[Nut-upsdev] Fenton UPS driver -- unknown UPS report
Daniel Pittman
daniel at rimspace.net
Sun Jan 21 03:48:51 CET 2007
"Carlos Rodrigues" <carlos.efr at mail.telepac.pt> writes:
> On 1/20/07, Daniel Pittman <daniel at rimspace.net> wrote:
[...]
>> The device has 2 x 12v batteries in series to provide 24 volt
>> internal operation. NUT still sees the voltage as off by a factor of
>> ten, apparently.
>
> In this case it looks like a factor of ten, but on 36 and 96V UPSes it
> isn't. So those 2.4V aren't really 24V.
OK. That seems strange to me but hey -- this is hardware. It almost
always seems to do crazy strange things. ;)
[...]
> Could you try it with the attached patch applied? It should give
> better results, however, I would still need to know the voltage
> reported by the UPS when it switches to low battery (I'm assuming the
> UPS is at 100% in those tests, right?).
OK, with the patch applied and full batteries I get this trace from
starting the driver, and from a upsc query. Low battery is apparently
2.0 volts, from this Q1 result at the switch over:
Asking for UPS status ("Q1" command)...
UPS status: 000.0 000.0 240.0 038 00.0 2.00 32.0 10000001
Asking for UPS status ("Q1" command)...
UPS status: 000.0 000.0 241.0 038 00.0 2.00 32.0 11000000
That was also at the 40 percent mark on the battery capacity guide,
though I didn't monitor how much further runtime the battery had.
One other issue: the 27.0 temperature reads 37.9 or 38.2 on the LCD
display. They could be driven from different sources, I guess.
At least the 38% load on the LCD agrees with the reports from the serial
port. The input and output voltages also agree.
Regards,
Daniel
Carlos Rodrigues (c) 2003-2006
debug level is '3'
Starting UPS detection process...
Attempting to detect the UPS...
Sending "Q1" command...
"Q1" command successful.
[... repeated 5 times, as expected ...]
0 out of 5 detection attempts failed (minimum failures: 2).
Asking for UPS information ("I" command)...
UPS information: M+H SMK-800 2000 V6.2
Megatec protocol UPS detected [M+H SMK-800 2000 V6.2].
Asking for UPS power ratings ("F" command)...
UPS power ratings: 240.0 004 024.0 50.0
Asking for UPS status ("Q1" command)...
UPS status: 252.0 252.0 253.0 038 49.9 2.40 27.0 00000000
24.0V battery, interval [1.7V, 2.4V].
Done setting up the UPS.
Asking for UPS status ("Q1" command)...
UPS status: 252.0 252.0 252.0 038 49.9 2.40 27.0 00000000
battery.charge: 100.0
battery.voltage: 2.40
battery.voltage.nominal: 24.0
driver.name: megatec
driver.parameter.port: /dev/ttyS0
driver.version: 2.0.5
driver.version.internal: 1.5
input.frequency: 50.0
input.voltage: 253.0
input.voltage.fault: 253.0
input.voltage.maximum: 253.0
input.voltage.minimum: 252.0
output.voltage: 252.0
output.voltage.nominal: 240.0
ups.beeper.status: disabled
ups.delay.shutdown: 0
ups.delay.start: 2
ups.load: 38.0
ups.mfr: M+H
ups.model: SMK-800 2000 V6.2
ups.serial: unknown
ups.status: OL
ups.temperature: 27.0
--