[Nut-upsdev] Error "Data for UPS [pcmusb] is stale - check driver"
Rushabh Sanghavi (Rush)
Rushabh at pp-ontime.co.th
Fri Jan 31 03:50:58 GMT 2025
Dear NUT Developers,
A very good morning to you and hope that you are in the best of health and spirits.
For an upcoming UPS Project, our team has been testing Powercom’s Cleanline T-1500 UPS model whose photo has been attached with this e-mail. Our team has been testing this UPS with one of our 4G LTE WiFi router models on which Network UPS Tools (NUT) Version 2.8.0-3 has been installed. BUT during the testing our team observed multiple instances of error message "Data for UPS [pcmusb] is stale - check driver" being randomly reported by our 4G LTE WiFi router. Here is the SUMMARY of the issue below for clear understanding purposes.
* NUT Version 2.8.0-3 was installed on our 4G LTE WiFi router by our team.
* Also our 4G LTE WiFi router had Linux Kernel Version 5.15.127, OpenWRT Distribution release “23.05.0-rc3” and OpenWRT Distribution Revision “r23389-5deed175a5” installed on it.
* Powercom’s Cleanline T-1500 UPS was connected with our 4G LTE WiFi router via USB to USB Cable Connection (i.e. USB Port on router side and USB Port on UPS side)
Now when NUT installed on our 4G LTE WiFi router model unit tried to poll and fetch values of different UPS parameters from Powercom’s Cleanline T-1500 UPS model
after both UPS and router had been running for sometime (i.e. for random period of time):
* router started reporting the error message “Data for UPS [pcmusb] is stale - check driver”
* after that router could not get UPS’s status any more unless we restart the NUT service
* and the router started reporting the error message “Data for UPS [pcmusb] is stale - check driver” after running for sometime again
Note: [pcmusb] represents the name or identifier assigned to the UPS instance within the NUT (Network UPS Tools) configuration
* Our team tried to increase value of NUT’s timers such as “pollinterval”, “pollfreq”, “maxage” but still the issue could not get solved or fixed
* Kindly NOTE that our team tested the above with both the NUT Drivers i.e. blazer_usb and nutdrv_qx. But the same error message mentioned above was observed.
* Also kindly NOTE that our team also tried to test with NUT Driver “usbhid-ups” but it is seems that this particular Driver is not supported by Powercom’s Cleanline T-1500 UPS model whose photo has been attached with this e-mail.
* Currently our team is not 100% sure about the exact root cause.
Our team need to know the following from NUT Developers.
* Which the is correct NUT Driver that our team need to use on the 4G LTE WiFi router so that it can communicate smoothly and successfully with Powercom’s Cleanline T-1500 UPS model whose photo has been attached with this e-mail?
* Which specific parameters within the default Configuration Settings file of NUT Version 2.8.0-3 on our 4G LTE WiFi router need to be tweaked / changed so that our 4G LTE WiFi router model can communicate with the Powercom’s Cleanline T-1500 UPS model smoothly and successfully?
* Which specific parameters within the default ups.conf / upsd.conf file on our 4G LTE WiFi router needs to be tweaked / changed so that our 4G LTE WiFi router model can communicate with the Powercom’s Cleanline T-1500 UPS model smoothly and successfully?
Also I am hereby attaching the Log Files with the Log Messages reported on our 4G LTE WiFi router model. The 1st Log file contains Log Messages during testing with NUT Driver “blazer_usb” while the 2nd Log file contains Log Messages during testing with NUT Driver “nutdrv_qx”. You will observe the ERROR Message “Data for UPS [pcmusb] is stale - check driver” within both these attached Log Files.
Awaiting your swift response back.
Thanking you,
Yours sincerely,
[Legs Logo]
Rushabh N. S
Research and Development Director
PP Ontime Company Limited
PP Group of Companies
Address: 1011 Supalai Grand Tower,
16th Floor, Rama 3 Road,
Chongnonsi, Yannawa,
Bangkok – 10120, Thailand
Landline No: +66-2-0562099 Ext. 2201
Fax No: +66-2-0562088
Cell Phone No: +66-8-59118578 / +66-6-22236221
E-mail: rushabh at pp-ontime.co.th<mailto:rushabh at pp-ontime.co.th>
Web: www.pp-ontime.co.th<http://www.pp-ontime.co.th>
Skype ID: rushabh.sanghavi
Disclaimer:
***************************************************************
Important
Confidentiality: This Information is intended for the above-named person and may contain confidential and/or legally privileged material. Any opinions expressed in this information are not necessarily those of the company. If it has come to you in error you must take no action based on it, nor must you copy or show it to anyone; please delete/destroy and inform the sender immediately.
