[Nut-upsdev] No matching MIB found for sysOID
Jim Klimov
jimklimov+nut at gmail.com
Thu Feb 16 07:01:42 GMT 2023
That is a message from NUT 2.7.4 and older, emitted as snmp-ups driver
tries to guess the vendor that matches a device (by extended sub-trees) or
see if it has to fall back to IETF data tree, if `mibs=...` were not
specified.
Current versions should not post that as a sort-of-drastic situation.
Jim
On Thu, Feb 16, 2023, 02:16 Brad Tarver via Nut-upsdev <
nut-upsdev at alioth-lists.debian.net> wrote:
> Hello all,
>
> Thank you in advance for a great FOSS project. Also, thank you for reading
> my question.
>
> I have a CyberPower OR1500LCDRTXL2U with an RMCARD205. There are a handful
> of devices plugged into the UPS.
>
> I received a message today saying to send upsc output to NUT developers
> after this message: "No matching MIB found for sysOID
> '.1.3.6.1.4.1.3808.1.1.1'"
>
> root at delta:/etc/nut# systemctl status nut-driver.service
> Feb 15 17:47:52 delta upsdrvctl[519]: No matching MIB found for sysOID
> '.1.3.6.1.4.1.3808.1.1.1'!
> Feb 15 17:47:52 delta upsdrvctl[519]: Please report it to NUT developers,
> with an 'upsc' output for your device.
> Feb 15 17:47:52 delta upsdrvctl[519]: Going back to the classic MIB
> detection method.
> Feb 15 17:47:52 delta upsdrvctl[519]: Detected OR1500LCDRTXL2U on host
> 172.16.20.30 (mib: cyberpower 0.1)
> Feb 15 17:47:52 delta upsdrvctl[519]: [network-ups] unhandled ASN 0x5
> received from .1.3.6.1.4.1.3808.1.1.1.2.2.2.0
> Feb 15 17:47:52 delta snmp-ups[576]: Startup successful
>
> UPS.CONF
> ========
> maxretry = 3
> [network-ups]
> driver = snmp-ups
> port = 172.16.20.30
> snmp_version = v2c
> community = cybernut
> pollfreq = 15
> desc = "CyperPower OR1500LCDRTXL2U"
>
>
> UPSC OUTPUT
> ========
> root at delta:/etc/nut# upsc network-ups at localhost
> Init SSL without certificate database
> battery.runtime: 262800.00
> battery.runtime.elapsed: 0.00
> device.mfr: CYBERPOWER
> device.model: OR1500LCDRTXL2U
> device.serial: REDACTED SERIAL NUMBER
> device.type: ups
> driver.name: snmp-ups
> driver.parameter.pollfreq: 15
> driver.parameter.pollinterval: 2
> driver.parameter.port: 172.16.20.30
> driver.parameter.snmp_version: v2c
> driver.parameter.synchronous: no
