[Nut-upsdev] You lost support of Belkin Universal UPS F6C1100-UNV
Cadence
cadence at rogers.com
Sun Oct 3 04:00:18 UTC 2010
Hi.
My Belkin UPS F6C1100-UNV works fine with megatec_usb version 1.6
(2.4.1). However, it doesn't work with 2.4.2 nor 2.4.3.
# /lib/nut/megatec_usb_old -D -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.1)
Serial-over-USB transport layer 0.10
debug level is '1'
Starting UPS detection process...
0 out of 5 detection attempts failed (minimum failures: 2).
Cancelling any pending shutdown or battery test.
Megatec protocol UPS detected.
24.0V battery, interval [19.4V, 27.4V].
Done setting up the UPS.
# /lib/nut/megatec_usb -D -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.3)
Serial-over-USB transport layer 0.10
0.000000 debug level is '1'
32.427474 Starting UPS detection process...
75.263380 ser_get_line: Device detached? (error -1: error sending
control message: Operation not permitted)
75.646279 Successfully reconnected
118.177387 ser_get_line: Device detached? (error -1: error sending
control message: Operation not permitted)
118.562286 Successfully reconnected
161.087388 ser_get_line: Device detached? (error -1: error sending
control message: Operation not permitted)
161.470290 Successfully reconnected
161.470319 Megatec protocol UPS not detected.
Below are the outputs with higher debugging level:
# /lib/nut/megatec_usb_old -DDDDDDDDDDDD -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.1)
Serial-over-USB transport layer 0.10
send_to_all: SETINFO driver.parameter.port "/dev/ttyS0"
debug level is '12'
Checking device (1D6B/0001) (006/001)
- VendorID: 1d6b
- ProductID: 0001
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 006
Trying to match device
Device does not match - skipping
Checking device (1D6B/0001) (005/001)
- VendorID: 1d6b
- ProductID: 0001
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 005
Trying to match device
Device does not match - skipping
Checking device (1D6B/0001) (004/001)
- VendorID: 1d6b
- ProductID: 0001
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 004
Trying to match device
Device does not match - skipping
Checking device (0665/5161) (003/002)
- VendorID: 0665
- ProductID: 5161
- Manufacturer: Cypress Semiconductor
- Product: USB to Serial
- Serial Number: unknown
- Bus: 003
Trying to match device
Device matches
none (-110)
DTR=1, RTS=0
Starting UPS detection process...
Asking for UPS information [I]...
none (-110)
I => FAILED [short read]
I detail: (1 bytes) => 49
Asking for UPS status [Q1]...
ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
ok
get_data_phoenix: got so far [(121.3 121.6 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
32 31
ok
get_data_phoenix: got so far [(121.3 121.6 121.6 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
32 31 2e 36 20 30 31 37 20 35
ok
get_data_phoenix: got so far [(121.3 121.6 121.6 017 59.9 27.2]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 32
ok
get_data_phoenix: got so far [(121.3 121.6 121.6 017 59.9 27.2 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 32 20 4e 2f 2e 41 20 30
30
ok
0]t_data_phoenix: got so far [(121.3 121.6 121.6 017 59.9 27.2 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 32 20 4e 2f 2e 41 20 30
30 30 30 31 30 30 31 0d 30
none (-110)
Q1 => OK [(121.3 121.6 121.6 017 59.9 27.2 N/.A 00001001]
Q1 VALUES => [121.3 121.6 121.6 17.0 59.9 27.2 0.0 00001001]
Asking for UPS status [Q1]...
none (-110)
ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30
ok
0]t_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30 30 30 31 30 30 31 0d 30
none (-110)
Q1 => OK [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.3 17.0 59.9 27.1 0.0 00001001]
Asking for UPS status [Q1]...
none (-110)
ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.6 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 36 20 30 31 37 20 35
ok
get_data_phoenix: got so far [(121.3 121.3 121.6 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.6 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30
ok
0]t_data_phoenix: got so far [(121.3 121.3 121.6 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30 30 30 31 30 30 31 0d 30
none (-110)
Q1 => OK [(121.3 121.3 121.6 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.6 17.0 59.9 27.1 0.0 00001001]
Asking for UPS status [Q1]...
none (-110)
ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30
ok
0]t_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30 30 30 31 30 30 31 0d 30
none (-110)
Q1 => OK [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.3 17.0 59.9 27.1 0.0 00001001]
Asking for UPS status [Q1]...
none (-110)
ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30
ok
0]t_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
30 30 30 31 30 30 31 0d 30
none (-110)
Q1 => OK [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.3 17.0 59.9 27.1 0.0 00001001]
0 out of 5 detection attempts failed (minimum failures: 2).
send_to_all: SETINFO ups.type "standby"
Cancelling any pending shutdown or battery test.
