2012/5/14 Ivan Kuznetsov <kia at solvo.ru>:
> Hello Arnaud
Hello Ivan,
> I can confirm that version 2.6.3 with the patch succeffully works with
> Socomec NetVision Web/SNMP adaptor.
ok, I've applied your original patch only (Ie "9" for ecomode) to the
trunk, r590.
thanks
> The adaptor shows the projected battery runtime
> (1.3.6.1.4.1.4555.1.1.1.1.2.3.0) only in 1 minute intervals and constantly
> returns -60 (-1 minute) when UPS is on line power. The "Low battery" flag is
> raised when runtime is last 1 min. It can be too little for some
> applications to shut down but I can't find an adjustment method.
>
> I'm still not know what is output status 8 (standby).
standby is another word for "offline" type UPS:
http://en.wikipedia.org/wiki/Uninterruptible_power_supply#Offline_.2F_standby
in your context, this may either be the type of the UPS, or a mode (as
for the ecomode) in which the UPS is running (Ie lower quality, but a
bit more efficient)
> 24.04.2012 17:59, Arnaud Quette пишет:
>>
>>
>> 2012/4/16 Ivan Kuznetsov <kia at solvo.ru <mailto:kia at solvo.ru>>
>>
>>
>> Hello
>>
>>
>> Hello Ivan,
>>
>> We have an Socomec Sicon Netys PR3000 UPS equipped with NetVision
>> Web/SNMP adaptor. I try to monitor the ups using snmp-ups driver and
>> netvision mibs set. The snmp-ups driver starts correctly and
>> connects to the UPS, upsd confirms it, but upsmon constantly shows
>> "No communication" error
>>
>> I think the cause is the SNMP adapter reports the UPS status as "ECO
>> mode" (snmpget .1.3.6.1.4.1.4555.1.1.1.1.4.1.__0 returns 9), but
>>
>> snmp-ups does not correctly process this. Here is output of
>> 'snmp-ups -a socomec -u nut -D':
>>
>> Network UPS Tools - Generic SNMP UPS driver 0.50 (2.6.1)
>> 0.000000 debug level is '1'
>> 0.000260 SNMP UPS driver : entering upsdrv_initups()
>> 0.027868 load_mib2nut: trying netvision mib
>> 0.029798 load_mib2nut: using netvision mib
>> 0.031731 Detected NETYS 3 kVA on host 192.168.0.227 (mib:
>> netvision 0.1)
>> 0.031751 SNMP UPS driver : entering upsdrv_initinfo()
>> 0.031785 getting data: ups.mfr
>> (.1.3.6.1.4.1.4555.1.1.1.1.1.__3.0)
>> (...)
why are these OIDs exposing "__"?
cheers,
Arnaud
--