> driver.version: 2.7.4
> driver.version.data: cyberpower MIB 0.1
> driver.version.internal: 0.97
> ups.firmware: BF02018B7V11
> ups.mfr: CYBERPOWER
> ups.model: OR1500LCDRTXL2U
> ups.serial: REDACTED SERIAL NUMBER
> ups.status: OL
>
> SNMPWALK
> ========
> root at delta:/etc/nut# snmpwalk -c cybernut -v 2c 172.16.20.30
> iso.3.6.1.2.1.1.1.0 = STRING: "UPS SNMP Card"
> iso.3.6.1.2.1.1.2.0 = OID: iso.3.6.1.4.1.3808.1.1.1
> iso.3.6.1.2.1.1.3.0 = Timeticks: (11125500) 1 day, 6:54:15.00
> iso.3.6.1.2.1.1.4.0 = STRING: "REDACTED CONTACT"
> iso.3.6.1.2.1.1.5.0 = STRING: "network-ups"
> iso.3.6.1.2.1.1.6.0 = STRING: "REDACTED LOCATION"
> iso.3.6.1.2.1.1.7.0 = INTEGER: 72
> iso.3.6.1.2.1.2.1.0 = INTEGER: 2
> iso.3.6.1.2.1.2.2.1.1.1 = INTEGER: 1
> iso.3.6.1.2.1.2.2.1.1.2 = INTEGER: 2
> iso.3.6.1.2.1.2.2.1.2.1 = Hex-STRING: 61 67 00 00 00
> iso.3.6.1.2.1.2.2.1.2.2 = Hex-STRING: 00 08 3D 12 00
> iso.3.6.1.2.1.2.2.1.3.1 = INTEGER: 0
> iso.3.6.1.2.1.2.2.1.3.2 = INTEGER: 18
> iso.3.6.1.2.1.2.2.1.4.1 = INTEGER: 1500
> iso.3.6.1.2.1.2.2.1.4.2 = INTEGER: 4657
> iso.3.6.1.2.1.2.2.1.5.1 = Gauge32: 10000000
> iso.3.6.1.2.1.2.2.1.5.2 = Gauge32: 134222401
> iso.3.6.1.2.1.2.2.1.6.1 = Hex-STRING: 00 0C 15 04 C6 E6
> iso.3.6.1.2.1.2.2.1.6.2 = ""
> iso.3.6.1.2.1.2.2.1.7.1 = INTEGER: 7
> iso.3.6.1.2.1.2.2.1.7.2 = INTEGER: 2
> iso.3.6.1.2.1.2.2.1.8.1 = INTEGER: 1
> iso.3.6.1.2.1.2.2.1.8.2 = INTEGER: 2
> iso.3.6.1.2.1.2.2.1.9.1 = Timeticks: (0) 0:00:00.00
> iso.3.6.1.2.1.2.2.1.9.2 = Timeticks: (134222405) 15 days, 12:50:24.05
> iso.3.6.1.2.1.2.2.1.10.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.10.2 = Counter32: 134222409
> iso.3.6.1.2.1.2.2.1.11.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.11.2 = Counter32: 134222413
> iso.3.6.1.2.1.2.2.1.12.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.12.2 = Counter32: 134222417
> iso.3.6.1.2.1.2.2.1.13.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.13.2 = Counter32: 134222421
> iso.3.6.1.2.1.2.2.1.14.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.14.2 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.15.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.15.2 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.16.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.16.2 = Counter32: 134222425
