[Nut-upsdev] Best Ferrups reporting uptime in minutes, not seconds

Charles Lepple clepple at gmail.com
Tue Jun 17 14:58:50 UTC 2008


On Tue, Jun 17, 2008 at 10:36 AM, Chris Adams <cmadams at hiwaay.net> wrote:
> Once upon a time, Charles Lepple <clepple at gmail.com> said:
>> On Fri, Jun 13, 2008 at 3:11 PM, Chris Adams <cmadams at hiwaay.net> wrote:
>> > I had a power hiccup yesterday and a server connected to a Best Ferrups
>> > 18KVA shutdown.  The problem is that the UPS is reporting remaining
>> > runtime in minutes but nut treats it as seconds (so nut thought it only
>> > had 46 seconds left).
>>
>> The patch looks good at first glance, but by default, NUT should not
>> use the runtime estimate to initiate a shutdown.
>>
>> Are you using upssched? Any special parameters to the driver?
>>
>> Otherwise, NUT will shut down when the UPS signals LB (low battery),
>> which is a unit-less boolean value.
>
> No, I'm not using upssched.  I wasn't sure exactly how nut decided when
> to shut down (maybe a gap in the documentation or a gap in my reading).
> Here's what I got in my log:
>
> Jun 12 17:05:10 spider upsmon[27383]: UPS best at localhost on battery
> Jun 12 17:05:10 spider upsmon[27383]: UPS best at localhost battery is low
> Jun 12 17:05:10 spider upsd[27379]: Client monuser at 127.0.0.1 set FSD on UPS [best]
> Jun 12 17:05:10 spider upsmon[27383]: Executing automatic power-fail shutdown
> Jun 12 17:05:10 spider upsmon[27383]: Auto logout and shutdown proceeding
> Jun 12 17:05:20 spider upsd[27379]: Signal 15: exiting
>
> The UPS does have old batteries (we're getting them replaced), but it
> still is reporting 46 minutes of runtime, so I didn't expect that it
> would have instantly reported low battery.

Rob's explanation most likely applies here.

As for the patch, did you verify the 46 minutes versus seconds with
another program?

-- 
- Charles Lepple