[Nut-upsdev] Findings of dual APC UPS sensor attachments
Arnaud Quette
aquette.dev at gmail.com
Fri May 15 20:05:57 UTC 2009
2009/5/7 Steffen Plotner <swplotner at amherst.edu>
> Hi,
>
Hi Stephen,
> We have several APC Smart UPSes (serial port/apcsmart) with the APC
> Temp/Humidity sensor cards (AP9612TH). The sensor cards have 2 plugs for 2
> separate sensors. So far, we have only used one of the sensors in
> conjunction with the apcsmart module from nut. This has been working great.
> Example output:
>
> [nut at nut]# upsc APC11
> ambient.humidity: 037.2
> ambient.humidity.alarm.maximum: NO,NO
> ambient.humidity.alarm.minimum: NO,NO
> ambient.temperature: 21.08
> ambient.temperature.alarm.maximum: NO,NO
> ambient.temperature.alarm.minimum: NO,NO
>
> We thought of utilizing the second sensor port and have not been able to
> determine how to read the values of the second port.
>
> Looking at the source code of apcsmart we noticed that the following
> characters are sent to the UPS to retrieve the current data: the letter 't'
> for temperature and the letter 'h' for humidity.
>
> One of our co-workers decided to use the Windows based software from APC
> and showed me that he can read both sensors fine. Ok, so we fired up from
> sysinternals the portmon tool to study what is happening on the serial port
> and we find the following:
>
> The upper case letter 'T' produces 2 values:
> 21.08,20.09
>
> The upper case letter 'H' produces 2 values:
> 037.2,034.0
>
> If sensor 1 is not plugged in and sensor 2 is, then the output can look
> like:
> ,034.3
>
> I have 2 questions:
>
> 1. could the web page *
> http://www.networkupstools.org/protocols/apcsmart.html*<http://www.networkupstools.org/protocols/apcsmart.html>be updated to include this finding?
>
> 2. could we modify the source code to accommodate this?
>
> In regards to the software, there are some issues. By default we still have
> to query for the old values so that the above output is maintained. Maybe a
> config switch (man apcsmart: extra arguments: multisensor:1 and default to
> 0) would specifically allow the admin to enable the dual values, then the
> output might look like:
>
> ambient.humdity1: x.x
> ambient.humidty2: x.x
> ambient.temperature1: x.x
> ambient.temperatuer2: x.x
>
> I am unclear currently about the alarm.min and max values what exactly does
> NO,NO mean? Is that referring by chance to the 2 possible sensors?
>
> I am willing to work on the source code - unless some else already knows
> and wants to implement this feature… I would like have to have feed back in
> particularly about how we should go about implementing the above (i.e. is
> that in line with the current project, for example).
>
first, thanks for your mail and investigations.
we sadly lack an APC maintainer, which explains the lack of answer and
evolution of this driver.
if you're willing to work on implementing your findings, you're welcome.
I, and maybe others, will be glad to help you.
on my side, I'll check for the protocol update, possibly also using:
http://www.apcupsd.org/manual/APC_smart_protocol.html
if you need directions to start, tell me so.
cheers,
Arnaud
--
Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/