> iso.3.6.1.2.1.2.2.1.17.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.17.2 = Counter32: 134222429
> iso.3.6.1.2.1.2.2.1.18.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.18.2 = Counter32: 134222433
> iso.3.6.1.2.1.2.2.1.19.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.19.2 = Counter32: 134222437
> iso.3.6.1.2.1.2.2.1.20.1 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.20.2 = Counter32: 0
> iso.3.6.1.2.1.2.2.1.21.1 = Gauge32: 0
> iso.3.6.1.2.1.2.2.1.21.2 = Gauge32: 0
> iso.3.6.1.2.1.2.2.1.22.1 = OID: ccitt.0
> iso.3.6.1.2.1.2.2.1.22.2 = OID: ccitt.0
> iso.3.6.1.2.1.3.1.1.1.1.172.16.20.1 = INTEGER: 1
> iso.3.6.1.2.1.3.1.1.1.1.172.16.20.4 = INTEGER: 1
> iso.3.6.1.2.1.3.1.1.1.1.172.16.20.5 = INTEGER: 1
> iso.3.6.1.2.1.3.1.1.1.1.172.16.20.9 = INTEGER: 1
> iso.3.6.1.2.1.3.1.1.1.1.172.16.20.32 = INTEGER: 1
> iso.3.6.1.2.1.3.1.1.1.1.172.16.20.203 = INTEGER: 1
> iso.3.6.1.2.1.3.1.1.2.1.172.16.20.1 = Hex-STRING: 74 AC B9 D3 F8 CF
> iso.3.6.1.2.1.3.1.1.2.1.172.16.20.4 = Hex-STRING: B4 FB E4 51 47 4F
> iso.3.6.1.2.1.3.1.1.2.1.172.16.20.5 = Hex-STRING: 24 5E BE 3E 7B 5A
> iso.3.6.1.2.1.3.1.1.2.1.172.16.20.9 = Hex-STRING: 00 1E 06 51 09 55
> iso.3.6.1.2.1.3.1.1.2.1.172.16.20.32 = Hex-STRING: DC A6 32 03 75 8C
> iso.3.6.1.2.1.3.1.1.2.1.172.16.20.203 = Hex-STRING: 4C 20 B8 ED FB 19
> iso.3.6.1.2.1.3.1.1.3.1.172.16.20.1 = IpAddress: 172.16.20.1
> iso.3.6.1.2.1.3.1.1.3.1.172.16.20.4 = IpAddress: 172.16.20.4
> iso.3.6.1.2.1.3.1.1.3.1.172.16.20.5 = IpAddress: 172.16.20.5
> iso.3.6.1.2.1.3.1.1.3.1.172.16.20.9 = IpAddress: 172.16.20.9
> iso.3.6.1.2.1.3.1.1.3.1.172.16.20.32 = IpAddress: 172.16.20.32
> iso.3.6.1.2.1.3.1.1.3.1.172.16.20.203 = IpAddress: 172.16.20.203
> iso.3.6.1.2.1.4.1.0 = INTEGER: 2
> iso.3.6.1.2.1.4.2.0 = INTEGER: 255
> iso.3.6.1.2.1.4.3.0 = Counter32: 652326
> iso.3.6.1.2.1.4.4.0 = Counter32: 0
> iso.3.6.1.2.1.4.5.0 = Counter32: 521619
> iso.3.6.1.2.1.4.6.0 = Counter32: 0
> iso.3.6.1.2.1.4.7.0 = Counter32: 0
> iso.3.6.1.2.1.4.8.0 = Counter32: 521619
> iso.3.6.1.2.1.4.9.0 = Counter32: 130713
> iso.3.6.1.2.1.4.10.0 = Counter32: 67770
> iso.3.6.1.2.1.4.11.0 = Counter32: 0
> iso.3.6.1.2.1.4.12.0 = Counter32: 0
> iso.3.6.1.2.1.4.13.0 = INTEGER: 0
