    <font face="Verdana">Hello Manuel,<br>
      <br>
      <blockquote type="cite">that looks perfectly fine</blockquote>
      <br>
      That one yes, but as I wrote, LB and FSD are happening on much
      higher battery charge values - 90% or more, which is not fine.<br>
      <br>
      <blockquote type="cite">That's... surprisingly well, assuming your
        multimeter indicates correct values. I would have expected
        values well below 12V</blockquote>
      <br>
      My multimeter hasn't gone inspection recently, but I do not have
      reasons to believe that the readings are wrong :-)<br>
      <br>
      <blockquote type="cite">Can you please show us all the
        configuration files ? I can only suspect that there is something
        wrong there because (from a hardware point of view) the UPS
        behaves very very well, according to your tests and logs.</blockquote>
      <br>
      Which configuration files you'd like to see exactly? I haven't
      made many configuration changes anyway. Isn't the UPS that reports
      LB (Low Battery) and FSB (forcing shutdown of the machine)? I mean
      if this is a configuration issue, then why I did not have this
      problem before? Why the shutdown happens on different battery
      charge levels?<br>
      <br>
      <br>
      Regards,<br>
      --<br>
      Georgi<br>
    </font><br>
    <div class="moz-cite-prefix">On 27.1.2020 at 2:53, Manuel Wolfshant
      wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:43f304a7-7878-de73-fed5-5bcbaa28fc13@nobugconsulting.ro">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <div class="moz-cite-prefix">On 1/25/20 10:53 AM, Georgi D.
        Sotirov wrote:<br>
      </div>
      <blockquote type="cite"
        cite="mid:9344bd05-80b9-b4dc-6424-52a0c83e2d16@gmail.com">
        <meta http-equiv="Content-Type" content="text/html;
          charset=UTF-8">
        <div align="justify">OK, so yesterday evening I done a real test
          cutting of the power to the UPS. And it went good... the UPS
          supported my server for 28:50 minutes (i.e. the expected
          runtime with this load), before forcing shutdown. The
          batteries could still hold as charge was 30 % with about 15
          minutes run time. And the UPS did hold for another full 10
          minutes before powering off. These are the relevant lines from
          /var/log/ups:<br>
          <br>
          <font face="Courier New, Courier, monospace">20200124 201318
            32 0.0 12 [OB] NA 0.0<br>
            <font color="#ff0000">20200124 201323 30 0.0 13 [ALARM OB
              LB] NA 0.0</font><br>
            20200124 201328 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
            20200124 201333 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
            20200124 201338 30 0.0 13 [FSD ALARM OB LB] NA 0.0<br>
            20200124 201340 30 0.0 13 [FSD ALARM OB LB] NA 0.0</font><br>
        </div>
      </blockquote>
      <p>that looks perfectly fine<br>
      </p>
      <p><br>
      </p>
      <blockquote type="cite"
        cite="mid:9344bd05-80b9-b4dc-6424-52a0c83e2d16@gmail.com">
        <div align="justify"> <br>
          The server was shutdown properly, but for some reason it did
          not power off. I saw an error from <font face="Courier New,
            Courier, monospace">umount</font> about busy file system,
          but I'm sure this doesn't always happen.<br>
        </div>
      </blockquote>
      <p>the error is related to your linux system, not to nut<br>
      </p>
      <p><br>
      </p>
      <blockquote type="cite"
        cite="mid:9344bd05-80b9-b4dc-6424-52a0c83e2d16@gmail.com">
        <div align="justify"> <br>
          With everything powered off, I extracted the original
          batteries to check them and measure the voltage. The batteries
          are Leoch DJW12-9.0 with one of them at 12.57 V and the other
          at 12.64 V (measured without load after the discharge).<br>
        </div>
      </blockquote>
      <p>That's... surprisingly well, assuming your multimeter indicates
        correct values. I would have expected values well below 12V</p>
      <p><br>
      </p>
      <p><br>
      </p>
      <blockquote type="cite"
        cite="mid:9344bd05-80b9-b4dc-6424-52a0c83e2d16@gmail.com">
        <div align="justify"> <br>
          And this morning there was again a short power failure (not
          more than 30 minutes, because the router connected to the
          battery power from the UPS did hold up). With batteries
          charged up to 91% the UPS supported the server for just 07:10
          minutes and forced shutdown with 69% battery charge and over
          20 minutes of run time...<br>
          <br>
          <font face="Courier New, Courier, monospace">20200125 021123
            70 0.0 16 [OB] NA 0.0<br>
            <font color="#ff0000">20200125 021128 69 0.0 16 [FSD ALARM
              OB LB] NA 0.0</font><br>
            20200125 021133 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
            20200125 021138 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
            20200125 021143 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
            20200125 021148 69 0.0 16 [FSD ALARM OB LB] NA 0.0<br>
            20200125 021150 69 0.0 16 [FSD ALARM OB LB] NA 0.0</font><br>
          <br>
          So, it seems to me that my UPS forces shutdown pretty
          randomly. Why the UPS is not waiting for the preset low
          battery charge value of 15%? What is actually driving this FSD
          ALARM and LB signal when batteries for sure could hold up
          more?</div>
      </blockquote>
      <p><br>
      </p>
      <p>Can you please show us all the configuration files ? I can only
        suspect that there is something wrong there because (from a
        hardware point of view) the UPS behaves very very well,
        according to your tests and logs.<br>
      </p>
      <p><br>
      </p>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
Nut-upsuser mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Nut-upsuser@alioth-lists.debian.net">Nut-upsuser@alioth-lists.debian.net</a>
<a class="moz-txt-link-freetext" href="https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser">https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser</a></pre>
    </blockquote>
    <br>
  </body>
</html>