Monitoring/Viruses/Malwares
PP-Ontime reserves the right to monitor all incoming and outgoing emails via PP-Ontime's systems. Although we have security program to monitor and eliminate virus/malware, we also advise that in keeping with good computing practice the recipient should ensure they are actually virus/malwares free.
***************************************************************
Disclaimer:
***********************************************************************************************
Important
Confidentiality: This Information is intended for the above-named person and may contain confidential and/or legally privileged material. Any opinions expressed in this information are not necessarily those of the company. If it has come to you in error you must take no action based on it, nor must you copy or show it to anyone; please delete/destroy and inform the sender immediately.
Monitoring/Viruses/Malwares
PP-Ontime reserves the right to monitor all incoming and outgoing emails via PP-Ontime's systems. Although we have security program to monitor and eliminate virus/malware, we also advise that in keeping with good computing practice the recipient should ensure they are actually virus/malwares free.
**********************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsdev/attachments/20250131/6c7c01fa/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4031 bytes
Desc: image001.jpg
URL: <http://alioth-lists.debian.net/pipermail/nut-upsdev/attachments/20250131/6c7c01fa/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Powercom?s Cleanline T-1500 UPS model.png
Type: image/png
Size: 1720860 bytes
Desc: Powercom?s Cleanline T-1500 UPS model.png
URL: <http://alioth-lists.debian.net/pipermail/nut-upsdev/attachments/20250131/6c7c01fa/attachment-0001.png>
-------------- next part --------------
2023-08-19T21:01:23.000000+07:00 PPL404I-112 boot[1062] ********************* PWR logger-Power Up(syslog) *******************
2023-08-19T21:02:09.899836+07:00 PPL404I-112 : [origin software="rsyslogd" swVersion="8.2110.0" x-pid="3237" x-info="https://www.rsyslog.com"] start
2023-08-19T21:02:17.574925+07:00 PPL404I-112 netifd: Interface 'lan' is enabled
2023-08-19T21:02:17.593870+07:00 PPL404I-112 netifd: Interface 'lan' is now up
2023-08-19T21:02:17.750734+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T21:02:17.754789+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T21:02:18.319623+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T21:02:18.322773+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T21:02:18.335565+07:00 PPL404I-112 netifd: Interface 'loopback' is enabled
2023-08-19T21:02:18.349058+07:00 PPL404I-112 netifd: Interface 'loopback' is now up
2023-08-19T21:02:18.469042+07:00 PPL404I-112 netifd: Interface 'loopback' has link connectivity
2023-08-19T21:03:01.076794+07:00 PPL404I-112 mount_root: performing overlay whiteout
2023-08-19T21:03:01.094361+07:00 PPL404I-112 mount_root: synchronizing overlay
2023-08-19T21:03:03.823783+07:00 PPL404I-112 mount_root: failed to sync jffs2 overlay
2023-08-19T21:03:04.026889+07:00 PPL404I-112 procd: /etc/rc.d/S96led: setting up led lan4
2023-08-19T21:03:04.057303+07:00 PPL404I-112 procd: /etc/rc.d/S96led: setting up led lan3
2023-08-19T21:03:04.087544+07:00 PPL404I-112 procd: /etc/rc.d/S96led: setting up led lan2
2023-08-19T21:03:04.117803+07:00 PPL404I-112 procd: /etc/rc.d/S96led: setting up led lan1
2023-08-19T21:03:04.147972+07:00 PPL404I-112 procd: /etc/rc.d/S96led: setting up led wan
2023-08-19T21:03:06.866795+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/pre_zl502.sh
2023-08-19T21:03:07.243849+07:00 PPL404I-112 urandom_seed[3920]: Seed saved (/etc/urandom.seed)
2023-08-19T21:03:14.496260+07:00 PPL404I-112 root: service QoS Stop ...