> iso.3.6.1.2.1.4.14.0 = Counter32: 0
> iso.3.6.1.2.1.4.15.0 = Counter32: 0
> iso.3.6.1.2.1.4.16.0 = Counter32: 0
> iso.3.6.1.2.1.4.17.0 = Counter32: 0
> iso.3.6.1.2.1.4.18.0 = Counter32: 0
> iso.3.6.1.2.1.4.19.0 = Counter32: 0
> iso.3.6.1.2.1.4.20.1.1.172.16.20.30 = IpAddress: 172.16.20.30
> iso.3.6.1.2.1.4.20.1.2.172.16.20.30 = INTEGER: 1
> iso.3.6.1.2.1.4.20.1.3.172.16.20.30 = IpAddress: 255.255.255.0
> iso.3.6.1.2.1.4.20.1.4.172.16.20.30 = INTEGER: 1
> iso.3.6.1.2.1.4.20.1.5.172.16.20.30 = INTEGER: 0
> iso.3.6.1.2.1.4.21.1.1.0.0.0.0 = IpAddress: 0.0.0.0
> iso.3.6.1.2.1.4.21.1.1.172.16.20.0 = IpAddress: 172.16.20.0
> iso.3.6.1.2.1.4.21.1.2.0.0.0.0 = INTEGER: 1
> iso.3.6.1.2.1.4.21.1.2.172.16.20.0 = INTEGER: 1
> iso.3.6.1.2.1.4.21.1.3.0.0.0.0 = INTEGER: 1
> iso.3.6.1.2.1.4.21.1.3.172.16.20.0 = INTEGER: 0
> iso.3.6.1.2.1.4.21.1.4.0.0.0.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.4.172.16.20.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.5.0.0.0.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.5.172.16.20.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.6.0.0.0.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.6.172.16.20.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.7.0.0.0.0 = IpAddress: 172.16.20.1
> iso.3.6.1.2.1.4.21.1.7.172.16.20.0 = IpAddress: 172.16.20.30
> iso.3.6.1.2.1.4.21.1.8.0.0.0.0 = INTEGER: 4
> iso.3.6.1.2.1.4.21.1.8.172.16.20.0 = INTEGER: 3
> iso.3.6.1.2.1.4.21.1.9.0.0.0.0 = INTEGER: 2
> iso.3.6.1.2.1.4.21.1.9.172.16.20.0 = INTEGER: 2
> iso.3.6.1.2.1.4.21.1.10.0.0.0.0 = INTEGER: 0
> iso.3.6.1.2.1.4.21.1.10.172.16.20.0 = INTEGER: 0
> iso.3.6.1.2.1.4.21.1.11.0.0.0.0 = IpAddress: 0.0.0.0
> iso.3.6.1.2.1.4.21.1.11.172.16.20.0 = IpAddress: 255.255.255.0
> iso.3.6.1.2.1.4.21.1.12.0.0.0.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.12.172.16.20.0 = INTEGER: -1
> iso.3.6.1.2.1.4.21.1.13.0.0.0.0 = OID: ccitt.0
> iso.3.6.1.2.1.4.21.1.13.172.16.20.0 = OID: ccitt.0
> iso.3.6.1.2.1.4.22.1.1.1.172.16.20.1 = INTEGER: 1
> iso.3.6.1.2.1.4.22.1.1.1.172.16.20.4 = INTEGER: 1
> iso.3.6.1.2.1.4.22.1.1.1.172.16.20.5 = INTEGER: 1
> iso.3.6.1.2.1.4.22.1.1.1.172.16.20.9 = INTEGER: 1
> iso.3.6.1.2.1.4.22.1.1.1.172.16.20.32 = INTEGER: 1
> iso.3.6.1.2.1.4.22.1.1.1.172.16.20.203 = INTEGER: 1
