[Nut-upsdev] APC SmartUPS 750 (SUA750) missing ambient data with usbhid-ups

Ric Anderson ric at Opus1.COM
Sun Sep 21 04:40:15 UTC 2008


That change did the trick.

Thanks,
Ric

Arjen de Korte wrote:
> Citeren "Ric Anderson" <ric at Opus1.COM>:
> 
>> Running the SVN version (USB driver.version: 2.3.0-1528) adds
>>    ambient.humidity: 29.2
>>    ambient.temperature: -4310085730494.6
>> to the upsc output.  The serial port driver on 2.2.2 says
>>    ambient.humidity: 029.2
>>    ambient.temperature: 29.21
>> which is correct based on temp(c)/humidity(%) data I get from a table
>> top instrument.  So there is progress, but the USB temperature is a
>> tad off :-)
>>
>> Any debug info I can gather to help with this?
> 
> I'm sorry, I messed up. The kelvin_celsius_conversion function returns a 
> pointer to a string, so it should be
> 
> { "ambient.temperature", 0, 0, 
> "UPS.APCEnvironment.APCProbe1.Temperature", NULL, "%s", 0, 
> kelvin_celsius_conversion },
> 
> I'll fix this in SVN later today.
> 
> Best regards, Arjen