Yes it could be problem with some of the cells. I consider going to
the service, but I do not have another backup UPS and the service
requires leaving the UPS for at least 3 days (I presume, so they
could perform such tests). I'll try replacing the batteries and if
it doesn't help, then I'll go to the service.<br>
<br>
<br>
Regards,<br>
--<br>
Georgi<br>
<br>
<div class="moz-cite-prefix">On 27.1.2020 at 10:38, nicolae788
wrote:<br>
</div>
<blockquote type="cite"
cite="mid:CAE076VCi-CQacsDi+YHS8x0dHyOg9WC1JRi9tHvt0-L1=uJ3OA@mail.gmail.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<div dir="auto">Hello.
<div dir="auto"><br>
</div>
<div dir="auto">I sometimes encountered batteries that were ok,
but at times one of the cells would develop a random
short/open, therefore reducing the real capacity even if
voltage reading was ok. In the absence of a battery load
tester i would suggest running multiple tests with a load (car
headlight bulb or similar) on the battery outside the ups.
This is to eliminate the suspicion of a software or UPS unit
fault.</div>
<div dir="auto"><br>
</div>
<div dir="auto">Alex. </div>
</div>
<br>
<div class="gmail_quote">
<div dir="ltr" class="gmail_attr">On Mon, 27 Jan 2020, 02:53
Manuel Wolfshant, <<a
href="mailto:wolfy@nobugconsulting.ro"
moz-do-not-send="true">wolfy@nobugconsulting.ro</a>>
wrote:<br>
</div>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">
<div>
<div>On 1/25/20 10:53 AM, Georgi D. Sotirov wrote:<br>
</div>
<blockquote type="cite">
<div align="justify">OK, so yesterday evening I done a
real test cutting of the power to the UPS. And it went
good... the UPS supported my server for 28:50 minutes
(i.e. the expected runtime with this load), before
forcing shutdown. The batteries could still hold as
charge was 30 % with about 15 minutes run time. And the
UPS did hold for another full 10 minutes before powering
off. These are the relevant lines from /var/log/ups:<br>
<br>
<font face="Courier New, Courier, monospace">20200124
201318 32 0.0 12 [OB] NA 0.0<br>
<font color="#ff0000">20200124 201323 30 0.0 13 [ALARM
OB LB] NA 0.0</font><br>
20200124 201328 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
20200124 201333 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
20200124 201338 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
20200124 201340 30 0.0 13 [FSD ALARM OB LB] NA 0.0</font><br>
</div>
</blockquote>
<p>that looks perfectly fine<br>
</p>
<p><br>
</p>
<blockquote type="cite">
<div align="justify"> <br>
The server was shutdown properly, but for some reason it
did not power off. I saw an error from <font
face="Courier New, Courier, monospace">umount</font>
about busy file system, but I'm sure this doesn't always
happen.<br>
</div>
</blockquote>
<p>the error is related to your linux system, not to nut<br>
</p>
<p><br>
</p>
<blockquote type="cite">
<div align="justify"> <br>
With everything powered off, I extracted the original
batteries to check them and measure the voltage. The
batteries are Leoch DJW12-9.0 with one of them at 12.57
V and the other at 12.64 V (measured without load after
the discharge).<br>
</div>
</blockquote>
<p>That's... surprisingly well, assuming your multimeter
indicates correct values. I would have expected values
well below 12V</p>
<p><br>
</p>
<p><br>
</p>
<blockquote type="cite">
<div align="justify"> <br>
And this morning there was again a short power failure
(not more than 30 minutes, because the router connected
to the battery power from the UPS did hold up). With
batteries charged up to 91% the UPS supported the server
for just 07:10 minutes and forced shutdown with 69%
battery charge and over 20 minutes of run time...<br>
<br>
<font face="Courier New, Courier, monospace">20200125
021123 70 0.0 16 [OB] NA 0.0<br>
<font color="#ff0000">20200125 021128 69 0.0 16 [FSD
ALARM OB LB] NA 0.0</font><br>
20200125 021133 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
20200125 021138 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
20200125 021143 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
20200125 021148 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
20200125 021150 69 0.0 16 [FSD ALARM OB LB] NA 0.0</font><br>
<br>
So, it seems to me that my UPS forces shutdown pretty
randomly. Why the UPS is not waiting for the preset low
battery charge value of 15%? What is actually driving
this FSD ALARM and LB signal when batteries for sure
could hold up more?</div>
</blockquote>
<p><br>
</p>
<p>Can you please show us all the configuration files ? I
can only suspect that there is something wrong there
because (from a hardware point of view) the UPS behaves
very very well, according to your tests and logs.<br>
</p>
<p><br>
</p>
</div>
_______________________________________________<br>
Nut-upsuser mailing list<br>
<a href="mailto:Nut-upsuser@alioth-lists.debian.net"
target="_blank" rel="noreferrer" moz-do-not-send="true">Nut-upsuser@alioth-lists.debian.net</a><br>
<a
href="https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser"
rel="noreferrer noreferrer" target="_blank"
moz-do-not-send="true">https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser</a></blockquote>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
Nut-upsuser mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Nut-upsuser@alioth-lists.debian.net">Nut-upsuser@alioth-lists.debian.net</a>
<a class="moz-txt-link-freetext" href="https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser">https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser</a></pre>
</blockquote>
<br>
</body>
</html>