<div dir="ltr"><div>Hi,</div><div><br></div><div>An Update. Thanks to David from Tripplite, he did perform some tests and was able to reproduce the problem. <br></div><div>Please note the UPS works, just that the reporting is off and is always underreporting.</div><div> </div><div>Kind Regards,</div><div><br></div><div>Yogesh<br></div><div><br></div><div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sat, Feb 27, 2021 at 11:09 AM Yogesh Bhanu <<a href="mailto:yogesh.bhanu@gmail.com">yogesh.bhanu@gmail.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr"><div>Dear Gene <a href="http://et.al" target="_blank">et.al</a>,</div><div><br></div><div>Thanks for the insightful reply. I have already involved our Grid Electricity Supplier and Solar Company. There is a general consensus that the grid company needs to do something. Seems to be general problem here.  </div><div>I discovered the issue by chance as the issue autoresolves and the inverter monitoring only displays open unresolved faults in its default mode.<br></div><div>My issue is three of four voltage measurements devices I have did measure closer to the inverter shutdown voltage and since I was only tracking UPS input voltage I did not see the issue with <br></div><div>high grid voltage hence the reason for my question. <br></div><div><br></div><div>Have a great weekend.</div><div><br></div><div>Kind Regards,</div><div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Fri, Feb 26, 2021 at 7:02 AM Gene Heskett <<a href="mailto:gheskett@shentel.net" target="_blank">gheskett@shentel.net</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">On Thursday 25 February 2021 22:50:05 Yogesh Bhanu via Nut-upsuser wrote:<br>
<br>
> Hello all,<br>
><br>
> I have a Grid Overvoltage issue in my Area 'cause of solar inverter.<br>
> Unfortunately the Tripplite ups underreports the input voltage -- It<br>
> happens with the Display Panel and with SNMP. I 'm aware that with<br>
> SNMP I'm polling the system. So I can never  measure instant input<br>
> Voltage. I'm polling at 3s interval without an issue.<br>
><br>
> I have tested this with a Wattmeter and a Fluke Digital meter.  The<br>
> input voltage is off by alteast 3 - 5 V.  So when the UPS reports<br>
> 250.5 V or 251 V the input voltage usually is between 253.5 and 255V<br>
> and this is the case when the grid input Voltage is high for 10s at<br>
> which point Solar inverter resets.<br>
><br>
> My question is,<br>
> Is it possible the UPS Display is not reporting Instant input Voltage <br>
> ?<br>
<br>
Its entirely possible since the invertor may take liberties with the <br>
waveform delivered, combined with whatever meter you are using's <br>
faithfullness to true rms response. With the more squareish waves output <br>
by an invertor, the measurement errors can exceed 10%. Bear in mind that <br>
most so called rms metering, is only truly accurate at 60 hertz, or 50 <br>
hertz depending on the environment its meant to be sold into.  The only <br>
true way to find out where the error actually lies, is to look at the <br>
invertors output with an oscilloscope, but even the eye can be confused <br>
if the distortion is seemingly well filtered, in which case a comparison <br>
with the sine wave output of a Good audio test oscillator can be <br>
informative. See a good explanation for the term rms, which stands for <br>
the square Root, of the Mean of the of Sum the squares, which is a fancy <br>
way of saying how much heat is generated by a suitable resistor hooked <br>
across the src. One massive enough that its temperature is not pulsing <br>
from the frequency of the applied voltage which will effect its <br>
resistance. This is very difficult to do in a modern digital multimeter <br>
because to do it right, they would have to do all that squaring and <br>
adding for a complete cycle, or about 6000 times a second, then on the <br>
zero crossing, instantly calculate the square root of all that to <br>
display it.<br>
<br>
Doing that, given the power src for such a meter making those claims is a <br>
9 volt battery expected to last 6+ months, is patently impossible.<br>
<br>
I just bought a new scope, a 4 trace, 350 MHz rated, 2GHz sampler by <br>
Siglent, that may be able to do that. It certainly has the horsepower to <br>
do it, but I've no clue if the code has been written to do it.<br>
<br>
Your other choices are a bolometer, generally used for signals above 500 <br>
MHz, or calorimetric involving measuring the temp rise of the water <br>
cooling the resistor, meaning 2 very accurate thermometers, and some <br>
means of measuring the water flow, all accurate to .1 degree and .1% <br>
flow.<br>
<br>
If its being a PITB, I believe I'd see if the invertor output could be <br>
turned down 1 or 2%. But if the scope says it outputting a square wave, <br>
flat across the top and bottom, I'd yell at the invertor maker. Its a <br>
BBLB invertor, so expect some additional expense for a smarter one.<br>
<br>
> Kind Regards,<br>
><br>
> Yogesh<br>
<br>
Good luck Yogesh.<br>
<br>
Cheers, Gene Heskett<br>
-- <br>
"There are four boxes to be used in defense of liberty:<br>
 soap, ballot, jury, and ammo. Please use in that order."<br>
-Ed Howdershelt (Author)<br>
If we desire respect for the law, we must first make the law respectable.<br>
 - Louis D. Brandeis<br>
Genes Web page <<a href="http://geneslinuxbox.net:6309/gene" rel="noreferrer" target="_blank">http://geneslinuxbox.net:6309/gene</a>><br>
<br>
_______________________________________________<br>
Nut-upsuser mailing list<br>
<a href="mailto:Nut-upsuser@alioth-lists.debian.net" target="_blank">Nut-upsuser@alioth-lists.debian.net</a><br>
<a href="https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser" rel="noreferrer" target="_blank">https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser</a><br>
</blockquote></div>
</blockquote></div>