[Nut-upsdev] apcsmart and ambient data (was: NUT and MonAMI plugin)

Arnaud QUETTE Arnaud.QUETTE at mgeups.com
Thu Nov 23 14:38:19 CET 2006


Hi Paul,

> I have another NUT client for your client-projects[1] page: MonAMI[2].
> 
> MonAMI aims to be a "universal sensor framework".  The data gathered 
from 
> MonAMI's NUT plugin can be sent to any of the output plugins. Currently, 

> these include Ganglia, Nagios, KSysguard and a file-logger (amongst 
others).

interesting though I've not had time to investigate more.
I've just added a new entry on the client projects page.
Thanks for your work on this point. 

> As an aside, I've configured NUT to talk to our APC-8000[3], which comes 
with 
> an "AP9619" [4] expansion card.  This card has an external temperature 
probe, 
> but it doesn't seem to appear in the variables NUT returns: the UPS's 
> internal temperature is mentioned, but no 
"ambient.temperature.measured". 
> I've copied the output below.
> 
> Should the external probe's temperature be reported or does the 
smart-apc 
> driver and/or the serial interface not support this?

in theory, we have the ambient.* collection (check 
http://eu1.networkupstools.org/doc/2.0.1/new-names.html)
to report such data. And the apcsmart driver seems to support the ambient 
data.
So, so the problem might sit in the sensor data acquisition.
But I'm not the right person to follow up. Maybe some other NUT developers 
will be able to...

> ...
> 
> [1] http://www.networkupstools.org/client-projects/
> [2] http://monami.sourceforge.net/
> [3] 
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI

> [4] 
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9619
> 
> BEGIN LIST VAR APC-8000RMXLI
> VAR APC-8000RMXLI battery.alarm.threshold "0"
> VAR APC-8000RMXLI battery.charge "100.0"
> VAR APC-8000RMXLI battery.charge.restart "00"
> VAR APC-8000RMXLI battery.date "07/01/06"
> VAR APC-8000RMXLI battery.packs "001"
> VAR APC-8000RMXLI battery.packs.bad "000"
> VAR APC-8000RMXLI battery.runtime "1500"
> VAR APC-8000RMXLI battery.runtime.low "120"
> VAR APC-8000RMXLI battery.voltage "217.0"
> VAR APC-8000RMXLI battery.voltage.nominal "192"
> VAR APC-8000RMXLI driver.name "apcsmart"
> VAR APC-8000RMXLI driver.parameter.port "/dev/ttyS0"
> VAR APC-8000RMXLI driver.version "2.0.3"
> VAR APC-8000RMXLI driver.version.internal "1.99.7"
> VAR APC-8000RMXLI input.frequency "50.05"
> VAR APC-8000RMXLI input.quality "FF"
> VAR APC-8000RMXLI input.sensitivity "A"
> VAR APC-8000RMXLI input.transfer.high "253"
> VAR APC-8000RMXLI input.transfer.low "161"
> VAR APC-8000RMXLI input.transfer.reason "S"
> VAR APC-8000RMXLI input.voltage "244.8"
> VAR APC-8000RMXLI input.voltage.maximum "244.8"
> VAR APC-8000RMXLI input.voltage.minimum "240.4"
> VAR APC-8000RMXLI output.current "12.72"
> VAR APC-8000RMXLI output.voltage "231.6"
> VAR APC-8000RMXLI output.voltage.target.battery "230"
> VAR APC-8000RMXLI ups.delay.shutdown "020"
> VAR APC-8000RMXLI ups.delay.start "000"
> VAR APC-8000RMXLI ups.display.language "E"
> VAR APC-8000RMXLI ups.firmware "477.15.W"
> VAR APC-8000RMXLI ups.id "UPS_IDEN"
> VAR APC-8000RMXLI ups.load "042.0"
> VAR APC-8000RMXLI ups.mfr "APC"
> VAR APC-8000RMXLI ups.mfr.date "07/01/06"
> VAR APC-8000RMXLI ups.model "Smart-UPS RT 8000 XL    "
> VAR APC-8000RMXLI ups.serial "NS0627025684  "
> VAR APC-8000RMXLI ups.status "OL"
> VAR APC-8000RMXLI ups.temperature "027.4"
> VAR APC-8000RMXLI ups.test.interval "1209600"
> VAR APC-8000RMXLI ups.test.result "NO"
> END LIST VAR APC-8000RMXLI

Arnaud Quette
--
Linux / Unix Expert - MGE UPS SYSTEMS - R&D Dpt
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://people.debian.org/~aquette/
OpenSource Developer - http://arnaud.quette.free.fr/




More information about the Nut-upsdev mailing list