[Nut-upsdev] 2.0.3-pre2: Spurious UPS UPS@localhost battery is
low ?
Gordon Rowell
gordonr-nut at gormand.com.au
Wed Feb 8 01:12:34 UTC 2006
Peter Selinger wrote:
> Hi Gordon,
Sorry for the delay - life has been busy with getting a release together.
> Just looking at the numbers, it looks like you might have found a bug
> in the voltage conversion function that might be related to the
> signedness/unsignedness of numbers; note that -6301.0 + 65536/10 =
> 252.6. The latter could be a legitimate voltage, but seems unusually
> high for any country (your "nominal" voltage is 230).
As Charlie said, I believe we are or were nominally 240V. I don't know
that the power to my shed is all that "nice".
> I am also worried about your battery.temperature, ups.temperature,
It gets hot in my shed. I'd suspect we might see up to 45C ambient on a
really hot day, but not 302F, which would be even more unpleasant.
> and
> battery.date. It looks like we might need to tweak the driver a bit
> for your unit. (This seems to be a different UPS than the one you
> wrote about last week?)
Yes - this is my UPS at home. The one last week was at a site I support.
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.date: 3150/08/01
battery.mfr.date: 2005/01/20
battery.runtime: 247
battery.runtime.low: 120
battery.temperature: 302.0
battery.voltage: 13.0
battery.voltage.nominal: 12.0
driver.name: newhidups
driver.version: 2.0.3-pre2
driver.version.data: APC HID 0.8
driver.version.internal: 0.28
input.voltage: -6299.0
input.voltage.nominal: 230
output.voltage: 230.0
output.voltage.target.line: 230.0
ups.beeper.status: enabled
ups.delay.shutdown: -1
ups.firmware: 814.s3.I
ups.firmware.aux: s3
ups.load: 80.0
ups.mfr: American Power Conversion
ups.mfr.date: 2005/01/20
ups.model: Back-UPS BF500
ups.serial: AB0504244053
ups.status: OL
ups.temperature: 302.0
ups.test.result: No test initiated
> Could you again run "./drivers/newhidups -u root -DD -a UPS auto" and
> post the "Path" lines, so that I can see the raw, unconverted values
> of these variables?
Path: UPS.PowerSummary.iProduct, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.iSerialNumber, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.iManufacturer, Type: Feature, Value: 3.000000
Path: UPS.PowerSummary.iOEMInformation, Type: Feature, Value: 3.000000
Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, Value: 4.000000
Path: UPS.PowerSummary.Rechargeable, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.CapacityMode, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.DesignCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, Value: 50.000000
Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, Value:
10.000000
Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, Value: 12852.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, Value: 240.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, Value: 240.000000
Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, Value: -1.000000
Path: UPS.PowerSummary.DelayBeforeReboot, Type: Feature, Value: 0.000000
Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, Value: 120.000000
Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, Value: 12.000000
Path: UPS.PowerSummary.Voltage, Type: Feature, Value: 13.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, Value:
1.000000
Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, Value:
1.00000 0
Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature,
Value: 1.000 000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Input, V alue: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Input,
Value: 0.00 0000
Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Feature,
Value: 0. 000000
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input,
Value: 0.000 000
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature,
Value: 0.0 00000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type:
Input, Val ue: 0.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type:
Feature, V alue: 0.000000
Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input,
Value: 0.00 0000
Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature,
Value: 0. 000000
Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input,
Value: 0.0000 00
Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature,
Value: 0.00 0000
Path: UPS.PowerSummary.PresentStatus.OverLoad, Type: Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.OverLoad, Type: Feature, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Input,
Value: 0. 000000
Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Feature,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Feature, Value:
0.000000
Path: UPS.Battery.Test, Type: Input, Value: 6.000000
Path: UPS.Battery.Test, Type: Feature, Value: 6.000000
Path: UPS.Battery.APCBattCapBeforeStartup, Type: Feature, Value: 0.000000
Path: UPS.Battery.ff86001a, Type: Feature, Value: 0.000000
Path: UPS.Battery.ff86001b, Type: Feature, Value: 0.000000
Path: UPS.Battery.APCBattReplaceDate, Type: Feature, Value: 599297.000000
Path: UPS.Battery.ManufacturerDate, Type: Feature, Value: 12852.000000
Path: UPS.Battery.RemainingCapacity, Type: Feature, Value: 100.000000
Path: UPS.Battery.RemainingTimeLimit, Type: Feature, Value: 120.000000
Path: UPS.Battery.RunTimeToEmpty, Type: Feature, Value: 240.000000
Path: UPS.Battery.Temperature, Type: Feature, Value: 302.000000
Path: UPS.Battery.ConfigVoltage, Type: Feature, Value: 12.000000
