[Nut-upsdev] MGE MIB related bug
Kiss Gabor (Bitman)
kissg at ssg.ki.iif.hu
Mon Nov 14 12:58:11 UTC 2011
> > According to mge-mib.c (NUT 2.6.2) LB condition
> > is gained from variable .1.3.6.1.4.1.705.1.5.14.0 (i.e.
> > upsmgBatteryLowBattery.0).
> >
> > The test device of me does not set this variable to yes(1)
> > even if runtime drops below the preconfigured limit.
> > I complained about this at Schneider Electric.
> > They replied that low battery status is indicated by
> > .1.3.6.1.4.1.705.1.5.14.0 (upsmgBatteryLowCondition.0).
Original mail:
| When "upsmgConfigLowBatteryTime" is SET to 9999 and current
| "upsmgBatteryRemainingTime" is below 9999 second,
| "upsmgBatteryLowCondition" will have value 1, when UPS will be on battery
| => NOT "upsmgBatteryLowBattery", which is linked with
| "upsmgBatteryLowBatteryLevel" (i suppose, not tested)
|
| Now, for IETF MIB, "upsBatteryStatus" goes to value 3 when
| "upsmgBatteryLowCondition" goes to value 1
> copy/paste error: you probably meant 1.3.6.1.4.1.705.1.5.16.0
Sure. You are absolutely right. :)
I missed the number.
> That said, I've added and committed the above OID with the standard lowbatt
> mapping (1 = LB, 2 = <not LB>)
> Can you please test the trunk, r3318?
Thanks.
I'll do in a week or so.
Unfortunately at this moment I'm quite busy.
Regards
Gabor
--
E-mail = m-mail * c-mail ^ 2
More information about the Nut-upsdev