Asking for UPS information [I]...
I => FAILED [short read]
I detail: (1 bytes) => 49
send_to_all: SETINFO ups.mfr "unknown"
send_to_all: SETINFO ups.model "unknown"
Megatec protocol UPS detected.
send_to_all: SETINFO ups.serial "unknown"
Parameter [ignoreoff]: [false]
Asking for UPS power ratings [F]...
ok
get_data_phoenix: got so far [#120.0 0]
get_data_phoenix: (8 bytes) => 23 31 32 30 2e 30 20 30
ok
get_data_phoenix: got so far [#120.0 006 24.00]
get_data_phoenix: (16 bytes) => 23 31 32 30 2e 30 20 30 30 36 20 32 34 2e
30 30
ok
00]_data_phoenix: got so far [#120.0 006 24.00 60.0
get_data_phoenix: (24 bytes) => 23 31 32 30 2e 30 20 30 30 36 20 32 34 2e
30 30 20 36 30 2e 30 0d 30 30
none (-110)
F => OK [#120.0 006 24.00 60.0]
F VALUES => [120.0 6.0 24.0 60.0]
send_to_all: SETINFO battery.voltage.nominal "24.0"
send_to_all: SETINFO input.voltage.nominal "120.0"
send_to_all: SETINFO input.frequency.nominal "60.0"
24.0V battery, interval [19.4V, 27.4V].
send_to_all: SETINFO ups.delay.start "2"
send_to_all: SETINFO ups.delay.shutdown "0"
send_to_all: ADDCMD test.battery.start.deep
send_to_all: ADDCMD test.battery.start
send_to_all: ADDCMD test.battery.stop
send_to_all: ADDCMD shutdown.return
send_to_all: ADDCMD shutdown.stayoff
send_to_all: ADDCMD shutdown.stop
send_to_all: ADDCMD load.on
send_to_all: ADDCMD load.off
send_to_all: ADDCMD reset.input.minmax
send_to_all: ADDCMD reset.watchdog
send_to_all: ADDCMD beeper.toggle
Done setting up the UPS.
*************************************************************************************************
# /lib/nut/megatec_usb -DDDDDDDDDDDD -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.3)
Serial-over-USB transport layer 0.10
0.000000 send_to_all: SETINFO driver.parameter.port "/dev/ttyS0"
0.000120 debug level is '12'
0.372785 Checking device (1D6B/0001) (006/001)
0.372905 - VendorID: 1d6b
0.372920 - ProductID: 0001
0.372932 - Manufacturer: unknown
0.372945 - Product: unknown
0.372956 - Serial Number: unknown
0.372969 - Bus: 006
0.372980 Trying to match device
0.372999 Device does not match - skipping
0.373020 Checking device (1D6B/0001) (005/001)
0.373062 - VendorID: 1d6b
0.373074 - ProductID: 0001
0.373085 - Manufacturer: unknown
0.373097 - Product: unknown
0.373108 - Serial Number: unknown
0.373119 - Bus: 005
0.373130 Trying to match device
0.373145 Device does not match - skipping
0.373162 Checking device (1D6B/0001) (004/001)
0.373201 - VendorID: 1d6b
0.373214 - ProductID: 0001
0.373225 - Manufacturer: unknown
0.373237 - Product: unknown
0.373248 - Serial Number: unknown
0.373260 - Bus: 004
0.373271 Trying to match device
0.373285 Device does not match - skipping
0.373301 Checking device (0665/5161) (003/002)
0.382882 - VendorID: 0665
0.382903 - ProductID: 5161
0.382915 - Manufacturer: Cypress Semiconductor
0.382927 - Product: USB to Serial
0.382939 - Serial Number: unknown
0.382950 - Bus: 003
0.382961 Trying to match device
0.382976 Device matches
1.387897 libusb_get_interrupt: Connection timed out
1.387921 get_data_phoenix: got so far []
1.387943 get_data_phoenix: (8 bytes) => 00 00 00 00 00 00 00 00
2.389105 libusb_get_interrupt: Connection timed out
2.389159 get_data_phoenix: got so far []
2.389185 get_data_phoenix: (16 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
2.389200 00 00
3.389906 libusb_get_interrupt: Connection timed out
3.389947 get_data_phoenix: got so far []
3.389972 get_data_phoenix: (24 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
3.389992 00 00 00 00 00 00 00 00 00 00
4.390898 libusb_get_interrupt: Connection timed out
4.390944 get_data_phoenix: got so far []
4.390969 get_data_phoenix: (32 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
4.390993 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
5.391894 libusb_get_interrupt: Connection timed out
5.391919 get_data_phoenix: got so far []
5.391943 get_data_phoenix: (40 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
5.391971 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
5.391985 00
6.392894 libusb_get_interrupt: Connection timed out
6.392919 get_data_phoenix: got so far []
6.392942 get_data_phoenix: (48 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
6.392970 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
6.392988 00 00 00 00 00 00 00 00 00
7.393892 libusb_get_interrupt: Connection timed out
7.393915 get_data_phoenix: got so far []
7.393936 get_data_phoenix: (56 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
7.393963 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
7.393985 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
8.394897 libusb_get_interrupt: Connection timed out
8.394928 get_data_phoenix: got so far []
8.394952 get_data_phoenix: (64 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
8.394979 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
8.395006 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
9.395894 libusb_get_interrupt: Connection timed out
9.395918 get_data_phoenix: got so far []
9.395940 get_data_phoenix: (72 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
9.395967 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
9.395994 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
9.396013 00 00 00 00 00 00 00 00
10.397896 libusb_get_interrupt: Connection timed out
10.397924 get_data_phoenix: got so far []
10.397947 get_data_phoenix: (80 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
10.397974 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
10.398000 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
10.398023 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
11.399896 libusb_get_interrupt: Connection timed out
11.399924 get_data_phoenix: got so far []
11.399948 get_data_phoenix: (88 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
11.399976 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
11.400004 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
11.400032 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00
12.400906 libusb_get_interrupt: Connection timed out
12.400942 get_data_phoenix: got so far []
12.400967 get_data_phoenix: (96 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
12.400994 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
12.401021 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
12.401048 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
12.401065 00 00 00 00 00 00 00
13.402904 libusb_get_interrupt: Connection timed out
13.402945 get_data_phoenix: got so far []
13.402970 get_data_phoenix: (104 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
13.402998 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