Path: UPS.Battery.Voltage, Type: Feature, Value: 13.000000
Path: UPS.Battery.ff860024, Type: Feature, Value: 244.000000
Path: UPS.Battery.ff860018, Type: Feature, Value: -2146919680.000000
Path: UPS.Input.Voltage, Type: Feature, Value: -214695680.000000
Path: UPS.Input.ConfigVoltage, Type: Feature, Value: 230.000000
Path: UPS.Input.ff860052, Type: Feature, Value: 8.000000
Path: UPS.Input.ff860061, Type: Feature, Value: 1.000000
Path: UPS.Input.ff860024, Type: Feature, Value: 130.000000
Path: UPS.Output.PercentLoad, Type: Feature, Value: 81.000000
Path: UPS.Output.00840044, Type: Feature, Value: 325.000000
Path: UPS.Output.Frequency, Type: Feature, Value: 51.000000
Path: UPS.Output.Voltage, Type: Feature, Value: 230.000000
Path: UPS.Output.ConfigVoltage, Type: Feature, Value: 230.000000
Path: UPS.Output.HighVoltageTransfer, Type: Feature, Value: 266.000000
Path: UPS.Output.LowVoltageTransfer, Type: Feature, Value: 180.000000
Path: UPS.Output.APCDelayBeforeStartup, Type: Feature, Value: 0.000000
Path: UPS.Output.APCShutdownAfterDelay, Type: Feature, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, Value: -1.000000
Path: UPS.Output.DelayBeforeStartup, Type: Feature, Value: 0.000000
Path: UPS.Output.DelayBeforeReboot, Type: Feature, Value: 0.000000
Path: UPS.Output.APCForceShutdown, Type: Feature, Value: 0.000000
Path: UPS.Output.APCDelayBeforeShutdown, Type: Feature, Value: 810.000000
Path: UPS.iProduct, Type: Feature, Value: 5.000000
Path: UPS.iSerialNumber, Type: Feature, Value: 2.000000
Path: UPS.iManufacturer, Type: Feature, Value: 3.000000
Path: UPS.00840001, Type: Feature, Value: 6.000000
Path: UPS.APC_UPS_FirmwareRevision, Type: Feature, Value: 7.000000
Path: UPS.APC_USB_FirmwareRevision, Type: Feature, Value: 8.000000
Path: UPS.APCPanelTest, Type: Feature, Value: 0.000000
Path: UPS.ManufacturerDate, Type: Feature, Value: 12852.000000
Path: UPS.ff860027, Type: Feature, Value: 0.000000
Path: UPS.ff860028, Type: Feature, Value: 0.000000
Path: UPS.AudibleAlarmControl, Type: Feature, Value: 2.000000
Path: UPS.PresentStatus.Charging, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.Charging, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.Discharging, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.Discharging, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.ACPresent, Type: Input, Value: 1.000000
Path: UPS.PresentStatus.ACPresent, Type: Feature, Value: 1.000000
Path: UPS.PresentStatus.BatteryPresent, Type: Input, Value: 1.000000
Path: UPS.PresentStatus.BatteryPresent, Type: Feature, Value: 1.000000
Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Input, Value:
0.00000 0
Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
Value: 0.000 000
Path: UPS.PresentStatus.ShutdownRequested, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.ShutdownRequested, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.ShutdownImminent, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Input, Value:
0.000000
Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Feature, Value:
0.00000 0
Path: UPS.PresentStatus.CommunicationLost, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.CommunicationLost, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.NeedReplacement, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.NeedReplacement, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.OverLoad, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.OverLoad, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.VoltageNotRegulated, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.ff860080, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.ff860080, Type: Feature, Value: 0.000000
Path: UPS.ff860001.ff860023, Type: Feature, Value: 0.000000
Path: UPS.ff860001.ff860026, Type: Feature, Value: 6.000000
Path: UPS.ff860001.ff860025, Type: Feature, Value: 50462976.000000
Path: UPS.PowerConverter.ff860024, Type: Feature, Value: 219.000000
[root at bigted sbin]# ./newhidups -u root -DD -a UPS auto 2>&1 | grep Path
Path: UPS.PowerSummary.iProduct, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.iSerialNumber, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.iManufacturer, Type: Feature, Value: 3.000000
Path: UPS.PowerSummary.iOEMInformation, Type: Feature, Value: 3.000000
Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, Value: 4.000000
Path: UPS.PowerSummary.Rechargeable, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.CapacityMode, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.DesignCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, Value: 50.000000
Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, Value:
10.000000
Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, Value: 12852.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, Value: 240.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, Value: 240.000000
Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, Value: -1.000000
Path: UPS.PowerSummary.DelayBeforeReboot, Type: Feature, Value: 0.000000
Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, Value: 120.000000
Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, Value: 12.000000
Path: UPS.PowerSummary.Voltage, Type: Feature, Value: 13.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, Value:
1.000000
Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, Value:
1.000000
Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature,
Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Input,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Feature,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type:
Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type:
Feature, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.OverLoad, Type: Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.OverLoad, Type: Feature, Value:
0.000000
Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Input,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Feature,
Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Input, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Feature, Value:
0.000000
Path: UPS.Battery.Test, Type: Input, Value: 6.000000
Path: UPS.Battery.Test, Type: Feature, Value: 6.000000
Path: UPS.Battery.APCBattCapBeforeStartup, Type: Feature, Value: 0.000000
Path: UPS.Battery.ff86001a, Type: Feature, Value: 0.000000
Path: UPS.Battery.ff86001b, Type: Feature, Value: 0.000000
Path: UPS.Battery.APCBattReplaceDate, Type: Feature, Value: 599297.000000
Path: UPS.Battery.ManufacturerDate, Type: Feature, Value: 12852.000000
Path: UPS.Battery.RemainingCapacity, Type: Feature, Value: 100.000000
Path: UPS.Battery.RemainingTimeLimit, Type: Feature, Value: 120.000000
Path: UPS.Battery.RunTimeToEmpty, Type: Feature, Value: 240.000000
Path: UPS.Battery.Temperature, Type: Feature, Value: 302.000000
Path: UPS.Battery.ConfigVoltage, Type: Feature, Value: 12.000000
Path: UPS.Battery.Voltage, Type: Feature, Value: 13.000000
Path: UPS.Battery.ff860024, Type: Feature, Value: 244.000000
Path: UPS.Battery.ff860018, Type: Feature, Value: -2146919680.000000
Path: UPS.Input.Voltage, Type: Feature, Value: -214695680.000000
Path: UPS.Input.ConfigVoltage, Type: Feature, Value: 230.000000
Path: UPS.Input.ff860052, Type: Feature, Value: 8.000000
Path: UPS.Input.ff860061, Type: Feature, Value: 1.000000
Path: UPS.Input.ff860024, Type: Feature, Value: 130.000000
Path: UPS.Output.PercentLoad, Type: Feature, Value: 81.000000
Path: UPS.Output.00840044, Type: Feature, Value: 325.000000
Path: UPS.Output.Frequency, Type: Feature, Value: 51.000000
Path: UPS.Output.Voltage, Type: Feature, Value: 230.000000
Path: UPS.Output.ConfigVoltage, Type: Feature, Value: 230.000000
Path: UPS.Output.HighVoltageTransfer, Type: Feature, Value: 266.000000
Path: UPS.Output.LowVoltageTransfer, Type: Feature, Value: 180.000000
Path: UPS.Output.APCDelayBeforeStartup, Type: Feature, Value: 0.000000
Path: UPS.Output.APCShutdownAfterDelay, Type: Feature, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, Value: -1.000000
Path: UPS.Output.DelayBeforeStartup, Type: Feature, Value: 0.000000
Path: UPS.Output.DelayBeforeReboot, Type: Feature, Value: 0.000000
Path: UPS.Output.APCForceShutdown, Type: Feature, Value: 0.000000
Path: UPS.Output.APCDelayBeforeShutdown, Type: Feature, Value: 810.000000
Path: UPS.iProduct, Type: Feature, Value: 5.000000
Path: UPS.iSerialNumber, Type: Feature, Value: 2.000000
Path: UPS.iManufacturer, Type: Feature, Value: 3.000000
Path: UPS.00840001, Type: Feature, Value: 6.000000
Path: UPS.APC_UPS_FirmwareRevision, Type: Feature, Value: 7.000000
Path: UPS.APC_USB_FirmwareRevision, Type: Feature, Value: 8.000000
Path: UPS.APCPanelTest, Type: Feature, Value: 0.000000
Path: UPS.ManufacturerDate, Type: Feature, Value: 12852.000000
Path: UPS.ff860027, Type: Feature, Value: 0.000000
Path: UPS.ff860028, Type: Feature, Value: 0.000000
Path: UPS.AudibleAlarmControl, Type: Feature, Value: 2.000000
Path: UPS.PresentStatus.Charging, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.Charging, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.Discharging, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.Discharging, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.ACPresent, Type: Input, Value: 1.000000
Path: UPS.PresentStatus.ACPresent, Type: Feature, Value: 1.000000
Path: UPS.PresentStatus.BatteryPresent, Type: Input, Value: 1.000000
Path: UPS.PresentStatus.BatteryPresent, Type: Feature, Value: 1.000000
Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Input, Value:
0.000000
Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
Value: 0.000000
Path: UPS.PresentStatus.ShutdownRequested, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.ShutdownRequested, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.ShutdownImminent, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Input, Value:
0.000000
Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Feature, Value:
0.000000
Path: UPS.PresentStatus.CommunicationLost, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.CommunicationLost, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.NeedReplacement, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.NeedReplacement, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.OverLoad, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.OverLoad, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.VoltageNotRegulated, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, Value: 0.000000
Path: UPS.PresentStatus.ff860080, Type: Input, Value: 0.000000
Path: UPS.PresentStatus.ff860080, Type: Feature, Value: 0.000000
Path: UPS.ff860001.ff860023, Type: Feature, Value: 0.000000
Path: UPS.ff860001.ff860026, Type: Feature, Value: 6.000000
Path: UPS.ff860001.ff860025, Type: Feature, Value: 50462976.000000
Path: UPS.PowerConverter.ff860024, Type: Feature, Value: 219.000000
Gordon
More information about the Nut-upsdev