[Nut-upsdev] [HCL] <Fideltronik INIGO> <Viper 1200> supported by <nutdrv_qx>
AWa.
awa_wp at wp.pl
Fri Jul 10 11:42:49 UTC 2015
Device manufacturer: Fideltronik INIGO
Device name: Viper 1200
Device type: UPS
Bus type: USB
WWW: http://fideltronikinigo.com/viper/viper-1200/
" nut-scanner -U" output:
[nutdev1]
driver = "blazer_usb"
port = "auto"
vendorid = "0001"
productid = "0000"
product = "MEC0003"
vendor = "MEC"
bus = "004"
---------------------------------------------------
But "blazer_usb" driver does not work with this device.
My working "ups.conf":
[Viper1200]
driver = "nutdrv_qx"
port = "auto"
vendorid = "0001"
productid = "0000"
product = "MEC0003"
vendor = "MEC"
bus = "004"
default.battery.voltage.high = 27.50
default.battery.voltage.low = 20.90
offdelay = 60
ondelay = 60
desc = "Fideltronik Viper 1200 UPS"
runtimecal = 60,100,900,21
idleload = 10
chargetime = 28800
---------------------------------------------------
"lsusb -s 004:0002 -v": http://bpa.ksu.pl/pub/lsusb.txt (28kB)
"nutdrv_qx -a Viper1200 -DDDD" output (init): http://bpa.ksu.pl/pub/nutdrv_qx_start.txt (7kB)
Supported command:
UPS Information Command (I)
1.817212 send: I
1.817224 command index: 0x0c
2.008115 read: # 1200VA VER 1.00
UPS Rating Information (F)
2.239335 send: F
2.239347 command index: 0x0d
2.354142 read: #230.0 5.2 24.00 50.0
Status Inquiry (Q1)
2.008223 send: Q1
2.008233 command index: 0x03
2.239141 read: (226.2 226.2 226.2 0 50.0 27.7 25.0 00001001
beeper.toggle (Q)
- if the beeper emits a beep at the time when command is issued the beep never ends...
- the beeper can not be switched off if UPS is on line.
396.231354 instcmd(beeper.toggle, [NULL])
396.231400 send: Q
396.231414 command index: 0x07
396.250914 read: UPS No Ack
396.250947 instcmd: FAILED
load.off (S00R0000)
- load are switched off after 30s,
- "C" command will not break the shutdown.
- nutdrv_qx output: http://bpa.ksu.pl/pub/nutdrv_qx_load.off.txt (4kB)
load.on or shutdown.stop (C)
- load are switched on after 10s,
- stop olny "shutdown.return",
- nutdrv_qx output: http://bpa.ksu.pl/pub/nutdrv_qx_load.on.txt (2kB)
shutdown.return (S01R0001)
- load is switched on immediately, the "Rxx" part does not matter,
- "C" command can break the shutdown.
- nutdrv_qx output: http://bpa.ksu.pl/pub/nutdrv_qx_shutdown.return.txt (7kB)
shutdown.stayoff (S01)
- "C" command will not break the shutdown.
- nutdrv_qx output: http://bpa.ksu.pl/pub/nutdrv_qx_shutdown.stayoff.txt (7kB)
Unsupported command:
Status Inquiry *disable (D)
0.200806 send: D
0.200815 read: D
test.battery.start
2070.664898 instcmd(test.battery.start, [NULL])
2070.664919 send: T10
2070.664933 read: T10
2070.664944 instcmd: FAILED
test.battery.start.deep
2083.480425 instcmd(test.battery.start.deep, [NULL])
2083.480476 send: TL
2083.480493 read: TL
2083.480504 instcmd: FAILED
test.battery.start.quick
2091.280535 instcmd(test.battery.start.quick, [NULL])
2091.280593 send: T
2091.280609 read: T
2091.280620 instcmd: FAILED
test.battery.stop
2099.425817 instcmd(test.battery.stop, [NULL])
2099.425865 send: CT
2099.425882 read: CT
2099.425907 instcmd: FAILED
Others:
Temperature reported by UPS is set to constant value of 25.0C it is not real temperature.
Discharge and die sequence:
http://bpa.ksu.pl/pub/nutdrv_qx_off.txt (209kB)
"upsc" output:
on line: http://bpa.ksu.pl/pub/nutdrv_qx_upsc.txt (1kB)
on battery: http://bpa.ksu.pl/pub/nutdrv_qx_upsc_OB.txt (1kB)
--
Best regards,
AWa.