2023-08-19T21:03:15.129140+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2023-08-19T21:03:16.777914+07:00 PPL404I-112 root: [usb_upsd]...Stopped
2023-08-19T21:03:22.542857+07:00 PPL404I-112 : [origin software="rsyslogd" swVersion="8.2110.0" x-pid="4716" x-info="https://www.rsyslog.com"] start
2023-08-19T21:03:22.698596+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/post_zl502.sh
2023-08-19T21:03:23.154963+07:00 PPL404I-112 root: service iptables Stop ...
2023-08-19T21:03:29.426692+07:00 PPL404I-112 root: service QoS Stop ...
2023-08-19T21:03:29.787026+07:00 PPL404I-112 dropbear[5350]: Child connection from 192.168.99.55:60607
2023-08-19T21:03:30.284885+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2023-08-19T21:03:31.287002+07:00 PPL404I-112 procd: - init complete -
2023-08-19T21:03:33.712275+07:00 PPL404I-112 root: [usb_upsd]...Stopped
2023-08-19T21:03:36.263326+07:00 PPL404I-112 root: service iptables Stop ...
2023-08-19T21:03:37.649082+07:00 PPL404I-112 root: service iptables Starting ...
2023-08-19T21:03:46.873776+07:00 PPL404I-112 dropbear[5350]: Password auth succeeded for 'admin' from 192.168.99.55:60607
2023-08-19T21:03:54.061711+07:00 PPL404I-112 CLI-admin[5350]: CLI
2023-08-19T21:03:54.696588+07:00 PPL404I-112 CLI-admin[5350]: CLI/status
2023-08-19T21:05:29.372934+07:00 PPL404I-112 CLI-admin[5350]: CLI/status/exit
2023-08-19T21:05:29.375523+07:00 PPL404I-112 CLI-admin[5350]: CLI
2023-08-19T21:05:29.850637+07:00 PPL404I-112 CLI-admin[5350]: CLI/config
2023-08-19T21:05:30.137665+07:00 PPL404I-112 CLI-admin[5350]: CLI/config/cli_upload
2023-08-19T21:05:32.793551+07:00 PPL404I-112 CLI-admin[5350]: CLI/config/write_config
2023-08-19T21:05:32.886342+07:00 PPL404I-112 root: CLI-admin[5350]:CLI/config/write_config_CHANGE:cli.startup.disableservice=agentd squid usb_upsd serial_upsd log xl2tpd dnsmasq keepalived odhcpd qos dot1x -> agentd squid serial_upsd log xl2tpd dnsmasq keepalived odhcpd qos dot1x
2023-08-19T21:05:32.933318+07:00 PPL404I-112 root: CLI-admin[5350]:CLI/config/write_config_CHANGE:cli.startup.enableservice=iptables -> iptables usb_upsd
2023-08-19T21:05:32.970008+07:00 PPL404I-112 root: CLI-admin[5350]:CLI/config/write_config_CHANGE:cli.startup.stop_as_reboot=iptables -> squid
2023-08-19T21:05:33.424122+07:00 PPL404I-112 CLI-admin[5350]: CLI/config/save_running_2flash
2023-08-19T21:05:34.293325+07:00 PPL404I-112 CLI-admin[5350]: CLI/config/exit
2023-08-19T21:05:34.295916+07:00 PPL404I-112 CLI-admin[5350]: CLI
2023-08-19T21:05:34.610059+07:00 PPL404I-112 CLI-admin[5350]: CLI/status
2023-08-19T21:05:35.653877+07:00 PPL404I-112 CLI-admin[5350]: CLI/status/reboot
2023-08-19T21:05:35.689666+07:00 PPL404I-112 procd: - shutdown -
2023-08-19T21:05:36.885986+07:00 PPL404I-112 reboot[7701]: ********************* logger-Reboot/Power Down *******************
2023-08-19T21:05:49.000000+07:00 PPL404I-112 boot[871] ********************* PWR logger-Power Up(syslog) *******************
2023-08-19T21:06:19.867329+07:00 PPL404I-112 : [origin software="rsyslogd" swVersion="8.2110.0" x-pid="2502" x-info="https://www.rsyslog.com"] start
2023-08-19T21:06:24.262509+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/pre_zl502.sh
2023-08-19T21:06:29.162773+07:00 PPL404I-112 root: service QoS Stop ...
