[Nut-upsdev] Tripplite OMNI1000LCD Watchdog
Arjen de Korte
nut+devel at de-korte.org
Wed Dec 12 20:25:23 UTC 2007
Thomas Golding wrote:
> My Apologies,
>
> here's the output of: usbhid-ups -DD -a omni1000lcd
Thanks!
> debug level is '2'
> upsdrv_initups...
> Checking device (09AE/2005) (3/5)
> - VendorID: 09ae
> - ProductID: 2005
> - Manufacturer: Tripp Lite
> - Product: TRIPP LITE UPS
> - Serial Number: 692195 A
> - Bus: 3
> Trying to match device
> Device matches
> Warning: two different HID descriptors retrieved (Reportlen = 459 vs. 618)
Hmmm, this is probably right, but does raise some concern.
> HID descriptor length 618
> Report Descriptor size = 618
> Using subdriver: TrippLite HID 0.2 (experimental)
[...]
> Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a,
> Offset: 0, Size: 8, Value: 24.000000
This most likely is wrong. See the problems with the AVR 550U we had a
couple of days ago, where reading this string descriptor confuses the
heck out of the UPS, to the point where it just shuts down without
warning. I think we better not read this.
[...]
> Can't retrieve Report 154: Broken pipe
> Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID: 0x9a, Offset: 0,
> Size: 32
That's probably OK.
> Can't retrieve Report 49: Value too large for defined data type
> Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x31, Offset: 0,
> Size: 8
[...]
> Can't retrieve Report 49: Value too large for defined data type
> HIDGetDataValue: Value too large for defined data type
> Can't initialize data from HID UPS
It's not a problem that we can't read this value, we can also use
'UPS.PowerConverter.Input.Voltage' here, so we don't loose anything by
just ignoring this. This seems to be the only
> I'll attempt the quick fix you mentioned so I can test the watchdog stuff.
Good. I patched the version in the trunk too, so you can check that out
as well. If all works, could you run
upsc <ups>
and post the output here, so that we can check if everything reported by
the UPS is also used?
Best regards, Arjen
More information about the Nut-upsdev