[Nut-upsdev] Re: [Nut-upsuser] Ablerex 625L USB version
Alexander I. Gordeev
lasaine at lvk.cs.msu.su
Tue Feb 6 09:15:24 CET 2007
On Sat, 03 Feb 2007 01:27:11 +0300, Alexander I. Gordeev <lasaine at lvk.cs.msu.su> wrote:
>> It does not matter which version we use as both work for me,
>> now. We just need to implement a few more commands into your code,
>> if we use that, and work out how to implement the code that sends
>> data to the UPS, ie the S<n>, S<n>R<m> and T<n> commands. I also
>> want to implement the TL, C and CT commands, but I whilst I can see
>> the reaction to these it is a little difficult to work out the code to use.
>
> I'll try to figure it out. usbsnoop will help me :)
>
As I promised, I've tried usbsnoop on the Windows driver last weekend.
This is the updated list of _string_ descriptors (type = 3) to use:
0x3 Q1
0x4 T
0x5 TL
0x6 T<n> (don't know how to pass the parameter)
0x7 Q
0xb CT
0xc I
0xd F
0x68 and 0x69 both cause shutdown after an undefined interval :)
These are results of reverse-engineering, my own UPS doesn't
perform all things right. For example, T* commands make it doing
test but only for 1-2 seconds. Shutdown time varies from 17 to 40
seconds.
I've solved also the majority of problems I had earlier, I'll write
about these issues a bit later, since the solutions could vary.
--