2023-08-19T21:06:29.676175+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2023-08-19T21:06:30.730386+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN4 link down
2023-08-19T21:06:31.000326+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN3 link down
2023-08-19T21:06:31.231559+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2023-08-19T21:06:31.470125+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN1 link up
2023-08-19T21:06:31.622387+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: wan link down
2023-08-19T21:06:33.190110+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/post_zl502.sh
2023-08-19T21:06:34.731948+07:00 PPL404I-112 root: service iptables Stop ...
2023-08-19T21:06:40.630388+07:00 PPL404I-112 root: service QoS Stop ...
2023-08-19T21:06:40.761775+07:00 PPL404I-112 procd: - init complete -
2023-08-19T21:06:42.384718+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2023-08-19T21:06:45.142091+07:00 PPL404I-112 root: [usb_upsd]...Stopped
2023-08-19T21:06:45.547068+07:00 PPL404I-112 root: service iptables Stop ...
2023-08-19T21:06:46.934705+07:00 PPL404I-112 root: service iptables Starting ...
2023-08-19T21:06:53.378196+07:00 PPL404I-112 netifd: Interface 'lan' is enabled
2023-08-19T21:06:53.392948+07:00 PPL404I-112 netifd: Interface 'lan' is now up
2023-08-19T21:06:53.796553+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T21:06:53.800564+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T21:06:54.072630+07:00 PPL404I-112 root: [nut-server-usb]...Stopped
2023-08-19T21:06:54.322793+07:00 PPL404I-112 root: [usb_upsd]...Started
2023-08-19T21:06:54.336915+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T21:06:54.340190+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T21:06:54.353951+07:00 PPL404I-112 netifd: Interface 'loopback' is enabled
2023-08-19T21:06:54.360262+07:00 PPL404I-112 netifd: Interface 'loopback' is now up
2023-08-19T21:06:54.585251+07:00 PPL404I-112 netifd: Interface 'loopback' has link connectivity
2023-08-19T21:07:04.408292+07:00 PPL404I-112 root: [nut-server-usb]...Stopped
2023-08-19T21:07:06.111381+07:00 PPL404I-112 upsd-usbd[5208]: listening on 127.0.0.1 port 6490
2023-08-19T21:07:06.290139+07:00 PPL404I-112 root: [nut-server-usb]...Started
2023-08-19T21:07:06.292024+07:00 PPL404I-112 upsd-usbd[5209]: Startup successful
2023-08-19T21:07:16.759065+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2023-08-19T21:07:19.840070+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:2/3
2023-08-19T21:07:20.858567+07:00 PPL404I-112 dropbear[5431]: Child connection from 192.168.99.55:61559
2023-08-19T21:07:22.957189+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:3/3
2023-08-19T21:07:23.612976+07:00 PPL404I-112 dropbear[5431]: Password auth succeeded for 'admin' from 192.168.99.55:61559
2023-08-19T21:07:26.044023+07:00 PPL404I-112 u_main.pl: Uupsd:COMMUNICATION LOST-pls. check ups's connection
2023-08-19T21:07:26.675208+07:00 PPL404I-112 u_main.pl: Uupsd:Start-Service:AC-Status=0:UPS-Status=:Manual-Shutdown=1:Beeper=enabled
2023-08-19T21:07:26.815726+07:00 PPL404I-112 u_main.pl: Uupsd:UPS-Beeper=>Enable
2023-08-19T21:07:28.964514+07:00 PPL404I-112 hu_sys.pl: Uupsd:Syslog_Interval=300
2023-08-19T21:07:35.156364+07:00 PPL404I-112 CLI-admin[5431]: CLI
2023-08-19T21:07:35.780644+07:00 PPL404I-112 CLI-admin[5431]: CLI/status
2023-08-19T21:07:37.519594+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/log0_trace -n 205
2023-08-19T21:08:00.150894+07:00 PPL404I-112 crond[2639]: USER root pid 6876 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2023-08-19T21:08:07.171723+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2023-08-19T21:08:08.322779+07:00 PPL404I-112 blazer_usb[7375]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2023-08-19T21:08:08.573995+07:00 PPL404I-112 blazer_usb[7375]: Supported UPS detected with megatec protocol
2023-08-19T21:08:08.885592+07:00 PPL404I-112 blazer_usb[7375]: Vendor information read in 1 tries
2023-08-19T21:08:09.141577+07:00 PPL404I-112 blazer_usb[7375]: Warning information read in 1 tries
2023-08-19T21:08:09.621610+07:00 PPL404I-112 blazer_usb[7375]: Faultinfo information read in 1 tries
