[Nut-upsdev] new ups for database?

Peter Selinger selinger at mathstat.dal.ca
Sat Sep 23 23:16:37 UTC 2006


Hi Rob,

thanks for trying this. The patch I sent contained only a "stub"
driver. Its purpose is to see if you can read any of the device's
variables with upsc. Please post the output of "upsc
belkin at localhost".  It should list a number of variables whose names
start with the word "unmapped".

Before this driver will be actually useful, we need to change the
names of these variables so that NUT can understand them. This is
particularly important for the status variables (online, on battery,
etc). Also, we should try and map a few instant commands - at minimum,
we need an instant command to kill the power. 

-- Peter


spamwhole at gmail.com wrote:
> 
> Forgot to CC the list 
> 
> spamwhole at gmail.com writes: 
> 
> > Thanks for your help.  The program now works and connects as expected.  
> > 
> > Just one quick question though, upslog doesn't seem to have any output.  
> > Is this expected or should I have some details here?  
> > 
> > thanks  
> > 
> > Rob  
> > 
> > rmk bin # upslog -s belkin at localhost -l -
> > Network UPS Tools upslog 2.1.0
> > logging status of belkin at localhost to - (30s intervals)
> > 20060923 235602 NA NA NA [NA] NA NA
> > 20060923 235632 NA NA NA [NA] NA NA
> > 20060923 235702 NA NA NA [NA] NA NA  
> > 
> > 
> > Peter Selinger writes:  
> > 
> >> P.S. you may have to start the driver with "-a belkin" or "belkin"
> >> instead of "auto", or start the driver with "upsdrvctl", to make sure
> >> that the socket is named correctly. -- Peter  
> >> 
> >> spamwhole at gmail.com wrote:
> >>> 
> >>> Hi,   
> >>> 
> >>> I've checked all the permissions and they are all ok for root & nobody.  
> >>> I've even tried compiling it --with-user=root, but that doesn't make 
> >>> much different.  Running an strace on it doesn't bring up anything 
> >>> useful either.   
> >>> 
> >>> I've tried running it as root and using -u root. But I still get the 
> >>> same problem. I'm not sure if the 'Can't connect to UPS [belkin]' is the 
> >>> program trying to connect to a socket of some description, or if it's 
> >>> actually trying to connect to the UPS.   
> >>> 
> >>> thanks   
> >>> 
> >>> Rob   
> >>> 
> >>> rmk trunk # upsd -DD -u root
> >>> Network UPS Tools upsd 2.1.0
> >>> Can't connect to UPS [belkin] (belkin): No such file or directory
> >>> Synchronizing.................. giving up   
> >>> 
> >>> rmk trunk # strace upsd -DD -u root
> >>> munmap(0x2b0d2b273000, 4096)            = 0
> >>> socket(PF_FILE, SOCK_STREAM, 0)         = 5
> >>> connect(5, {sa_family=AF_FILE, path="newhidups"}, 110) = -1 ENOENT (No 
> >>> such file or directory)
> >>> close(5)                                = 0
> >>> write(2, "Can\'t connect to UPS [newhidups]"..., 72Can't connect to UPS 
> >>> [newhidups] (newhidups): No such file or directory   
> >>> 
> >>> 
> >>> Peter Selinger writes:   
> >>> 
> >>> > spamwhole at gmail.com wrote:
> >>> >> >> Hi,  >> >> Thanks for the very very quick patch. But, I can't seem 
> >>> to get things to >> work, unfortunately I'm not sure if the error is 
> >>> user induced ;-).  I get >> the following error:  >> >> ups # upsd
> >>> >> Network UPS Tools upsd 2.1.0
> >>> >> /var/state/ups is world readable
> >>> >> /usr/local/ups/etc/upsd.conf is world readable
> >>> >> Can't connect to UPS [belkin] (belkin): No such file or directory
> >>> >> /usr/local/ups/etc/upsd.users is world readable
> >>> >> Synchronizing.................. giving up > > This is probably a 
> >>> permissions problem. Try running upsd with "-u
> >>> > root".  > > Also make sure that upsd and newhidups are from the same 
> >>> NUT version.  > >> Here's my ups.conf:  >> >> [belkin]
> >>> >> port = /dev/usb/hiddev0             I've tried auto
> >>> >> driver = newhidups
> >>> >> vendorid = 0001 > > The "port" value is ignored; it can be any 
> >>> non-empty string. > >> Here's an strace of 'upsd':  >> >> [snip] >> >> 
> >>> Also, as a side note the make fell over when building the driver.  There 
> >>> was >> a normal 'gcc' line but with no source code to compile.  When I 
> >>> added >> mec-hid.c I I was able to continue/finish the compile. > > You 
> >>> could have also done "make depend" in drivers/. > > -- Peter > >> thanks 
> >>> >> >> Rob  >> >> >> Peter Selinger writes:  >> >> > Thanks for the info. 
