    <p>My experience on situations like this is that it is almost always
      a bad battery.  Once load is removed, the voltage bounced back,
      and thus you show time/capacity, but it's possible that the sag
      under load drops you into LB, and causes the shutdown. <br>
    </p>
    <p>If the UPS has a battery test, give it a try, or load test the
      battery external to the UPS if you can - I suspect that the UPS
      will be fine, and the battery degraded.</p>
    <p>- Tim<br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 08/17/2020 04:41 PM, Bartosz wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAGPeYS1pc1pFS+mVa9ROFLq_vW-zOshbYZPA9y3KWrDT7W5KsQ@mail.gmail.com">
      <div dir="auto">I would also be very interested in this topic.
        <div dir="auto"><br>
        </div>
        <div dir="auto">Best Regards, </div>
        <div dir="auto">Bart</div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">pon., 17 sie 2020, 12:55
          użytkownik Marc Franquesa <<a
            href="mailto:marc.franquesa@gmail.com"
            moz-do-not-send="true">marc.franquesa@gmail.com</a>>
          napisał:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0 0 0
          .8ex;border-left:1px #ccc solid;padding-left:1ex">
          <div dir="ltr">Sorry, because this is not a technical question
            rather than a Hardware advice/recommendation.<br>
            <br>
            I have been using NUT-UPS perfectly for more than 7 years
            using two different Eaton/MGE models.<br>
            <br>
            After a battery replacement (replaced 1 year ago) after 5
            years of service, my current unit seems to behave faulty, as
            just after 1-2 minutes of power outage, shows the LB battery
            flag and sets FSD although having enough battery charge and
            runtime.<br>
            <br>
            I'm now looking to replace the UPS, but after comparing
            various vendors and models (and check against the HCL) I
            found that the Eaton ones are quite more expensive than
            other vendors/models.<br>
            <br>
            I'm thinking to move to a cheaper model, but still have a
            good device/NUT support, mainly usb-hid or blazer-usb
            drivers.<br>
            <br>
            For one side I'm happy with Eaton, however they are quite
            expensive, and although in the past supported NUT
            development I'm not sure if this is still the same
            collaborative support.<br>
            <br>
            On the other hand I'm looking to get a Salicru SPS, I've
            read some good (and also some bad) reviews of the devices
            but would like to know of any NUT-user experience.<br>
            <br>
            So could anyone with experience regarding Salicru/blazer-ups
            with NUT ?<br>
            <br>
            Should I give them a try or better stick with Eaton as well
            supported and good device?<br>
            <br>
            Thanks</div>
          _______________________________________________<br>
          Nut-upsuser mailing list<br>
          <a href="mailto:Nut-upsuser@alioth-lists.debian.net"
            target="_blank" rel="noreferrer" moz-do-not-send="true">Nut-upsuser@alioth-lists.debian.net</a><br>
          <a
href="https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser"
            rel="noreferrer noreferrer" target="_blank"
            moz-do-not-send="true">https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser</a></blockquote>
      </div>
      <!--'"--><br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Nut-upsuser mailing list
<a class="moz-txt-link-abbreviated" href="mailto:Nut-upsuser@alioth-lists.debian.net">Nut-upsuser@alioth-lists.debian.net</a>
<a class="moz-txt-link-freetext" href="https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser">https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser</a></pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
Tim Dawson

972-567-9360
</pre>
  </body>
</html>