Hi there,
I am using an old (really old) APC Smart-UPS 600. It worked fine
under apcupsd but when I tried NUT it did not work.
The error I was getting was:
sudo /lib/nut/apcsmart -DDD /dev/ttyS1
Network UPS Tools (version 2.0.4) - APC Smart protocol driver
Driver version 1.99.8, command table version 2.0
debug level is '3'
Attempting firmware lookup
Firmware: [D4]
Not found in table - trying normal method
APC - Attempting to find command set
APC - Parsing out command set
Unable to split APC version string
Bailing out
I tried running commands manually from minicom, and indeed, the UPS
was returning D6, D5, or D4 in response to "b" command. I still do not
understand the inconsistency, but I have observed these 3 strings at least.
I came up with the following patch to apcsmart.h:
--- nut-2.0.4.orig/drivers/apcsmart.h
+++ nut-2.0.4/drivers/apcsmart.h
@@ -254,6 +254,10 @@
/* APC600 */
{ "6QD", "79ABCDEFGKLMNOPQRSUVWXYZcefgjklmnopqrsuxz", 0 },
{ "6TI", "79ABCDEFGKLMNOPQRSUVWXYZcefgjklmnopqrsuxz", 0 },
+ /* Smart-UPS 600 */
+ { "D6", "789ABCEFGKLMNOPQRSUVWXYZ", 0 },
+ { "D5", "789ABCEFGKLMNOPQRSUVWXYZ", 0 },
+ { "D4", "789ABCEFGKLMNOPQRSUVWXYZ", 0 },
/* CS 350 */
{ "5.4.D", "\1ABPQRSUYbdfgjmnx9", 0 },
I understand that it is a clumsy way to make it work but it was the easiest
for me.
I am not sure how many more old Smart-UPS 600 are still in use and if it's
worth including into NUT.