On Aug 31, 2012, at 5:26 PM, Petr Topiarz <topiarz at post.cz> wrote:
> Hi Charles,
> you're right, this is OpenBSD 5.1, I do not understand fully what you mean by the shutdown sequence. I make my cron read the upsc output and tell the system to shutdown if level is low. If the electricity supply is up again, my server automaticaly wakes up, if this is what you mean.
> Peter
>
Often people will either let upsmon send a shutdown command when the UPS reports a low battery, or they use upssched to do so after a certain length of time on battery. There are several different types of shutdown commands for an UPS, and the support for them is not always consistent.
>
>
> Dne 31.8.2012 23:15, Charles Lepple napsal(a):
>> On Aug 30, 2012, at 5:18 AM, Petr Topiarz wrote:
>>
>>> UPS - CYBERPOWER CPS DX600E
>>>
>>> upsc usb at localhost
>>> battery.charge: 100
>>> battery.charge.low: 10
>>> battery.charge.warning: 20
>>> battery.mfr.date: CPS
>>> battery.runtime: 1650
>>> battery.runtime.low: 300
>>> battery.type: PbAcid
>>> battery.voltage: 4.8
>>> battery.voltage.nominal: 12
>>> device.mfr: CPS
>>> device.model: DX600E
>>> device.type: ups
>>> driver.name: usbhid-ups
>>> driver.parameter.pollfreq: 30
>>> driver.parameter.pollinterval: 2
>>> driver.parameter.port: /dev/ugen0.00
>>> driver.version: 2.6.3-Unversioned directory
>>> driver.version.data: CyberPower HID 0.3
>>> driver.version.internal: 0.35
>>> input.transfer.high: 0
>>> input.transfer.low: 0
>>> input.voltage: 230.0
>>> input.voltage.nominal: 230
>>> output.voltage: 239.0
>>> ups.beeper.status: enabled
>>> ups.delay.shutdown: 20
>>> ups.delay.start: 30
>>> ups.load: 21
>>> ups.mfr: CPS
>>> ups.model: DX600E
>>> ups.productid: 0501
>>> ups.realpower.nominal: 360
>>> ups.status: OL
>>> ups.timer.shutdown: -60
>>> ups.timer.start: 0
>>> ups.vendorid: 0764
>> Which OS is this? Looks like *BSD or Solaris?
>>
>> Also, can you provide a few more details from this* list? In particular, it is helpful to know if the shutdown sequence works.
>>