[Nut-upsdev] usbhid-ups causing hang on boot with 2.6.35 - any ideas?
Arjen de Korte
nut+devel at de-korte.org
Fri Sep 3 08:49:27 UTC 2010
Citeren "David C. Rankin" <drankinatty op suddenlinkmail.com>:
> (Arjen - I apologize if you get two copies, I sent the first one to
> the old de-korte.org address)
That address isn't old, but the mailserver is configured to only
accept messages from the mailinglist server.
> Aug 30 20:31:03 archangel upsd[2295]: listening on 192.168.6.14 port 3493
> Aug 30 20:31:03 archangel upsd[2295]: listening on 127.0.0.1 port 3493
> Aug 30 20:31:03 archangel upsd[2295]: Can't connect to UPS
> [archangel_ups] (usbhid-ups-archangel_ups): No such file or directory
This means the driver isn't running (but you probably already knew that).
> Aug 30 20:31:03 archangel upsd[2296]: Startup successful
> Aug 30 20:31:03 archangel upsmon[2298]: Startup successful
> Aug 30 20:31:03 archangel upsmon[2300]: Login on UPS
> [archangel_ups op localhost] failed - got [ERR ACCESS-DENIED]
> Aug 30 20:31:03 archangel upsmon[2300]: Login on UPS
> [nirvana_ups op nirvana.3111skyline.com] failed - got [ERR ACCESS-DENIED]
The above two error messages indicate there is a problem with logging
into the server. You could run the server in debug mode, but my guess
is this has to do with either NUT being build with tcp-wrappers
support and you failed setting this up properly (see 'man 8 upsd') or
the credentials you're using are incorrect.
[...]
> Looks like some type of udev issue or kernel issue, but I
> thought I would check here to see if you guys have any more info on
> the problem. Anybody seen this behavior before?
This looks like the udev rules are incorrect. If memory serves, there
have been some changes in the syntax (BUS was changed to SUBSYSTEMS).
Other than that, there are no known issues.
Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)
More information about the Nut-upsdev
mailing list