<div dir="ltr"><div>Hello all,</div><div><br></div><div>I have a Grid Overvoltage issue in my Area 'cause of solar inverter. Unfortunately the Tripplite ups underreports the input voltage -- It happens with the Display Panel and with SNMP. I 'm aware that with SNMP I'm polling the system. So I can never  measure instant input Voltage. I'm polling at 3s interval without an issue. <br></div><div><br></div><div>I have tested this with a Wattmeter and a Fluke Digital meter.  The input voltage is off by alteast 3 - 5 V.  So when the UPS reports 250.5 V or 251 V the input voltage usually is between 253.5 and 255V and this is the case when the grid input Voltage is high for 10s at which point Solar inverter  resets.<br></div><div><br></div><div>My question is, <br></div><div>Is it possible the UPS Display is not reporting Instant input Voltage  ?</div><div><br></div><div>Kind Regards,</div><div><br></div><div>Yogesh<br></div><div><br></div><div><br></div></div>