    <div align="justify">OK, so yesterday evening I done a real test
      cutting of the power to the UPS. And it went good... the UPS
      supported my server for 28:50 minutes (i.e. the expected runtime
      with this load), before forcing shutdown. The batteries could
      still hold as charge was 30 % with about 15 minutes run time. And
      the UPS did hold for another full 10 minutes before powering off.
      These are the relevant lines from /var/log/ups:<br>
      <br>
      <font face="Courier New, Courier, monospace">20200124 201318 32
        0.0 12 [OB] NA 0.0<br>
        <font color="#ff0000">20200124 201323 30 0.0 13 [ALARM OB LB] NA
          0.0</font><br>
        20200124 201328 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
        20200124 201333 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
        20200124 201338 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
        20200124 201340 30 0.0 13 [FSD ALARM OB LB] NA 0.0</font><br>
      <br>
      The server was shutdown properly, but for some reason it did not
      power off. I saw an error from <font face="Courier New, Courier,
        monospace">umount</font> about busy file system, but I'm sure
      this doesn't always happen.<br>
      <br>
      With everything powered off, I extracted the original batteries to
      check them and measure the voltage. The batteries are Leoch
      DJW12-9.0 with one of them at 12.57 V and the other at 12.64 V
      (measured without load after the discharge).<br>
      <br>
      And this morning there was again a short power failure (not more
      than 30 minutes, because the router connected to the battery power
      from the UPS did hold up). With batteries charged up to 91% the
      UPS supported the server for just 07:10 minutes and forced
      shutdown with 69% battery charge and over 20 minutes of run
      time...<br>
      <br>
      <font face="Courier New, Courier, monospace">20200125 021123 70
        0.0 16 [OB] NA 0.0<br>
        <font color="#ff0000">20200125 021128 69 0.0 16 [FSD ALARM OB
          LB] NA 0.0</font><br>
        20200125 021133 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
        20200125 021138 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
        20200125 021143 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
        20200125 021148 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
        20200125 021150 69 0.0 16 [FSD ALARM OB LB] NA 0.0</font><br>
      <br>
      So, it seems to me that my UPS forces shutdown pretty randomly.
      Why the UPS is not waiting for the preset low battery charge value
      of 15%? What is actually driving this FSD ALARM and LB signal when
      batteries for sure could hold up more?<br>
    </div>
    <br>
    <br>
    Regards,<br>
    --<br>
    Georgi<br>
    <br>
    <div class="moz-cite-prefix">On 24.1.2020 at 18:28, Manuel Wolfshant
      wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:05C56614-98E8-4AAD-B6DD-E1D303964190@nobugconsulting.ro">
      <pre class="moz-quote-pre" wrap="">On January 24, 2020 6:13:31 PM GMT+02:00, "Georgi D. Sotirov" <a class="moz-txt-link-rfc2396E" href="mailto:gdsotirov@gmail.com"><gdsotirov@gmail.com></a> wrote:
</pre>
      <blockquote type="cite">
        <pre class="moz-quote-pre" wrap="">OK, my UPS turned out to be older that I thought. I apparently bought 
and installed it in September 2016 (not 2017 as I initially wrote).
That 
makes for over 3 years of work, which is over the life expectancy of
the 
batteries, 
</pre>
      </blockquote>
      <pre class="moz-quote-pre" wrap="">Good batteries can last 4-5 years. The chinese ones available in most shops last cca 2 years.
I use Panasonic (ordered from SOS Electronic) and they last 3-4 years. Even more.

</pre>
      <blockquote type="cite">
        <pre class="moz-quote-pre" wrap="">so I ordered new battery pack.

However, how could I make a full charge/discharge test? Should I
disable 
SHUTDOWNCMD in upsmon.conf? Or is there any other way to ignore forced 
shutdown? I'd like to see how long it would go until the batteries 
actually drain.

</pre>
      </blockquote>
      <pre class="moz-quote-pre" wrap="">Disconnect the computer from the UPS, connect a dummy load (like 2-3 * 100W tungsten light bulbs) , turn off the nut client on the computer. Start a stopwatch. Unplug the UPS from mains and wait for it to die. Read the value on the stopwatch.

wolfy