Citeren Marco Chiappero <marco op absence.it>:

> I'm sorry, I'm a bit tired and I didn't read carefully this part, so  
> please forget the previous message. So, connected mode only,  
> one_ups-one_driver, same configuration options from the previous  
> code? Ok?

More or less, yes. In order to limit the number of variables that need  
to be set, I would limit the configuration to LOCAL only and provide  
some sensible defaults for the shutdown delay and shutdown timer  
however. By explicitly setting these in the driver, this will make  
helping people setting this up easier (otherwise it would require  
setting up both the NMC and NUT).

Did you already try to connect multiple drivers yet? The NMC I'm using  
(66102 / GA) seems to allow only a single TCP connected subscription  
from any single IP. So if a driver is already connected, starting  
another one will make the NMC disconnect the others that are connected  
from the same IP. While this makes perfect sense for machines that use  
an NSM client to shut them down, this bites us if we want to monitor  
all outlets through multiple drivers in NUT.

This problem popped up when I added monitoring of the connection  
state. I added an automatic reconnection if the connection was lost.  
It took only a few seconds for three NSM connected drivers (connected  
to the main, outlet-1 and outlet-2) fighting for a subscription to  
confuse the NMC enough to trigger a reset. Ouch! :-)

Best regards, Arjen
-- 