [D5] read [  0]: (8 bytes) => 00 00 00 00 00 00 00 00
   3.801004     [D3] read: Operation timed out (-7)
   3.801025     [D4] qx_process: failed to preprocess answer
[battery.voltage.low]
   3.802276     [D3] send: QPD
   3.846839     [D5] read [  0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
   3.846844     [D3] read: (NAK
   3.846855     [D2] qx_process_answer: query rejected by the UPS
(input_phase_angle)
   3.846872     [D2] qx_process_answer: query rejected by the UPS
(output_phase_angle)
   3.848203     [D3] send: QPAR
   3.894852     [D5] read [  0]: (8 bytes) => 28 30 31 0d 00 00 00 00
   3.894870     [D3] read: (01
]  3.894874     [D2] voltronic_parallel: non numerical value
[voltronic_parallel: 01
]  3.894875     [D4] ups_infoval_set: failed to preprocess value
[voltronic_parallel: 01
   3.894883     [D5] send_to_all: ADDCMD load.off
   3.894898     [D5] send_to_all: ADDCMD load.on
   3.894900     [D5] send_to_all: ADDCMD shutdown.return
   3.894902     [D5] send_to_all: ADDCMD shutdown.stayoff
   3.894904     [D5] send_to_all: ADDCMD shutdown.stop
   3.894916     [D5] send_to_all: ADDCMD test.battery.start
   3.894918     [D5] send_to_all: ADDCMD test.battery.start.deep
   3.894920     [D5] send_to_all: ADDCMD test.battery.start.quick
   3.894922     [D5] send_to_all: ADDCMD test.battery.stop
   3.894934     [D5] send_to_all: ADDCMD beeper.toggle
   3.894937     [D5] send_to_all: ADDCMD beeper.enable
   3.894940     [D5] send_to_all: ADDCMD beeper.disable
   3.894942     [D5] send_to_all: ADDCMD bypass.start
   3.894956     [D5] send_to_all: ADDCMD bypass.stop
   3.894960     [D5] send_to_all: SETINFO ups.delay.start "180"
   3.894963     [D5] send_to_all: SETFLAGS ups.delay.start RW
   3.894978     [D5] send_to_all: ADDRANGE ups.delay.start 0 599940
   3.894981     [D5] send_to_all: SETFLAGS ups.delay.start RW NUMBER
   3.894983     [D5] send_to_all: SETINFO ups.delay.shutdown "30"
   3.894985     [D5] send_to_all: SETFLAGS ups.delay.shutdown RW
   3.894989     [D5] send_to_all: ADDRANGE ups.delay.shutdown 12 5940
   3.895001     [D5] send_to_all: SETFLAGS ups.delay.shutdown RW NUMBER
   3.895005     No values for battery high/low voltages
   3.895010     [D5] send_to_all: SETINFO battery.voltage.low "208.00"
   3.895023     [D5] send_to_all: SETINFO battery.voltage.high "260.00"
   3.895026     Using 'guesstimation' (low: 208.000000, high: 260.000000)!
   3.895037     setvar(ups.delay.start, 60)
   3.895041     [D2] setvar: setting server side variable ups.delay.start
   3.895044     [D5] send_to_all: SETINFO ups.delay.start "60"
   3.895046     setvar: SUCCEED
   3.895049     setvar(ups.delay.shutdown, 30)
   3.895051     setvar: nothing to do... [ups.delay.shutdown]
   3.895057     [D5] send_to_all: SETINFO driver.parameter.pollfreq "30"
   3.895065     [D5] send_to_all: SETINFO driver.state "init.updateinfo"
   3.895068     [D1] upsdrv_updateinfo...
   3.895071     [D1] Quick update...
   3.896659     [D3] send: QGS
   3.950819     [D5] read [  0]: (8 bytes) => 28 32 32 30 2e 34 20 35
   3.990855     [D5] read [  8]: (8 bytes) => 39 2e 39 20 32 31 38 2e
   4.022858     [D5] read [ 16]: (8 bytes) => 37 20 35 39 2e 39 20 30
   4.062843     [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
   4.094844     [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
   4.126840     [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 33
   4.166841     [D5] read [ 48]: (8 bytes) => 2e 32 20 2d 2d 2d 2e 2d
   4.198838     [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
   4.238833     [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
   4.254852     [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 33
   4.254868     [D3] read: (220.4 59.9 218.7 59.9 002.8 007 361.8
361.8 273.2 ---.- 022.9 100000000010
   4.254872     [D5] update_status: OL
   4.254875     [D5] update_status: !LB
   4.254879     [D5] update_status: !CAL
   4.254896     [D5] update_status: !FSD
   4.254918     [D5] send_to_all: SETINFO ups.status "OL"
   4.254921     [D5] send_to_all: DATAOK
   4.254924     [D5] send_to_all: SETINFO driver.state "init.quiet"
   4.254938     [D5] send_to_all: SETINFO driver.parameter.pollinterval "10"
   4.254941     [D5] send_to_all: SETINFO driver.parameter.synchronous "yes"
   4.254943     Running as foreground process, not saving a PID file
   4.254956     [D5] send_to_all: SETINFO driver.flag.allow_killpower "0"
   4.254960     [D5] send_to_all: SETFLAGS driver.flag.allow_killpower RW NUMBER
   4.254963     [D5] send_to_all: ADDCMD driver.killpower
   4.254976     [D5] send_to_all: ADDCMD driver.reload
   4.254979     [D5] send_to_all: ADDCMD driver.reload-or-exit
   4.254981     [D5] send_to_all: ADDCMD driver.reload-or-error
   4.254984     [D5] send_to_all: SETINFO driver.state "quiet"
   4.254986     [D1] Driver initialization completed, beginning data
dump (1 loops)
   4.254990     [D5] send_to_all: SETINFO driver.state "updateinfo"
   4.254993     [D1] upsdrv_updateinfo...
