[Nut-upsdev] [nut-commits] svn commit r3104 - branches/apcsmart-dev/drivers
Michal Soltys
soltys at ziu.info
Wed Jun 29 14:26:16 UTC 2011
On 11-06-28 21:08, Arjen de Korte wrote:
> Citeren Michal Soltys <msoltyspl-guest at alioth.debian.org>:
>
>> @@ -417,10 +414,12 @@
>> if (flags & SER_CC) {
>> iset = IGN_CCCHARS;
>> aset = "";
>> + sec = 6; usec = 0;
>> }
>> if (flags & SER_CS) {
>> iset = IGN_CSCHARS;
>> aset = "";
>> + sec = 6; usec = 0;
>> }
>>
>> memset(buf, '\0', buflen);
>
> Please see the following comment on upsdrv_updateinfo from the
> new-drivers documentation:
>
> "Don't spent more than a couple of seconds in this function. Typically
> five (5) seconds is the maximum time allowed before you risk that the
> server declares the driver stale. If your UPS hardware requires a
> timeout period of several seconds before it answers, consider returning
> from this function after sending a command immediately and read the
> answer the next time it is called."
>
> It looks like you're setting a timeout of 6 seconds here, which puts
> your driver being declared stale by the server. Drivers are single
> threaded (like all of NUT at present) so hanging around this long, will
> mean that it won't respond to polls from the server in time.
>
> If these commands really take this long to process, you really should
> split this up in multiple invocations of upsdrv_updateinfo (so send the
> command, return and process the reply the next time you enter).
>
Those two commands happen only once before the actual loop is in effect,
during the initialization stage - in upsdrv_initinfo(). It's the only
place where such large delay is used. Note this is only the max possible
delay, the read will return as quickly as possible (each command ends
with LF) - in case of one of my models it takes roughly 3 seconds
("capability set" command, "command set" is faster) - so I wanted to be
on the safe side.
I persume the upper limit it's not a problem when upsdrv_initinfo() is
considered ?
More information about the Nut-upsdev