2023-08-19T21:08:09.623371+07:00 PPL404I-112 blazer_usb[7375]: No values provided for battery high/low voltages in ups.conf
2023-08-19T21:08:09.625487+07:00 PPL404I-112 blazer_usb[7375]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2023-08-19T21:08:09.627414+07:00 PPL404I-112 blazer_usb[7375]: Battery runtime will not be calculated (runtimecal not set)
2023-08-19T21:08:09.797715+07:00 PPL404I-112 blazer_usb[7375]: Battery information read in 1 tries
2023-08-19T21:08:11.248275+07:00 PPL404I-112 blazer_usb[7413]: Startup successful
2023-08-19T21:08:13.135375+07:00 PPL404I-112 upsd-usbd[5209]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2023-08-19T21:08:13.135584+07:00 PPL404I-112 blazer_usb[7413]: sock_connect: enabling asynchronous mode (auto)
2023-08-19T21:08:17.857033+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/ups_status
2023-08-19T21:08:21.404505+07:00 PPL404I-112 u_main.pl: Uupsd:COMMUNICATION RESTORED
2023-08-19T21:08:25.167355+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/ups_status
2023-08-19T21:08:30.480533+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/log0_trace -n 205
2023-08-19T21:08:47.174131+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/log0_trace -n 205
2023-08-19T21:08:54.772881+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/ups_status
2023-08-19T21:08:59.624130+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/log0_trace
2023-08-19T21:09:07.050581+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/log0_trace -n 205
2023-08-19T21:09:28.092217+07:00 PPL404I-112 upsd-usbd[5209]: Data for UPS [pcmusb] is stale - check driver
2023-08-19T21:09:29.270746+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2023-08-19T21:09:32.329146+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:2/3
2023-08-19T21:09:35.387564+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:3/3
2023-08-19T21:09:38.416010+07:00 PPL404I-112 u_main.pl: Uupsd:COMMUNICATION LOST-pls. check ups's connection
2023-08-19T21:09:44.668992+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2023-08-19T21:09:45.784340+07:00 PPL404I-112 blazer_usb[9945]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2023-08-19T21:09:45.999004+07:00 PPL404I-112 blazer_usb[9945]: Supported UPS detected with megatec protocol
2023-08-19T21:09:46.334578+07:00 PPL404I-112 blazer_usb[9945]: Vendor information read in 1 tries
2023-08-19T21:09:46.670655+07:00 PPL404I-112 blazer_usb[9945]: Warning information read in 1 tries
2023-08-19T21:09:46.998606+07:00 PPL404I-112 blazer_usb[9945]: Faultinfo information read in 1 tries
2023-08-19T21:09:47.000057+07:00 PPL404I-112 blazer_usb[9945]: No values provided for battery high/low voltages in ups.conf
2023-08-19T21:09:47.001677+07:00 PPL404I-112 blazer_usb[9945]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2023-08-19T21:09:47.002002+07:00 PPL404I-112 blazer_usb[9945]: Battery runtime will not be calculated (runtimecal not set)
2023-08-19T21:09:47.190677+07:00 PPL404I-112 blazer_usb[9945]: Battery information read in 1 tries
2023-08-19T21:09:48.715180+07:00 PPL404I-112 blazer_usb[10119]: Startup successful
2023-08-19T21:09:48.791636+07:00 PPL404I-112 upsd-usbd[5209]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2023-08-19T21:09:50.302657+07:00 PPL404I-112 blazer_usb[10119]: sock_connect: enabling asynchronous mode (auto)
2023-08-19T21:09:58.894199+07:00 PPL404I-112 u_main.pl: Uupsd:COMMUNICATION RESTORED
2023-08-19T21:10:13.740512+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/ups_status
2023-08-19T21:10:16.862788+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/version
2023-08-19T21:10:28.520441+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/log0_trace -n 205
2023-08-19T21:11:18.477807+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/ups_status
2023-08-19T21:13:08.658147+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/ups_cmd --help
2023-08-19T21:13:17.649528+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/ups_cmd 127.0.0.1 1622 .1.3.6.1.2.1.33.1.2.28=1
2023-08-19T21:13:30.790936+07:00 PPL404I-112 dropbear[16058]: Child connection from 192.168.99.55:58886
2023-08-19T21:13:40.232287+07:00 PPL404I-112 dropbear[16058]: Bad password attempt for 'root' from 192.168.99.55:58886
