[Nut-upsdev] bcmxcp: Now supports more ups variables, help needed on testing on hardware

Alf Høgemark alf at i100.no
Sun Jul 7 13:48:42 UTC 2013


On 07/07/2013 03:33 PM, Alf Høgemark wrote:
> Hi
>
> I had to close pull request 33, due to misspelling of commit messages.
> Charles helped me to fix it, and I have made a new pull request.
>
> The new pull request is :
> https://github.com/networkupstools/nut/pull/35
>
> Regards
> Alf
>
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at lists.alioth.debian.org
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev
Here is the output from upsc for my UPS, running on the code in this 
pull request :

ambient.temperature.high: 64
ambient.temperature.low: 168
battery.charge.low: 11
battery.voltage:  13.7
battery.voltage.low: 10
device.mfr: Eaton
device.model: POWERWARE UPS    500i
device.part: 103004261-5591
device.serial:
device.type: ups
driver.name: bcmxcp_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.shutdown_delay: 50
driver.version: 2.6.5-170-g3f72709
driver.version.internal: 0.28
input.frequency:  49.7
input.frequency.high: 55
input.frequency.low: 45
input.frequency.nominal: 50
input.quality: 1
input.transfer.boost.high: 207
input.transfer.high: 275
input.transfer.low: 178
input.transfer.trim.low: 250
input.voltage: 238
input.voltage.nominal: 230
output.current:   0.7
output.current.nominal:   1.3
output.frequency:  49.7
output.frequency.nominal: 50
output.phases: 1
output.voltage: 238
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.description: Line-Interactive UPS, Single Phase
ups.firmware: Cont:00.50 Inve:01.50
ups.load: 58
ups.mfr: Eaton
ups.model: POWERWARE UPS    500i
ups.power.nominal: 500
ups.serial:
ups.status: OL
ups.test.result: Done and passed




More information about the Nut-upsdev mailing list