   4.254995     [D1] Quick update...
   4.256195     [D3] send: QGS
   4.310837     [D5] read [  0]: (8 bytes) => 28 32 31 39 2e 35 20 35
   4.350846     [D5] read [  8]: (8 bytes) => 39 2e 39 20 32 31 39 2e
   4.390858     [D5] read [ 16]: (8 bytes) => 35 20 36 30 2e 30 20 30
   4.422834     [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
   4.454832     [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
   4.494848     [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
   4.526837     [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
   4.566835     [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
   4.598847     [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
   4.614849     [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
   4.614855     [D3] read: (219.5 59.9 219.5 60.0 002.8 007 361.8
361.8 272.9 ---.- 022.9 100000000010
   4.614859     [D5] update_status: OL
   4.614862     [D5] update_status: !LB
   4.614866     [D5] update_status: !CAL
   4.614883     [D5] update_status: !FSD
   4.614903     [D5] send_to_all: SETINFO driver.state "quiet"
   4.614906     [D5] send_to_all: SETINFO driver.state "updateinfo"
   4.614908     [D1] upsdrv_updateinfo...
   4.614911     [D1] Quick update...
   4.616211     [D3] send: QGS
   4.670846     [D5] read [  0]: (8 bytes) => 28 32 32 31 2e 33 20 35
   4.710831     [D5] read [  8]: (8 bytes) => 39 2e 39 20 32 31 38 2e
   4.742850     [D5] read [ 16]: (8 bytes) => 37 20 35 39 2e 39 20 30
   4.782842     [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
   4.814822     [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
   4.846843     [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
   4.886822     [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
   4.918833     [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
   4.958839     [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
   4.974825     [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
   4.974829     [D3] read: (221.3 59.9 218.7 59.9 002.8 007 361.8
361.8 272.9 ---.- 022.9 100000000010
   4.974833     [D5] update_status: OL
   4.974836     [D5] update_status: !LB
   4.974839     [D5] update_status: !CAL
   4.974855     [D5] update_status: !FSD
   4.974864     [D5] send_to_all: SETINFO driver.state "quiet"
   4.974878     [D5] send_to_all: SETINFO driver.state "dumping"
   4.974881     [D3] Entering dstate_dump
battery.charge: 100
battery.packs: 1
battery.protection: yes
battery.runtime: 600
battery.voltage: 272.9
battery.voltage.high: 260.00
battery.voltage.low: 208.00
battery.voltage.nominal: 240.0
device.model: G10K
device.type: ups
driver.debug: 6
driver.flag.allow_killpower: 0
driver.name: nutdrv_qx
driver.parameter.bypass_when_off: disabled
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 10
driver.parameter.port: auto
driver.parameter.synchronous: yes
driver.state: dumping
driver.version: 2.8.0-2359-g6c0032e52
driver.version.data: Voltronic 0.08
driver.version.internal: 0.35
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.current.nominal: 45.0
input.frequency: 59.9
input.frequency.nominal: 60.0
input.phases: 1
input.transfer.high: 231
input.transfer.high.max: 244
input.transfer.high.min: 231
input.transfer.low: 209
input.transfer.low.max: 209
input.transfer.low.min: 196
input.voltage: 221.3
input.voltage.nominal: 230.0
outlet.0.switchable: no
output.current: 2.8
output.current.nominal: 45
output.frequency: 60.0
output.frequency.nominal: 60.0
output.phases: 1
output.powerfactor: 0.8
output.voltage: 220.4
output.voltage.nominal: 220.0
ups.beeper.status: enabled
ups.delay.shutdown: 30
ups.delay.start: 60
ups.firmware: 00077.13
ups.firmware.aux: P02
ups.load: 7
ups.power.nominal: 10000
ups.productid: 5161
ups.start.auto: yes
ups.status: OL
ups.temperature: 22.9
ups.type: online
ups.vendorid: 0665
   4.975010     [D5] send_to_all: SETINFO driver.state "cleanup.upsdrv"
   4.975014     [D1] upsdrv_cleanup...
   4.975125     [D5] send_to_all: SETINFO driver.state "cleanup.exit



More information about the Nut-upsdev mailing list