[Nut-upsdev] Question about voltage threshold setting in NUT
    Shen Chuan 
    shen at minutekey.com
       
    Fri Jun  6 14:35:09 UTC 2014
    
    
  
Hello Charles,
Thank you for your reply.
For the discrete value thing, this morning I did try to run
sudo upsrw -s input.transfer.low=x -u * -p * ups
I changed "x" value from 60 to 96 then checked upsc result. All the script
return OK but only 84 and 96 got picked up and working.
Out model is Eaton 3S 500. And in windows it has a Eaton Personal Solution
Pac. In Battery transfer threshold it has three voltage sensitivity ranges:
96-138, 84-142, 75-144. 96 and 84 are working in NUT, not sure why 75 is
not working.
Do you think that range is restricted in the firmware? We have a tripplitte
model and upsc doesn't have input.transfer.low at all.
Please let me know if some other information could be helpful with the NUT.
Happy to assist debugging and provide more information.
Shen
On Thu, Jun 5, 2014 at 9:05 PM, Charles Lepple <clepple at gmail.com> wrote:
> On Jun 5, 2014, at 10:53 PM, Charles Lepple wrote:
>
> > As you have seen, the "default.*" and "overwrite.*" names are not actual
> variables: they are configuration options to change what is returned from
> upsc. That is why you get VAR-NOT-SUPPORTED.
>
> typo; should have been "override.*"
>
> --
> Charles Lepple
> clepple at gmail
>
>
>
>