    <p>Hi Jim,</p>
    <p>Thanks for the prompt response.</p>
    <p>The restart I refer to was exactly as you say.  Where I restarted
      the service using: systemctl restart nut-server.  This was
      separate to where I mention the reboot of server machine, which
      resolves the issue.<br>
    </p>
    <p>The driver used was:<br>
      Network UPS Tools - UPS driver controller 2.8.0<br>
      Network UPS Tools - BCMXCP UPS driver 0.32 (2.8.0)</p>
    <p>I simulated the fault again, by putting the UPS in bypass and
      disconnecting the battery.  This caused the RB alert again.  With
      this I then reconnected battery, restored UPS to normal operating
      condition.  Then used upsdrvctl to STOP and START the driver.</p>
    Generating alert condition for simulating RB:<br>
    Alert type: REPLBATT<br>
    .....................<br>
    ups.status: ALARM OL BYPASS RB<br>
    ups.test.result: Done and error<br>
    <br>
    Alert cleared on UPS, and alert condition with RB persisting on
    NUT-SERVER:<br>
    Alert type: ONLINE<br>
    .................<br>
    ups.status: OL RB<br>
    <p>ups.test.result: Done and passed</p>
    Restarting using upsdrvctl start/stop command clears RB:<br>
    Alert type: COMMOK<br>
    ..................<br>
    ups.status: OL<br>
    ups.test.result: Done and passed<br>
    <p>So it seems that your and my suspicions have been verified. 
      Where bcmxcp seems to "latch" the alarm until driver restart or
      server reboot.</p>
    <p>I think you are correct, in that this can cause issues in other
      subsets of real-life cases.  Thinking here of automating and
      scripting and so forth.</p>
    <p>What would you suggest at this point?  Can this be submitted as a
      bug?</p>
    <p>Vyasa<br>
    </p>
    <p><br>
    </p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 6/30/25 14:18, Jim Klimov wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAJYg8v+8sm0vEjPg0uXALUcLd4xva=By8F4fD9d=tcM3UwKC0w@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div>Hello,</div>
        <div><br>
        </div>
        <div>  You mention that you've tried restarting the "nut-server"
          - I suppose you mean literally, the service unit by such name
          - of the NUT data server. Did you try restarting the unit for
          the NUT driver (e.g. `systemctl restart nut-drvier@upsname`
          with NUT v2.8.x and newer)?</div>
        <div><br>
        </div>
        <div>  You did not mention the driver used, but I wonder if that
          driver program "latches" the RB value when it goes bad and
          never updates it?.. This could make sense when UPS battery
          replacement means server downtime, but that is just a subset
          of real-life cases - so generally can be just an oversight.
          For example, `bcmxcp` code seems to only set
          `bcmxcp_status.alarm_replace_battery=1` (oddly neither the
          field nor struct is ever initialized to 0, so might be garbage
          on some systems/compilers that do not zero-out aggregate types
          by default).</div>
        <div><br>
        </div>
        <div>Jim</div>
        <div><br>
        </div>
      </div>
      <br>
      <div class="gmail_quote gmail_quote_container">
        <div dir="ltr" class="gmail_attr">On Mon, Jun 30, 2025 at
          7:53 PM Vyasa via Nut-upsuser <<a
            href="mailto:nut-upsuser@alioth-lists.debian.net"
            moz-do-not-send="true" class="moz-txt-link-freetext">nut-upsuser@alioth-lists.debian.net</a>>
          wrote:<br>
        </div>
        <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div>
            <p>Hello,</p>
            <p>CONFIGURATION:<br>
            </p>
            <p>I am using a Powerware PW9120 3000i, on a network
              configuration with a server and a couple of slaves. <br>
            </p>
            <p>The nut-server OS is <i>Debian 12 (6.1.0-37-amd64)</i>. 
              Nut was installed from the Debian repo with version <i>2.8.0-7
                amd64</i>, and client has the same version.</p>
            <p>UPS is connected with a standard RS232 serial connection,
              and works with all standard commands and functionality.</p>
            <p>Command "<i>upscmd -l upsname</i>" provides the
              following, where I have successfully used <i>test.battery.start</i>
              and <i>test.system.start</i>:</p>
            <p>beeper.disable - Disable the UPS beeper<br>
              beeper.enable - Enable the UPS beeper<br>
              beeper.mute - Temporarily mute the UPS beeper<br>
              load.on - Turn on the load immediately<br>
              outlet.1.load.off - Turn off the load on outlet 1
              immediately<br>
              outlet.1.load.on - Turn on the load on outlet 1
              immediately<br>
              outlet.1.shutdown.return - Turn off the outlet 1 and
              return when power is back<br>
              outlet.2.load.off - Turn off the load on outlet 2
              immediately<br>
              outlet.2.load.on - Turn on the load on outlet 2
              immediately<br>
              outlet.2.shutdown.return - Turn off the outlet 2 and
              return when power is back<br>
              shutdown.return - Turn off the load and return when power
              is back<br>
              shutdown.stayoff - Turn off the load and remain off<br>
              test.battery.start - Start a battery test<br>
              test.system.start - Start a system test<br>
            </p>
            <p>ISSUE:</p>
            <p>Every couple of years when I have to replace batteries in
              the UPS, I get an issue with not being able to clear the
              REPLBATT alert.  That is not until I reboot the server
              running NUT-SERVER.  This might seem as not a big deal,
              but becomes a hassle when batteries haven't quite failed
              yet and are still good after a ups battery test.</p>
            <p>The UPS itself reports OK after battery replacement or
              battery test, and clears alarm on its LCD.  But when I
              poll the UPS data using "upsc upsname" I still see the RB
              or REPLBATT and this will not clear until I reboot the
              server.  So without reboot the alert will then be
              generated based on RBWARNTIME in upsmon.conf, which is as
              per nut design.<br>
            </p>
            <p>So without reboot I always get the RB flag with status:</p>
            <i>Alert type: REPLBATT</i><br>
            <i>............</i><br>
            <i>ups.status: OL RB</i><br>
            <i>ups.test.result: Done and passed</i><br>
            <p>After reboot of server the alert is cleared:</p>
            <i>Alert type: COMMOK<br>
              ............<br>
              ups.status: OL<br>
              ups.test.result: Done and passed</i><br>
            <p>So my question becomes, why is this reboot required and
              it doesn't seem to make any sense?  I can't understand why
              the polled data from a UPS would change after a reboot,
              while on the UPS LCD its reporting all OK?  I tried
              restarting NUT-SERVER to see if it would make any
              difference.  Also, the command test.battery.start will
              clear the alarm on the UPS if battery test good.</p>
            <p>The only explanation that I have come up with is that the
              persistent RB/REPLBATT is latched to this condition and is
              an artifact of UPS to NUT handshaking.<br>
            </p>
            <p>Any feedback would be kindly appreciated, as I have
              searched and searched.</p>
            <p>Thank you!<br>
            </p>
            Vyasa<br>
          </div>
          _______________________________________________<br>
          Nut-upsuser mailing list<br>
          <a href="mailto:Nut-upsuser@alioth-lists.debian.net"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">Nut-upsuser@alioth-lists.debian.net</a><br>
          <a
href="https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser</a><br>
        </blockquote>
      </div>
    </blockquote>
  </body>
</html>