<div id="geary-body" dir="auto"><div><div>I have taken out the batteries and measured them with a multimeter. They put out 13V (they are rated 12V 9Ah).</div><div>Putting them back again and disconnecting the UPS from the mains it is kept on, powering all the connected devices.</div><div>The shutdowns only occur when the UPS is being monitored. Are you sure it's a battery problem? Do UPS perform further tests when they are being polled for data? I'll check with newer batteries then. I bought these one year ago :S</div></div></div><div id="geary-quote" dir="auto"><br>En dg., 2 de de des. 2018 a les 11:53 P. M., Charles Lepple <clepple@gmail.com> ha escrit:<br><blockquote type="cite"><div class="plaintext" style="white-space: pre-wrap;">On Dec 1, 2018, at 10:08 PM, raul <<a href="mailto:raulvior.bcn@gmail.com">raulvior.bcn@gmail.com</a>> wrote:
<blockquote> 
<blockquote> Also, given that the load is only 12%, double-check that the UPS is not configured for any power saving features that might cause the shutdown ("ECO mode" or similar). NUT does not get a notification for that event the way that it gets a normal LB shutdown notification.
</blockquote> 
 Are you referring to NUT (ups.conf) or to the UPS itself? I have checked the instruction manual and it says nothing about ECO modes. It talks only about disabling alarms or changing sensitivity to source voltage variations.
 
</blockquote>I was referring to a setting on the UPS (which NUT can change). It would look like this in the upsc output, so I don't think you have it:

outlet.1.autoswitch.charge.low: 0</div></blockquote></div>