    <div class="moz-cite-prefix">On 4/24/24 18:06, Charles Lepple wrote:<br>
    </div>
    <blockquote type="cite" cite="mid:219CB949-7A3E-44C7-BE5D-0235F1987C53@gmail.com">
      <pre>My guess is that if you sent 520, upsc would return 8 (for a revised 
maximum of 511 seconds). If not, the UPS is even weirder than most ðŸ™‚

As you found, the ignorelb option is available to work around 
limitations in the UPS shutdown logic.</pre>
    </blockquote>
    <p>I can confirm</p>
    <p>upsrw -s battery.runtime.low=520 -w CST150UC@localhost<br>
      battery.runtime.low: 8</p>
    <p>I also tried</p>
    <p>upsrw -s battery.runtime.low=480 -w CST150UC@localhost<br>
      battery.runtime.low: 480<br>
      <br>
      upsrw -s battery.runtime.low=540 -w CST150UC@localhost<br>
      battery.runtime.low: 28</p>
    <p>I guess none of this makes any sense to me so maybe the ignorelb
      option is the way to go unless you have a suggestion as to what
      value to use with upsrw -s battery.runtime.low, lol.</p>
    <p>This seems to work though</p>
    <p>mcedit /etc/nut/nut.conf<br>
      [CST150UC]<br>
      driver = usbhid-ups<br>
      port = auto<br>
      ignorelb<br>
      ondelay = -1<br>
      override.battery.runtime.low = 3600<br>
      <br>
      upsc CST150UC@localhost<br>
      battery.runtime.low: 3600 (system will shutdown when 60 minutes of
      runtime is left)<br>
      ups.delay.start: -1 (never powers on the load, even when main
      power returns)</p>
    <p>Thank you<br>
    </p>