Can't really say about ups.load without drilling into code diffs... may be
faster to just build current git master branch and run the driver in
data-dump mode:

git clone .../nut; cd nut
./ci_build.sh
./drivers/snmp-ups -s test -d1 -x port=UPSIP -x community=...

and maybe fiddle with mibs parameter - your report used the IETF standard
fallback, maybe we know a better featured vendor mib for the OEM under some
custom OID tree... or read up on subdriver generation and contribute a new
one or extend existing :)

Jim

On Fri, Dec 30, 2022, 23:13 Ireneusz Grycuk <igrycuk at wiredbit.com> wrote:

> Hello Jim!
>
> There is no problem - as you mentioned: the data is reported. I just
> wanted to let you know, for the record, besides - NUT made me do it ;) The
> only thing I noticed is that in case of PSI5-1500RT120 NUT (v2.7.4) doesn't
> report the ups.load value, do you know if this has been added in the newer
> wesion?
>
> Regards,
> ------------------------------
> IRENEUSZ GRYCUK
> CEO & Software Architect
> Mobile: +48 692 786 248 <+48692786248>
> E-Mail: igrycuk at wiredbit.com
> www.wiredbit.com
> Confidentiality Notice: This email and its attachments (if any) contain
> confidential information of the sender. The information is intended only
> for the use by the direct addressees of the original sender of this email.
> If you are not an intended recipient of the original sender (or responsible
> for delivering the message to such person), you are hereby notified that
> any review, disclosure, copying, distribution or the taking of any action
> in reliance of the contents of and attachments to this email is strictly
> prohibited. If you have received this email in error, please immediately
> notify the sender at the address shown herein and permanently delete any
> copies of this email (digital or paper) in your possession.
> On 12/30/22 21:49, Jim Klimov wrote:
>
> Thanks for the HCL report.
>
> Is the "problem" is "no OID found, tell devs"? - it is a benign message
> (muted in modern NUT - 2.7.4 is quite old) meaning that a subdriver match
> happened differently (per evidence - data is reported).
>
> Jim
>
>
> On Fri, Dec 30, 2022, 17:25 Ireneusz Grycuk <igrycuk at wiredbit.com> wrote:
>
>> Hello NUT dev!
>>
>> Reporting problem with NUT controller connected via SNMP v1 to Vertiv
>> PSI5-1500RT120 UPS:
>>
>>
>> Network UPS Tools - UPS driver controller 2.7.4
>> Network UPS Tools - Generic SNMP UPS driver 0.97 (2.7.4)
>> No matching MIB found for sysOID '.1.3.6.1.4.1.476.1.42'!
>> Please report it to NUT developers, with an 'upsc' output for your device.
>> Going back to the classic MIB detection method.
>> Detected PSI5-1500RT120 on host 10.1.1.32 (mib: ietf 1.5)
>>
>> $ upsc UPS01
>> Init SSL without certificate database
>> battery.charge: 100.00
>> battery.runtime: 1260.00
>> battery.runtime.low: 120.00
>> battery.voltage: 54.00
>> device.mfr: Vertiv
>> device.model: PSI5-1500RT120
>> device.type: ups
>> driver.name: snmp-ups
>> driver.parameter.pollfreq: 15
>> driver.parameter.pollinterval: 2
>> driver.parameter.port: 10.1.1.32
>> driver.parameter.snmp_version: v1
>> driver.parameter.synchronous: no
>> driver.version: 2.7.4
>> driver.version.data: ietf MIB 1.5
>> driver.version.internal: 0.97
>> input.current: 5.00
>> input.frequency: 60.00
>> input.frequency.nominal: 60.00
>> input.phases: 1.00
>> input.voltage: 115.00
>> input.voltage.nominal: 120.00
>> output.current: 4.40
>> output.frequency: 60.00
>> output.frequency.nominal: 60.00
>> output.phases: 1.00
>> output.power.nominal: 1500.00
>> output.voltage: 115.00
>> output.voltage.nominal: 120.00
>> ups.beeper.status: enabled
>> ups.firmware: 02418.03
>> ups.firmware.aux: 8.2.0.0
>> ups.mfr: Vertiv
>> ups.model: PSI5-1500RT120
>> ups.start.auto: yes
>> ups.status: OL
>> ups.test.result: done and passed
>> ups.timer.reboot: 0
>> ups.timer.shutdown: 0
>> ups.timer.start: 0
>>
>>
>> Regards,
>> --
>> ------------------------------
>> IRENEUSZ GRYCUK
>> CEO & Software Architect
>> Mobile: +48 692 786 248 <+48692786248>
>> E-Mail: igrycuk at wiredbit.com
>> www.wiredbit.com
>> Confidentiality Notice: This email and its attachments (if any) contain
>> confidential information of the sender. The information is intended only
>> for the use by the direct addressees of the original sender of this email.
>> If you are not an intended recipient of the original sender (or responsible
>> for delivering the message to such person), you are hereby notified that
>> any review, disclosure, copying, distribution or the taking of any action
>> in reliance of the contents of and attachments to this email is strictly
>> prohibited. If you have received this email in error, please immediately
>> notify the sender at the address shown herein and permanently delete any
>> copies of this email (digital or paper) in your possession.
>> _______________________________________________
>> Nut-upsdev mailing list
>> Nut-upsdev at alioth-lists.debian.net
>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev
>>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsdev/attachments/20221231/dbf56ac6/attachment.htm>


More information about the Nut-upsdev mailing list