> >>> Attached is the patch for an MEC subdriver stub.
> >>> >> > Plesae see if you can get this to work and read any info from the
> >>> >> > device via "upsd" and "upsc". Thanks, -- Peter >> > >> > 
> >>> spamwhole at gmail.com wrote:
> >>> >> >> >> >> Peter,  >> >> >> >> Please see below.  I've left the extra 
> >>> USB devices in there too, just in >> >> case.  >> >> >> >> thanks  >> >> 
> >>> >> >> Rob  >> >> >> >> rmk drivers # ./newhidups -DD -u root -x generic 
> >>> -x vendorid=0001 auto
> >>> >> >> Network UPS Tools: 0.28 USB communication driver 0.28 - core 0.30 
> >>> (2.1.0)  >> >> >> >> debug level is '2'
> >>> >> >> Checking device (0000/0000) (003/001)
> >>> >> >>  - VendorID: 0000
> >>> >> >>  - ProductID: 0000
> >>> >> >>  - Manufacturer: Linux 2.6.18-1 ohci_hcd
> >>> >> >>  - Product: OHCI Host Controller
> >>> >> >>  - Serial Number: 0000:00:02.0
> >>> >> >>  - Bus: 003
> >>> >> >> Trying to match device
> >>> >> >> Device does not match - skipping
> >>> >> >> Checking device (14AA/022B) (002/011)
> >>> >> >>  - VendorID: 14aa
> >>> >> >>  - ProductID: 022b
> >>> >> >>  - Manufacturer: Digital TV Receiver
> >>> >> >>  - Product: Digital TV Receiver
> >>> >> >>  - Serial Number: unknown
> >>> >> >>  - Bus: 002
> >>> >> >> Trying to match device
> >>> >> >> Device does not match - skipping
> >>> >> >> Checking device (0000/0000) (002/001)
> >>> >> >>  - VendorID: 0000
> >>> >> >>  - ProductID: 0000
> >>> >> >>  - Manufacturer: Linux 2.6.18-1 ehci_hcd
> >>> >> >>  - Product: EHCI Host Controller
> >>> >> >>  - Serial Number: 0000:05:06.2
> >>> >> >>  - Bus: 002
> >>> >> >> Trying to match device
> >>> >> >> Device does not match - skipping
> >>> >> >> Checking device (0000/0000) (004/001)
> >>> >> >>  - VendorID: 0000
> >>> >> >>  - ProductID: 0000
> >>> >> >>  - Manufacturer: Linux 2.6.18-1 uhci_hcd
> >>> >> >>  - Product: UHCI Host Controller
> >>> >> >>  - Serial Number: 0000:05:06.0
> >>> >> >>  - Bus: 004
> >>> >> >> Trying to match device
> >>> >> >> Device does not match - skipping
> >>> >> >> Checking device (0D3D/0001) (004/002)
> >>> >> >>  - VendorID: 0d3d
> >>> >> >>  - ProductID: 0001
> >>> >> >>  - Manufacturer: unknown
> >>> >> >>  - Product: USBPS2
> >>> >> >>  - Serial Number: unknown
> >>> >> >>  - Bus: 004
> >>> >> >> Trying to match device
> >>> >> >> Device does not match - skipping
> >>> >> >> Checking device (0000/0000) (001/001)
> >>> >> >>  - VendorID: 0000
> >>> >> >>  - ProductID: 0000
> >>> >> >>  - Manufacturer: Linux 2.6.18-1 ehci_hcd
> >>> >> >>  - Product: EHCI Host Controller
> >>> >> >>  - Serial Number: 0000:00:02.1
> >>> >> >>  - Bus: 001
> >>> >> >> Trying to match device
> >>> >> >> Device does not match - skipping
> >>> >> >> Checking device (0001/0000) (005/004)
> >>> >> >>  - VendorID: 0001
> >>> >> >>  - ProductID: 0000
> >>> >> >>  - Manufacturer: MEC
> >>> >> >>  - Product: MEC0002
> >>> >> >>  - Serial Number: unknown
> >>> >> >>  - Bus: 005
> >>> >> >> Trying to match device
> >>> >> >> Device matches
> >>> >> >> failed to claim USB device, trying 2 more time(s)...