13.403026 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
13.403055 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
13.403076 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
14.403901 libusb_get_interrupt: Connection timed out
14.403941 get_data_phoenix: got so far []
14.403966 get_data_phoenix: (112 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
14.403995 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
14.404023 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
14.404051 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
14.404078 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00
15.404896 libusb_get_interrupt: Connection timed out
15.404921 get_data_phoenix: got so far []
15.404944 get_data_phoenix: (120 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
15.404971 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
15.404998 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
15.405025 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
15.405052 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
15.405069 00 00 00 00 00 00
16.406898 libusb_get_interrupt: Connection timed out
16.406930 get_data_phoenix: got so far []
16.406953 get_data_phoenix: (128 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
16.406980 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
16.407006 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
16.407032 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
16.407058 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
16.407079 00 00 00 00 00 00 00 00 00 00 00 00 00 00
17.407907 libusb_get_interrupt: Connection timed out
17.407956 get_data_phoenix: got so far []
17.407981 get_data_phoenix: (136 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
17.408009 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
17.408035 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
17.408062 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
17.408089 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
17.408114 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00
18.409906 libusb_get_interrupt: Connection timed out
18.409955 get_data_phoenix: got so far []
18.409982 get_data_phoenix: (144 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
18.410010 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
18.410038 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
18.410066 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
18.410094 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
18.410121 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
18.410137 00 00 00 00 00
19.410905 libusb_get_interrupt: Connection timed out
19.410951 get_data_phoenix: got so far []
19.410976 get_data_phoenix: (152 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
19.411003 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
19.411029 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
19.411056 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
19.411083 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
19.411109 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
19.411130 00 00 00 00 00 00 00 00 00 00 00 00 00
20.411908 libusb_get_interrupt: Connection timed out
20.411959 get_data_phoenix: got so far []
20.411987 get_data_phoenix: (160 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
20.412013 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
20.412041 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
20.412067 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
20.412094 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
20.412120 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
20.412145 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00
21.412908 libusb_get_interrupt: Connection timed out
21.412956 get_data_phoenix: got so far []
21.412982 get_data_phoenix: (168 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
21.413010 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
21.413036 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
21.413063 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
21.413090 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
21.413116 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
21.413144 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
21.413160 00 00 00 00
22.413908 libusb_get_interrupt: Connection timed out
22.413958 get_data_phoenix: got so far []
22.413983 get_data_phoenix: (176 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
22.414012 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
22.414041 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
22.414068 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
22.414095 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
22.414124 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
22.414151 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
22.414172 00 00 00 00 00 00 00 00 00 00 00 00
23.414908 libusb_get_interrupt: Connection timed out
23.414956 get_data_phoenix: got so far []
23.414983 get_data_phoenix: (184 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
23.415011 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
23.415039 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
23.415066 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
23.415095 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
23.415122 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
23.415150 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
23.415175 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
24.415906 libusb_get_interrupt: Connection timed out
24.415956 get_data_phoenix: got so far []
24.415983 get_data_phoenix: (192 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
24.416011 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
24.416039 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
24.416067 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
24.416094 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
24.416122 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
24.416150 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
24.416177 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
24.416193 00 00 00
25.417892 libusb_get_interrupt: Connection timed out
25.417916 get_data_phoenix: got so far []
25.417939 get_data_phoenix: (200 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
25.417966 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
25.417994 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
25.418020 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
25.418047 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
