Hi Al,
(FYI, I cc'ed the NUT developers list for info)
2011/6/30 Albert Chu <chu11 at llnl.gov>
> Hi Arnaud,
>
> On Tue, 2011-06-28 at 12:19 -0700, Arnaud Quette wrote:
> > Hi Al,
> >
> > 2011/6/28 Albert Chu <chu11 at llnl.gov>
> > On Tue, 2011-06-28 at 02:28 -0700, Arnaud Quette wrote:
> > (...)
> > > I'm *very* interested in!
> > > this could even serve as a simple example, shipped in the
> > examples/
> > > directory.
> >
> >
> >
> > Unfortunately, it will require knowledge of the IPMI
> > protocol/specification, which makes it difficult (and why I
> > probably
> > never bothered with an example).
> >
> > Everything is in the ipmi-fru and ipmi-sensors tools, however
> > I imagine
> > a lot of the options, permutations of things, IPMI spec
> > details, etc. is
> > what's making it confusing.
> >
> > Give me some time, and I'll try to "whittle" the ipmi-fru and
> > ipmi-sensors tools into a far simpler example that can give
> > you a basis
> > for what you're trying to accomplish.
> >
> > sure, thanks a lot for your much appreciated proposition.
> > since I have some hard deadlines, do you have any approximate idea on
> > when you'd be able to release this?
>
> Attached is a simplified ipmi-fru that you can hopefully use to extract
> the FRU information you seek. "gcc ipmi-fru-example.c -lfreeipmi" is
> all you need to do. I took out a lot of stuff, and there a number of
> special cases not handled. It may not work for all motherboards, but is
> a good place to start.
>
awesome, thanks a lot Al!
I'm starting to see the light, though I've not yet read the code
thoroughly...
I just have to check (maybe with libdetect) how to identify PSU, but I
already got the following data by modifying ipmi_fru_parse_open_device_id()
to specify a known PSU ID:
FRU Board Language: English
FRU Board Manufacturing Date/Time: 01/05/11 - 08:51:00
FRU Board Manufacturer: DELL
FRU Board Product Name: PWR SPLY,717W,RDNT
FRU Board Serial Number: CN179721130031
FRU Board Part Number: 0RN442A01
FRU Power Supply Overall Capacity: 717 Watts
FRU Power Supply Peak VA: 0 VA
FRU Power Supply Max Inrush Current: 0 Amps
FRU Power Supply Inrush Interval: 0 ms
FRU Power Supply Low End Input Voltage 1: 90000 mV
FRU Power Supply High End Input Voltage 1: 264000 mV
FRU Power Supply Low End Input Voltage 2: 0 mV
FRU Power Supply High End Input Voltage 2: 0 mV
FRU Power Supply Low End Acceptable Frequencey: 47 Hz
FRU Power Supply High End Acceptable Frequencey: 63 Hz
FRU Power Supply A/C Dropout Tolerance: 0 ms
FRU Power Supply Predictive Fail Support: No
FRU Power Supply Power Factor Correction Supported: No
FRU Power Supply AutoSwitch Supprt: Yes
FRU Power Supply Hot Swap Support: Yes
FRU Power Supply Peak Capacity: 0 Watts
FRU Power Supply Hold Up Time: 0 s
FRU Power Supply Voltage 1: 12V
FRU Power Supply Voltage 2: 12V
FRU Power Supply Total Combined Wattage: 0 Watts
> As for sensors, I figured you would probably want to use
> libipmimonitoring, since it's at a much higher level. I would suggest
> looking at the ipmimonitoring-sensors.c file.
>
indeed, that's what I understood.
as told above, I just got to check libdetect for PSU identification, then
everything should be alright.
Hopefully that's enough to get you going. LMK if you need some help
> deciphering the code more.
>
this should not be needed, but thanks for your kind proposition.
but you should probably publish this code in examples/, with a name like
"simple-ipmi-fru.c" or alike, and highlight this code sample a bit.
thanks again,
Arnaud
--
Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20110701/fe109a17/attachment-0001.html>
More information about the Nut-upsdev
mailing list