> iso.3.6.1.2.1.4.22.1.2.1.172.16.20.1 = Hex-STRING: 74 AC B9 D3 F8 CF
> iso.3.6.1.2.1.4.22.1.2.1.172.16.20.4 = Hex-STRING: B4 FB E4 51 47 4F
> iso.3.6.1.2.1.4.22.1.2.1.172.16.20.5 = Hex-STRING: 24 5E BE 3E 7B 5A
> iso.3.6.1.2.1.4.22.1.2.1.172.16.20.9 = Hex-STRING: 00 1E 06 51 09 55
> iso.3.6.1.2.1.4.22.1.2.1.172.16.20.32 = Hex-STRING: DC A6 32 03 75 8C
> iso.3.6.1.2.1.4.22.1.2.1.172.16.20.203 = Hex-STRING: 4C 20 B8 ED FB 19
> iso.3.6.1.2.1.4.22.1.3.1.172.16.20.1 = IpAddress: 172.16.20.1
> iso.3.6.1.2.1.4.22.1.3.1.172.16.20.4 = IpAddress: 172.16.20.4
> iso.3.6.1.2.1.4.22.1.3.1.172.16.20.5 = IpAddress: 172.16.20.5
> iso.3.6.1.2.1.4.22.1.3.1.172.16.20.9 = IpAddress: 172.16.20.9
> iso.3.6.1.2.1.4.22.1.3.1.172.16.20.32 = IpAddress: 172.16.20.32
> iso.3.6.1.2.1.4.22.1.3.1.172.16.20.203 = IpAddress: 172.16.20.203
> iso.3.6.1.2.1.4.22.1.4.1.172.16.20.1 = INTEGER: 3
> iso.3.6.1.2.1.4.22.1.4.1.172.16.20.4 = INTEGER: 3
> iso.3.6.1.2.1.4.22.1.4.1.172.16.20.5 = INTEGER: 3
> iso.3.6.1.2.1.4.22.1.4.1.172.16.20.9 = INTEGER: 3
> iso.3.6.1.2.1.4.22.1.4.1.172.16.20.32 = INTEGER: 3
> iso.3.6.1.2.1.4.22.1.4.1.172.16.20.203 = INTEGER: 3
> iso.3.6.1.2.1.4.23.0 = Counter32: 0
> iso.3.6.1.2.1.5.1.0 = Counter32: 11555
> iso.3.6.1.2.1.5.2.0 = Counter32: 0
> iso.3.6.1.2.1.5.3.0 = Counter32: 0
> iso.3.6.1.2.1.5.4.0 = Counter32: 0
> iso.3.6.1.2.1.5.5.0 = Counter32: 0
> iso.3.6.1.2.1.5.6.0 = Counter32: 0
> iso.3.6.1.2.1.5.7.0 = Counter32: 0
> iso.3.6.1.2.1.5.8.0 = Counter32: 0
> iso.3.6.1.2.1.5.9.0 = Counter32: 0
> iso.3.6.1.2.1.5.10.0 = Counter32: 0
> iso.3.6.1.2.1.5.11.0 = Counter32: 0
> iso.3.6.1.2.1.5.12.0 = Counter32: 0
> iso.3.6.1.2.1.5.13.0 = Counter32: 0
> iso.3.6.1.2.1.5.14.0 = Counter32: 14270
> iso.3.6.1.2.1.5.15.0 = Counter32: 0
> iso.3.6.1.2.1.5.16.0 = Counter32: 0
> iso.3.6.1.2.1.5.17.0 = Counter32: 2716
> iso.3.6.1.2.1.5.18.0 = Counter32: 0
> iso.3.6.1.2.1.5.19.0 = Counter32: 0
> iso.3.6.1.2.1.5.20.0 = Counter32: 0
> iso.3.6.1.2.1.5.21.0 = Counter32: 0
> iso.3.6.1.2.1.5.22.0 = Counter32: 11554
> iso.3.6.1.2.1.5.23.0 = Counter32: 0
> iso.3.6.1.2.1.5.24.0 = Counter32: 0
> iso.3.6.1.2.1.5.25.0 = Counter32: 0
> iso.3.6.1.2.1.5.26.0 = Counter32: 0
> iso.3.6.1.2.1.6.1.0 = INTEGER: 4
> iso.3.6.1.2.1.6.2.0 = INTEGER: 1000