> >>> >> >> detaching kernel driver from USB device...
> >>> >> >> trying again to claim USB device...
> >>> >> >> HID descriptor retrieved (Reportlen = 624)
> >>> >> >> Report descriptor retrieved (Reportlen = 624)
> >>> >> >> Found HID device
> >>> >> >> Report Descriptor size = 624
> >>> >> >> Detected a UPS: MEC/MEC0002
> >>> >> >> Using subdriver: GENERIC HID 0.1
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.FlowID, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.ConfigVoltage, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.ConfigFrequency, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.LowVoltageTransfer, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.HighVoltageTransfer, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.iManufacturer, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.iProduct, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.iSerialNumber, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.FlowID, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.ConfigVoltage, Type: Feature
> >>> >> >> Can't retrieve Report 1 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.ConfigFrequency, Type: Feature
> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.ConfigApparentPower, Type: Feature
> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.ConfigActivePower, Type: Feature
> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.DelayBeforeStartup, Type: Feature
> >>> >> >> Can't retrieve Report 2 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.Flow.DelayBeforeShutdown, Type: Feature
> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.BatterySystem.BatterySystemID, Type: Feature
> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.BatterySystem.PresentStatus.Used, Type: Feature
> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.BatterySystem.PresentStatus.Good, Type: Feature
> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.BatterySystem.Voltage, Type: Feature
> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.BatterySystem.Temperature, Type: Feature
> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.BatterySystem.Test, Type: Input
> >>> >> >> Can't retrieve Report 3 (-32/32): Broken pipe
> >>> >> >> Path: 00860004.BatterySystem.Test, Type: Feature
> >>> >> >> Can't find object 00860004.PowerConverter.PowerConverterID
> >>> >> >> Path: 00860004.PowerConverter.PowerConverterID, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Input.InputID
> >>> >> >> Path: 00860004.PowerConverter.Input.InputID, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Input.FlowID
> >>> >> >> Path: 00860004.PowerConverter.Input.FlowID, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Input.PresentStatus.Good
> >>> >> >> Path: 00860004.PowerConverter.Input.PresentStatus.Good, Type: 
> >>> Input
> >>> >> >> Can't find object 00860004.PowerConverter.Input.Voltage
> >>> >> >> Path: 00860004.PowerConverter.Input.Voltage, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Input.Frequency
> >>> >> >> Path: 00860004.PowerConverter.Input.Frequency, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Output.OutputID
> >>> >> >> Path: 00860004.PowerConverter.Output.OutputID, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Output.FlowID
> >>> >> >> Path: 00860004.PowerConverter.Output.FlowID, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Output.Voltage
> >>> >> >> Path: 00860004.PowerConverter.Output.Voltage, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Output.Frequency
> >>> >> >> Path: 00860004.PowerConverter.Output.Frequency, Type: Input
> >>> >> >> Can't find object 00860004.PowerConverter.Output.PercentLoad
> >>> >> >> Path: 00860004.PowerConverter.Output.PercentLoad, Type: Input
> >>> >> >> Can't find object 
> >>> 00860004.PowerConverter.Output.PresentStatus.Overload
> >>> >> >> Path: 00860004.PowerConverter.Output.PresentStatus.Overload, Type: 
> >>> Input
> >>> >> >> Can't find object 
> >>> 00860004.PowerConverter.Output.PresentStatus.Boost
> >>> >> >> Path: 00860004.PowerConverter.Output.PresentStatus.Boost, Type: 
> >>> Input
> >>> >> >> Can't find object 
> >>> 00860004.PowerConverter.Output.PresentStatus.Buck
> >>> >> >> Path: 00860004.PowerConverter.Output.PresentStatus.Buck, Type: 
> >>> Input
> >>> >> >> upsdrv_updateinfo...
