Matt Schulte gimpyestrada at gmail.com
Tue Feb 14 17:46:59 UTC 2012


On Tue, Feb 14, 2012 at 2:42 AM, Arnaud Quette <aquette.dev at gmail.com> wrote:
> Hi Matt,
>
> 2012/2/13 Matt Schulte <gimpyestrada at gmail.com>:
>> Device manufacturer and name:
>> Tripp-Lite OmniSmart500
>>
>> upsc output:
>> matt at backup:/etc$ sudo upsc tripplite
>> battery.charge: 100
>> battery.test.status: Battery OK
>> battery.voltage: 14.56
>> battery.voltage.nominal: 12
>> device.mfr: Tripp Lite
>> device.model: OMNISMART500
>> device.type: ups
>> driver.name: tripplite_usb
>> driver.parameter.pollinterval: 2
>> driver.parameter.port: auto
>> driver.version: 2.4.3
>> driver.version.internal: 0.20
>> input.voltage: 108.60
>> input.voltage.nominal: 120
>> output.voltage: 113.0
>> ups.debug.load_banks: 0
>> ups.debug.V: 31 30 32 30 58 58 0d '1020XX.'
>> ups.delay.shutdown: 64
>> ups.firmware: F0966.A
>> ups.firmware.aux: protocol 2001
>> ups.mfr: Tripp Lite
>> ups.model: OMNISMART500
>> ups.power.nominal: 500
>> ups.productid: 0001
>> ups.status: OL
>> ups.vendorid: 09ae
>> matt at backup:/etc$
>>
>> shutdown sequence testing results:
>> Not sure exactly what you would like to see here, but after
>> configuring everything and pulling the plug the system shut down
>> correctly when the UPS dropped below 20%.
>
> we just need a confirmation as you did, plus the fact that the UPS was
> powered off in the end.
>
>> /etc/log/daemon.log:
>> Feb 13 10:11:47 backup upsmon[12058]: UPS tripplite at localhost battery is low
>> Feb 13 10:11:47 backup upsd[11649]: Client upsmon at 127.0.0.1 set FSD on UPS [trip
>> plite]
>> Feb 13 10:11:47 backup upsmon[12058]: Executing automatic power-fail shutdown
>> Feb 13 10:11:47 backup upsmon[12058]: Auto logout and shutdown proceeding
>>
>> link:
>> http://www.tripplite.com/en/products/model.cfm?txtModelID=21
>
> thanks for your report.
> I've just added an entry to the HCL.
> For the sake of completion, could you please also send upsrw and upscmd outputs?
>
Specifically what parameters do you want me to use when running upsrw
and upscmd?  Maybe this is what you are looking for?

matt at backup:~$ upscmd -l tripplite
Instant commands supported on UPS [tripplite]:

shutdown.return - Turn off the load and return when power is back

matt at backup:~$ upsrw tripplite
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 64

Matt Schulte



More information about the Nut-upsdev mailing list