> iso.3.6.1.2.1.6.3.0 = INTEGER: 60000
> iso.3.6.1.2.1.6.4.0 = INTEGER: 60
> iso.3.6.1.2.1.6.5.0 = Counter32: 0
> iso.3.6.1.2.1.6.6.0 = Counter32: 1049
> iso.3.6.1.2.1.6.7.0 = Counter32: 0
> iso.3.6.1.2.1.6.8.0 = Counter32: 1045
> iso.3.6.1.2.1.6.9.0 = Gauge32: 0
> iso.3.6.1.2.1.6.10.0 = Counter32: 13324
> iso.3.6.1.2.1.6.11.0 = Counter32: 8743
> iso.3.6.1.2.1.6.12.0 = Counter32: 0
> iso.3.6.1.2.1.6.13.7.1.0 = Counter32: 41937
> iso.3.6.1.2.1.6.14.0 = Counter32: 0
> iso.3.6.1.2.1.6.15.0 = Counter32: 1927
> iso.3.6.1.2.1.7.1.0 = Counter32: 41940
> iso.3.6.1.2.1.7.2.0 = Counter32: 2716
> iso.3.6.1.2.1.7.3.0 = Counter32: 0
> iso.3.6.1.2.1.7.4.0 = Counter32: 41849
> iso.3.6.1.2.1.7.5.1.1.0.0.0.0.53 = IpAddress: 0.0.0.0
> iso.3.6.1.2.1.7.5.1.1.0.0.0.0.161 = IpAddress: 0.0.0.0
> iso.3.6.1.2.1.7.5.1.1.0.0.0.0.53565 = IpAddress: 0.0.0.0
> iso.3.6.1.2.1.7.5.1.1.0.0.0.0.53566 = IpAddress: 0.0.0.0
> iso.3.6.1.2.1.7.5.1.2.0.0.0.0.53 = INTEGER: 53
> iso.3.6.1.2.1.7.5.1.2.0.0.0.0.161 = INTEGER: 161
> iso.3.6.1.2.1.7.5.1.2.0.0.0.0.53565 = INTEGER: 53565
> iso.3.6.1.2.1.7.5.1.2.0.0.0.0.53566 = INTEGER: 53566
> iso.3.6.1.2.1.11.1.0 = Counter32: 41932
> iso.3.6.1.2.1.11.2.0 = Counter32: 41837
> iso.3.6.1.2.1.11.3.0 = Counter32: 0
> iso.3.6.1.2.1.11.4.0 = Counter32: 0
> iso.3.6.1.2.1.11.5.0 = Counter32: 0
> iso.3.6.1.2.1.11.6.0 = Counter32: 35
> iso.3.6.1.2.1.11.8.0 = Counter32: 0
> iso.3.6.1.2.1.11.9.0 = Counter32: 0
> iso.3.6.1.2.1.11.10.0 = Counter32: 0
> iso.3.6.1.2.1.11.11.0 = Counter32: 0
> iso.3.6.1.2.1.11.12.0 = Counter32: 0
> iso.3.6.1.2.1.11.13.0 = Counter32: 67435
> iso.3.6.1.2.1.11.14.0 = Counter32: 0
> iso.3.6.1.2.1.11.15.0 = Counter32: 38242
> iso.3.6.1.2.1.11.16.0 = Counter32: 3609
> iso.3.6.1.2.1.11.17.0 = Counter32: 0
> iso.3.6.1.2.1.11.18.0 = Counter32: 0
> iso.3.6.1.2.1.11.19.0 = Counter32: 0
> iso.3.6.1.2.1.11.20.0 = Counter32: 714
> iso.3.6.1.2.1.11.21.0 = Counter32: 4678
> iso.3.6.1.2.1.11.22.0 = Counter32: 0
> iso.3.6.1.2.1.11.24.0 = Counter32: 0
> iso.3.6.1.2.1.11.25.0 = Counter32: 0
> iso.3.6.1.2.1.11.26.0 = Counter32: 0
> iso.3.6.1.2.1.11.27.0 = Counter32: 0
> iso.3.6.1.2.1.11.28.0 = Counter32: 41861
> iso.3.6.1.2.1.11.29.0 = Counter32: 0
> iso.3.6.1.2.1.11.30.0 = INTEGER: 2
> iso.3.6.1.2.1.33.1.1.1.0 = STRING: "CPS"
