[Nut-upsdev] New UPS ABB
Jim Klimov
jimklimov+nut at gmail.com
Tue Nov 19 08:23:23 GMT 2024
Hello,
The PDF User Manual linked from the product page indicates the port for
SNMP/Modbus/HTTP card - I assume you have it populated and set up.
Most of the vendors support the basic IETF standard data tree and often
their private extension branches for more detail, so it is a bit odd that
this MIB was not found.
Typical reasons would be security (for SNMP v1/v2c you must provide the
correct community string for R/O access at least, or R/W to work with
commands and settings; with v3 be sure the same crypto is supported on both
sides - linbnetsnmp builds varied in that).
Being historically UDP-based, with no dialog sessions, SNMP's lack of
response to unauthenticated queries tends to be indistinguishable from the
server being not online.
Also check the SNMP server is just enabled there, often it is off by
default.
Jim
On Tue, Nov 19, 2024, 04:34 Mjay via Nut-upsdev <
nut-upsdev at alioth-lists.debian.net> wrote:
> Hi Team
>
> While i;m searching on the internet about UPS SNMP monitoring , I found
> this NUT server. Thank God, But sad news is that my UPS is not listed in
> the compatibility list.
> But I download NUT server on my ubuntu node and just discover it
>
> sudo /lib/nut/snmp-ups -DD -a ups
>
> unfortunately got the below error message.
> 228.253598 [D2] Testing ups.model using OID 1.3.6.1.2.1.33.1.1.2.0
> 234.260010 [D2] load_mib2nut: trying classic sysOID matching method
> with 'ietf' mib
> 234.260031 [D2] Found entry, not a template 1.3.6.1.2.1.33.1.1.2.0
> 234.260033 [D2] Testing ups.model using OID 1.3.6.1.2.1.33.1.1.2.0
> 240.266446 No supported device detected at [myups] (host 10.186.29.30)
> 240.266779 upsnotify: failed to notify about state 4: no notification
> tech defined, will not spam more about it
>
> Can kindly someone help me to add my UPS.
> Model:
> *ABB PowerValue 11 RT G2 IEC *
> https://new.abb.com/ups/systems/single-phase-ups/powervalue-11-rt
>
> Thanks a lot
> MJ
>
>
>
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsdev/attachments/20241119/6707c3a1/attachment.htm>
More information about the Nut-upsdev