<div dir="ltr"><div>>What's the load (in watts or percent) <br></div><div>30.00 (upsc)</div><div>between 28-35% (LCD)<br></div><div><br></div><div>and what is the runtime value in 
minutes? <br></div><div>2160.00 (upsc)</div><div>21-24 minutes (LCD)<br></div><div><br></div><div>>Is the minutes remaining value changing on the UPS LCD or in 
the WEBCARDLX GUI when on battery?</div><div>Yes in the LCD. The WEBCARDLX GUI gives connection refused when I try to open it in a browser.<br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Jun 9, 2021 at 10:22 PM David Zomaya <<a href="mailto:David_Zomaya@tripplite.com">David_Zomaya@tripplite.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">



<div>
Re 2:<br>
What's the load (in watts or percent) and what is the runtime value in minutes? Is the minutes remaining value changing on the UPS LCD or in the WEBCARDLX GUI when on battery?<br>
<br>
More generally, if no one else chimes in with an answer, I can set up some tests when I'm in the office to compare.<br>
<br>
- David Zomaya <br>
Tripp Lite<br>
<hr style="display:inline-block;width:98%">
<div id="gmail-m_8006559187319293763divRplyFwdMsg" dir="ltr"><font style="font-size:11pt" face="Calibri, sans-serif" color="#000000"><b>From:</b> Nut-upsuser <nut-upsuser-bounces+david_zomaya=<a href="mailto:tripplite.com@alioth-lists.debian.net" target="_blank">tripplite.com@alioth-lists.debian.net</a>> on behalf of Nathan Dehnel via Nut-upsuser <<a href="mailto:nut-upsuser@alioth-lists.debian.net" target="_blank">nut-upsuser@alioth-lists.debian.net</a>><br>
<b>Sent:</b> Tuesday, June 8, 2021 11:15:19 PM<br>
<b>To:</b> <a href="mailto:nut-upsuser@alioth-lists.debian.net" target="_blank">nut-upsuser@alioth-lists.debian.net</a><br>
<b>Subject:</b> [EXTERNAL] [Nut-upsuser] Couple questions about the output of upsc command</font>
<div> </div>
</div>
<div><font size="2" face="verdana,arial,sans-serif" color="#C11B17"><span>This is an
<b>EXTERNAL</b> email. Please take a moment and think before clicking any links or opening any attachments from this email. If suspicious, please forward to <a href="mailto:ishelpdesk@tripplite.com" target="_blank">ishelpdesk@tripplite.com</a> for review.</span></font>
<hr>
<div dir="ltr">
<div>I have pfsense set up as a master with nut 2.7.4_8, controlling a Tripplite Smartonline SU1500RTXLCD2U with SNMPWEBCARDLX, using the snmp driver.
<br>
</div>
<div><br>
</div>
<div>1. upsc does not return battery.runtime.low or battery.charge.low. Does my UPS simply not support these variables, or could I fix it with a configuration change?</div>
<div><br>
</div>
<div>2. battery.runtime does not change with load, either when online or on battery power. Is this supposed to happen? If not, can it be fixed?<br>
</div>
</div>
</div>
<hr>
<font face="calibri" color="grey">This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes
 no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
</font>
</div>

</blockquote></div>