[Nut-upsdev] UPSC dump for Eaton/Powerware 5115 Rackmount unit (driver version 2.7.2)

Uwe Sauter uwe.sauter.de at gmail.com
Fri Jul 14 11:40:34 UTC 2017


Hi,

just wanted to provide a upsc dump for an Eaton/Powerware 5115 rack mount unit. This was on a CentOS 7.3 machine with
following packages installed:

nut-client-2.7.2-3.el7.x86_64
nut-2.7.2-3.el7.x86_64
nut-cgi-2.7.2-3.el7.x86_64

$ upsc eaton5115
ambient.temperature: 43
ambient.temperature.high: 75
battery.charge: 100
battery.runtime: 24171
battery.voltage: 40.96
device.mfr: Eaton
device.model: PW5115 RM 1500i
device.part: XXXXXXXXX-XXXX
device.serial: XXXXXXXXXX
device.type: ups
driver.name: bcmxcp_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.7.2
driver.version.internal: 0.28
input.frequency: 50.00
input.frequency.high: 55
input.frequency.low: 45
input.frequency.nominal: 50
input.transfer.boost.high: 207
input.transfer.high: 266
input.transfer.low: 194
input.transfer.trim.low: 243
input.voltage: 239
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 3
outlet.1.id: 1
outlet.1.status: On
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 13
outlet.2.id: 2
outlet.2.status: On
output.current:  0.0
output.current.nominal:  6.4
output.frequency: 50.00
output.frequency.nominal: 50
output.phases: 1
output.voltage: 239
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.description: Line-Interactive UPS, Single Phase
ups.firmware: Cont:01.20 Inve:01.02
ups.load:   0.2
ups.mfr: Eaton
ups.model: PW5115 RM 1500i
ups.power: 3
ups.power.nominal: 1500
ups.realpower: 0
ups.serial: XXXXXXXXXX
ups.status: OL
ups.test.result: Done and passed


$ upscmd -u root eaton5115 test.battery.start
Password:
OK

Regards,

	Uwe



More information about the Nut-upsdev mailing list