> >>> >> >> dstate_init: sock /var/state/ups/newhidups-auto open on fd 5
> >>> >> >> upsdrv_updateinfo...
> >>> >> >> Waiting for notifications...
> >>> >> >> upsdrv_updateinfo...
> >>> >> >> Waiting for notifications...
> >>> >> >> Signal 2: exiting
> >>> >> >> Closing device
> >>> >> >> rmk drivers #  >> >> >> >> >> >> Peter Selinger writes:  >> >> >> 
> >>> >> > Rob and Dave, >> >> > >> >> > that device looks like it is using an 
> >>> illegal vendor id, "0001". It
> >>> >> >> > also looks like it is made by MEC, not Belkin (probably sold 
> >>> under
> >>> >> >> > license).  >> >> > >> >> > We might be able to support its USB 
> >>> interface. To find out more,
> >>> >> >> > please do the following: >> >> > >> >> > * get the latest 
> >>> development version of NUT from SVN. You can follow
> >>> >> >> >   the instructions at http://www.networkupstools.org/source.html 
> >>> under
> >>> >> >> >   "Development tree" to get it. >> >> > >> >> > * post the 
> >>> output of >> >> > >> >> >    drivers/newhidups -DD -u root -x generic -x 
> >>> vendorid=0001 auto >> >> > >> >> >   from this newest NUT version. >> >> 
> >>> > >> >> > This should output a bunch of debugging data, and then go into 
> >>> an
> >>> >> >> > infinite loop waiting for data. You can do "Ctrl-C" to kill the 
> >>> driver
> >>> >> >> > (it will not do anything useful at this point). >> >> > >> >> > 
> >>> -- Peter >> >> > >> >> > spamwhole at gmail.com wrote:
> >>> >> >> >> >> >> >> Hi,  >> >> >> >> >> >> I have the same device, a 
> >>> F6H500ukUNV, it has both RS-232 and USB.  >> >> >> >> >> >> url:
> >>> >> >> >> 
> >>> http://catalog.belkin.com/IWCatProductPage.process?Product_Id=201050  >> 
> >>> >> >> >> >> >> >> >> >> The details I have from my system are below.  If 
> >>> you would like further >> >> >> informatinon, or a more verbose lsusb 
> >>> please let me know.  >> >> >> >> >> >> thanks  >> >> >> >> >> >> Rob  >> 
> >>> >> >> >> >> >> dmesg:
> >>> >> >> >> hiddev96: USB HID v1.00 Device [MEC MEC0002] on 
> >>> usb-0000:05:06.1-2  >> >> >> >> >> >> lsusb:
> >>> >> >> >> Bus 005 Device 004: ID 0001:0000 Fry's Electronics  >> >> >> >> 
> >>> >> >> cat /proc/bus/usb/device:
> >>> >> >> >> T:  Bus=05 Lev=01 Prnt=01 Port=01 Cnt=01 Dev#=  4 Spd=1.5 MxCh= 
> >>> 0
> >>> >> >> >> D:  Ver= 1.00 Cls=00(>ifc ) Sub=00 Prot=00 MxPS= 8 #Cfgs=  1
> >>> >> >> >> P:  Vendor=0001 ProdID=0000 Rev= 1.00
> >>> >> >> >> S:  Manufacturer=MEC
> >>> >> >> >> S:  Product=MEC0002
> >>> >> >> >> C:* #Ifs= 1 Cfg#= 1 Atr=80 MxPwr=100mA
> >>> >> >> >> I:  If#= 0 Alt= 0 #EPs= 1 Cls=03(HID  ) Sub=00 Prot=00 
> >>> Driver=usbhid
> >>> >> >> >> E:  Ad=81(I) Atr=03(Int.) MxPS=   8 Ivl=10ms  >> >> >> >> >> >> 
> >>> >
> >>> >> >> >> >Hi Dave, >> >> >> >
> >>> >> >> >> >nothing in the outputs you sent looks like any Belkin device 
> >>> is
> >>> >> >> >> >present. Are you sure it is attached to your computer? You 
