[Nut-upsdev] Re: [Nut-upsuser] Network UPS Tools version 2.0.5
released
Niels Baggesen
nba at users.sourceforge.net
Wed Jan 17 15:32:58 CET 2007
On Wed, Jan 17, 2007 at 10:18:21AM +0000, George Ross wrote:
> > Network UPS Tools version 2.0.5 has been released.
>
> There is some breakage in the status page's reporting of SNMP cards, which
> seems to me to be snmp-ups's fault. Input, output and load all show as
> "0.0 Not supported Not supported" for the single-phase Smart-UPS 3000 RM
> that I'm testing this out on.
>
> This seems to be because the driver is reporting 0.0 for the L1-L2 values,
> even though it's a single-phase UPS, so the status page tries to use them.
> That's where the "0.0" in the report comes from. However, the driver
> doesn't provide any L2-L3 or L3-L1 values, and that's where the two "Not
> supported" come from.
What variant of snmp-ups is this (what mib)?
I have a major update to snmp-ups in the works (actually I had forgotten
that I had not committed it to the trunk) that I will commit shortly,
which updates the IETF and PW mib variants (which are the one that I can
test) and it allows all data-elements to be made conditional on the
number of input or output phases.
/Niels
--
Niels Baggesen - @home - Århus - Denmark - nba at users.sourceforge.net
The purpose of computing is insight, not numbers --- R W Hamming
More information about the Nut-upsdev