> iso.3.6.1.2.1.33.1.1.2.0 = STRING: "OR1500LCDRTXL2U"
> iso.3.6.1.2.1.33.1.1.3.0 = STRING: "BF02018B7V11"
> iso.3.6.1.2.1.33.1.1.5.0 = STRING: "network-ups"
> iso.3.6.1.2.1.33.1.2.1.0 = INTEGER: 2
> iso.3.6.1.2.1.33.1.2.2.0 = INTEGER: 0
> iso.3.6.1.2.1.33.1.2.3.0 = INTEGER: 73
> iso.3.6.1.2.1.33.1.2.4.0 = INTEGER: 100
> iso.3.6.1.2.1.33.1.2.5.0 = NULL
> iso.3.6.1.2.1.33.1.2.7.0 = NULL
> iso.3.6.1.2.1.33.1.3.2.0 = INTEGER: 1
> iso.3.6.1.2.1.33.1.3.3.1.1.1 = INTEGER: 1
> iso.3.6.1.2.1.33.1.3.3.1.2.1 = INTEGER: 600
> iso.3.6.1.2.1.33.1.3.3.1.3.1 = INTEGER: 122
> iso.3.6.1.2.1.33.1.3.3.1.4.1 = INTEGER: 0
> iso.3.6.1.2.1.33.1.3.3.1.5.1 = INTEGER: 0
> iso.3.6.1.2.1.33.1.4.1.0 = INTEGER: 3
> iso.3.6.1.2.1.33.1.4.2.0 = INTEGER: 600
> iso.3.6.1.2.1.33.1.4.3.0 = INTEGER: 1
> iso.3.6.1.2.1.33.1.4.4.1.1.1 = INTEGER: 1
> iso.3.6.1.2.1.33.1.4.4.1.2.1 = INTEGER: 122
> iso.3.6.1.2.1.33.1.4.4.1.3.1 = INTEGER: 0
> iso.3.6.1.2.1.33.1.4.4.1.4.1 = INTEGER: 0
> iso.3.6.1.2.1.33.1.4.4.1.5.1 = INTEGER: 12
> iso.3.6.1.2.1.33.1.5.1.0 = INTEGER: 600
> iso.3.6.1.2.1.33.1.5.2.0 = INTEGER: 1
> iso.3.6.1.2.1.33.1.5.3.1.1.1 = INTEGER: 1
> iso.3.6.1.2.1.33.1.5.3.1.2.1 = INTEGER: 0
> iso.3.6.1.2.1.33.1.5.3.1.3.1 = INTEGER: 0
> iso.3.6.1.2.1.33.1.5.3.1.4.1 = INTEGER: 0
> iso.3.6.1.2.1.33.1.6.1.0 = Gauge32: 0
> iso.3.6.1.2.1.33.1.7.1.0 = OID: iso.3.6.1.2.1.33.1.7.7.4
> iso.3.6.1.2.1.33.1.7.2.0 = INTEGER: 0
> iso.3.6.1.2.1.33.1.7.3.0 = INTEGER: 1
> iso.3.6.1.2.1.33.1.7.4.0 = ""
> iso.3.6.1.2.1.33.1.7.5.0 = Timeticks: (0) 0:00:00.00
> iso.3.6.1.2.1.33.1.7.6.0 = INTEGER: 0
> iso.3.6.1.2.1.33.1.8.1.0 = INTEGER: 2
> iso.3.6.1.2.1.33.1.8.2.0 = INTEGER: -1
> iso.3.6.1.2.1.33.1.8.3.0 = INTEGER: -1
> iso.3.6.1.2.1.33.1.8.4.0 = INTEGER: -1
> iso.3.6.1.2.1.33.1.8.5.0 = INTEGER: 2
> iso.3.6.1.2.1.33.1.9.2.0 = INTEGER: 600
> iso.3.6.1.2.1.33.1.9.3.0 = INTEGER: 122
> iso.3.6.1.2.1.33.1.9.4.0 = INTEGER: 600
> iso.3.6.1.2.1.33.1.9.5.0 = INTEGER: 0
> iso.3.6.1.2.1.33.1.9.6.0 = INTEGER: 0
> iso.3.6.1.2.1.33.1.9.8.0 = INTEGER: 2
> iso.3.6.1.2.1.33.1.9.9.0 = INTEGER: 90
> iso.3.6.1.2.1.33.1.9.10.0 = INTEGER: 140
>
>
>
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsdev/attachments/20230216/2db0e33d/attachment-0001.htm>
More information about the Nut-upsdev
mailing list