> >>> should have
> >>> >> >> >> >something like this in /proc/bus/usb/devices: >> >> >> >
> >>> >> >> >> >T:  Bus=04 Lev=01 Prnt=01 Port=00 Cnt=01 Dev#=  3 Spd=1.5 
> >>> MxCh= 0
> >>> >> >> >> >D:  Ver= 1.10 Cls=00(>ifc ) Sub=00 Prot=00 MxPS= 8 #Cfgs=  1
> >>> >> >> >> >P:  Vendor=050d ProdID=0980 Rev= 0.06
> >>> >> >> >> >S:  Manufacturer=       >> >> >> >S:  Product=UPS
> >>> >> >> >> >C:* #Ifs= 1 Cfg#= 1 Atr=c0 MxPwr= 20mA
> >>> >> >> >> >I:  If#= 0 Alt= 0 #EPs= 1 Cls=03(HID  ) Sub=00 Prot=00 
> >>> Driver=usbhid
> >>> >> >> >> >E:  Ad=81(I) Atr=03(Int.) MxPS=   8 Ivl=248ms >> >> >> >
> >>> >> >> >> >Note "Vendor=050d", which is Belkin's vendor ID.  >> >> >> >
> >>> >> >> >> >The output from newhidups does not show a 050d/XXXX device 
> >>> either.  >> >> >> >
> >>> >> >> >> >-- Peter >> >> >> >
> >>> >> >> >> >meherenow at darkglobe.org wrote:
> >>> >> >> >> >> >> >> >> >> I have a Belkin F6H500ukUNV ups that I am 
> >>> attempting to get working =20
> >>> >> >> >> >> under nut, however it
> >>> >> >> >> >> does not appear to be detected by nut, I'm assuming that I 
> >>> need to =20
> >>> >> >> >> >> feed some information
> >>> >> >> >> >> back to you guys to get it included in the database 
> >>> somwhere. >> >> >> >> >> >> >> >> I've included (what I can think might 
> >>> be) the relivant outputs. Please >=20
> >>> >> >> >> >> let me know if you
> >>> >> >> >> >> require anything else. >> >> >> >> >> >> >> >> dmesg output
> >>> >> >> >> >> /sbin/newhidsups output
> >>> >> >> >> >> ll /dev/usb*
> >>> >> >> >> >> cat /proc/bus/usb/devices >> >> >> >> >> >> >> >> p.s. I 
> >>> tried chmodding /dev/usb<blah> 777 just incase it was a =20
> >>> >> >> >> >> permissions problem, but
> >>> >> >> >> >> that didn't help either. >> >> >> >> >> >> >> >> Many 
> >>> thanks. >> >> >> >> >> >> >> >> 
> >>> ###########################################################
> >>> >> >> >> >> dmesg output when connecting the ups >> >> >> >> >> >> >> >> 
> >>> usb 2-1: new low speed USB device using uhci_hcd and address 2
> >>> >> >> >> >> PM: Adding info for usb:2-1
> >>> >> >> >> >> PM: Adding info for No Bus:usbdev2.2_ep00
> >>> >> >> >> >> usb 2-1: configuration #1 chosen from 1 choice
> >>> >> >> >> >> PM: Adding info for usb:2-1:1.0
> >>> >> >> >> >> hiddev96: USB HID v1.00 Device [MEC MEC0002] on 
> >>> usb-0000:00:10.1-1
> >>> >> >> >> >> PM: Adding info for No Bus:usbdev2.2_ep81 >> >> >> >> >> >> 
> >>> _______________________________________________
> >>> >> >> >> Nut-upsdev mailing list
> >>> >> >> >> Nut-upsdev at lists.alioth.debian.org
> >>> >> >> >> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev >> 
> >>> >> >> >> >> >  >> >> >> >  >> >   
> >>> 
> >> 
> 
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at lists.alioth.debian.org
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
> 