    <p>Hi everybody,</p>
    <p>following UPS is successfuly tested.<br>
    </p>
    <p>Model: FSP Champ Tower 1k<br>
      <a class="moz-txt-link-freetext" href="https://www.fsp-europe.com/CS/champ-tower-series-1k2k3k/">https://www.fsp-europe.com/CS/champ-tower-series-1k2k3k/</a></p>
    <p>lsusb:</p>
    <p>Bus 002 Device 004: ID 0665:5161 Cypress Semiconductor USB to
      Serial<br>
    </p>
    <p><br>
    </p>
    <p>ups.conf:<br>
    </p>
    <p>[powerpal]<br>
          driver = blazer_usb<br>
          port = /dev/hidraw0</p>
    <p>Mode = standalone</p>
    <p>Distro = CentOS 8</p>
    <p>What I did to get UPS communicate.</p>
    <p>In terminal run as root:<br>
      ln -s /lib/udev/rules.d/62-nut-usbups.rules /etc/udev/rules.d/<br>
      udevadm control --reload-rules<br>
      udevadm trigger<br>
    </p>
    <p><br>
    </p>
    <p>output upsc:</p>
    <p>Init SSL without certificate database<br>
      battery.charge: 100<br>
      battery.voltage: 27.24<br>
      battery.voltage.high: 26.00<br>
      battery.voltage.low: 20.80<br>
      battery.voltage.nominal: 24.0<br>
      device.mfr: <br>
      device.model: WPHVT1K0<br>
      device.type: ups<br>
      driver.name: blazer_usb<br>
      driver.parameter.pollinterval: 2<br>
      driver.parameter.port: /dev/hidraw0<br>
      driver.parameter.synchronous: no<br>
      driver.version: 2.7.4<br>
      driver.version.internal: 0.12<br>
      input.current.nominal: 4.0<br>
      input.frequency: 50.0<br>
      input.frequency.nominal: 50<br>
      input.voltage: 232.9<br>
      input.voltage.fault: 232.9<br>
      input.voltage.nominal: 230<br>
      output.voltage: 229.7<br>
      ups.beeper.status: enabled<br>
      ups.delay.shutdown: 30<br>
      ups.delay.start: 180<br>
      ups.firmware: 01060.04<br>
      ups.load: 20<br>
      ups.mfr: <br>
      ups.model: WPHVT1K0<br>
      ups.productid: 5161<br>
      ups.status: OL<br>
      ups.temperature: 27.0<br>
      ups.type: online<br>
      ups.vendorid: 0665<br>
    </p>
    <p>output upscmd -l:<br>
    </p>
    <p>Instant commands supported on UPS [powerpal]:<br>
      <br>
      beeper.toggle - Toggle the UPS beeper<br>
      load.off - Turn off the load immediately<br>
      load.on - Turn on the load immediately<br>
      shutdown.return - Turn off the load and return when power is back<br>
      shutdown.stayoff - Turn off the load and remain off<br>
      shutdown.stop - Stop a shutdown in progress<br>
      test.battery.start - Start a battery test<br>
      test.battery.start.deep - Start a deep battery test<br>
      test.battery.start.quick - Start a quick battery test<br>
      test.battery.stop - Stop the battery test</p>