25.418074 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
25.418101 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
25.418128 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
25.418149 00 00 00 00 00 00 00 00 00 00 00
26.418899 libusb_get_interrupt: Connection timed out
26.418934 get_data_phoenix: got so far []
26.418961 get_data_phoenix: (208 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
26.418989 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
26.419016 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
26.419044 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
26.419071 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
26.419099 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
26.419127 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
26.419155 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
26.419180 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
27.420901 libusb_get_interrupt: Connection timed out
27.420930 get_data_phoenix: got so far []
27.420955 get_data_phoenix: (216 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
27.420984 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421011 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421038 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421067 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421094 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421121 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421149 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421177 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
27.421192 00 00
28.422897 libusb_get_interrupt: Connection timed out
28.422925 get_data_phoenix: got so far []
28.422949 get_data_phoenix: (224 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
28.422978 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423006 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423033 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423061 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423088 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423115 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423143 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423170 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
28.423190 00 00 00 00 00 00 00 00 00 00
29.424897 libusb_get_interrupt: Connection timed out
29.424921 get_data_phoenix: got so far []
29.424944 get_data_phoenix: (232 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
29.424973 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425001 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425028 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425056 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425084 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425112 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425139 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425166 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
29.425191 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
30.425894 libusb_get_interrupt: Connection timed out
30.425917 get_data_phoenix: got so far []
30.425940 get_data_phoenix: (240 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
30.425967 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.425994 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426021 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426049 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426075 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426103 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426130 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426157 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426184 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
30.426199 00
31.426894 libusb_get_interrupt: Connection timed out
31.426918 get_data_phoenix: got so far []
31.426941 get_data_phoenix: (248 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
31.426968 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.426996 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427023 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427050 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427077 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427104 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427131 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427159 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427186 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
31.427204 00 00 00 00 00 00 00 00 00
32.427903 libusb_get_interrupt: Connection timed out
32.427948 get_data_phoenix: got so far []
32.427975 get_data_phoenix: (256 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
32.428004 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428032 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428060 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428089 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428116 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428145 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428173 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428201 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428230 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
32.428254 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
32.428268 get_data_phoenix: buffer too small
32.428288 DTR=1, RTS=0
32.428317 send_to_all: SETINFO device.type "ups"
32.428336 send_to_all: SETINFO driver.version "2.4.3"
32.428354 send_to_all: SETINFO driver.version.internal "1.6"
32.428373 send_to_all: SETINFO driver.name "megatec_usb"
32.428398 Starting UPS detection process...
32.428412 Asking for UPS information [I]...
33.428908 libusb_get_interrupt: Connection timed out
33.428940 get_data_phoenix: got so far []
33.428962 get_data_phoenix: (8 bytes) => 00 00 00 00 00 00 00 00
34.429897 libusb_get_interrupt: Connection timed out
34.429926 get_data_phoenix: got so far []
34.429949 get_data_phoenix: (16 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
34.429964 00 00
35.431895 libusb_get_interrupt: Connection timed out
35.431919 get_data_phoenix: got so far []
35.431941 get_data_phoenix: (24 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
35.431961 00 00 00 00 00 00 00 00 00 00
36.432894 libusb_get_interrupt: Connection timed out
36.432920 get_data_phoenix: got so far []
36.432943 get_data_phoenix: (32 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
36.432966 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
37.433898 libusb_get_interrupt: Connection timed out
...and so on.