2023-08-19T21:13:45.058482+07:00 PPL404I-112 dropbear[16058]: Bad password attempt for 'root' from 192.168.99.55:58886
2023-08-19T21:13:48.820379+07:00 PPL404I-112 dropbear[16058]: Exit before auth from <192.168.99.55:58886>: (user 'root', 2 fails): Disconnect received
2023-08-19T21:14:21.828985+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2023-08-19T21:14:21.830058+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2023-08-19T21:14:22.504468+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN1 link down
2023-08-19T21:14:22.835788+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2023-08-19T21:14:22.835899+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2023-08-19T21:14:27.092117+07:00 PPL404I-112 upsd-usbd[5209]: Data for UPS [pcmusb] is stale - check driver
2023-08-19T21:14:27.110439+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2023-08-19T21:14:30.168607+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:2/3
2023-08-19T21:14:33.227400+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:3/3
2023-08-19T21:14:36.255561+07:00 PPL404I-112 u_main.pl: Uupsd:COMMUNICATION LOST-pls. check ups's connection
2023-08-19T21:14:51.868486+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T21:14:51.869772+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T21:14:51.877481+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T21:14:51.877565+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T21:14:52.339490+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2023-08-19T21:18:20.986259+07:00 PPL404I-112 dropbear[5431]: Exit (admin) from <192.168.99.55:61559>: Error reading: Connection reset by peer
2023-08-19T21:18:20.992782+07:00 PPL404I-112 CLI-admin[5431]: CLI/status/EOF
2023-08-19T21:19:43.611500+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2023-08-19T21:19:43.612550+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2023-08-19T21:19:44.647134+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2023-08-19T21:19:44.675924+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2023-08-19T21:19:44.676011+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2023-08-19T21:19:53.550042+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T21:19:53.551537+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T21:19:53.556294+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T21:19:53.556379+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T21:19:54.399860+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2023-08-19T21:19:57.021127+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2023-08-19T21:19:57.022169+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2023-08-19T21:19:57.872801+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2023-08-19T21:19:58.035771+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2023-08-19T21:19:58.035855+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2023-08-19T21:19:59.445743+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T21:19:59.447327+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T21:19:59.454405+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T21:19:59.454489+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T21:20:01.124803+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2023-08-19T21:25:27.955499+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2023-08-19T21:25:28.035851+07:00 PPL404I-112 upsd-usbd[5209]: Can't connect to UPS [pcmusb] (blazer_usb-pcmusb): Connection refused
2023-08-19T21:25:29.084800+07:00 PPL404I-112 blazer_usb[29224]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2023-08-19T21:25:29.743913+07:00 PPL404I-112 blazer_usb[29224]: Supported UPS detected with megatec protocol
2023-08-19T21:25:30.063575+07:00 PPL404I-112 blazer_usb[29224]: Vendor information read in 1 tries
2023-08-19T21:25:30.279577+07:00 PPL404I-112 blazer_usb[29224]: Warning information read in 1 tries
2023-08-19T21:25:30.599605+07:00 PPL404I-112 blazer_usb[29224]: Faultinfo information read in 1 tries
2023-08-19T21:25:30.601026+07:00 PPL404I-112 blazer_usb[29224]: No values provided for battery high/low voltages in ups.conf
2023-08-19T21:25:30.602632+07:00 PPL404I-112 blazer_usb[29224]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2023-08-19T21:25:30.604118+07:00 PPL404I-112 blazer_usb[29224]: Battery runtime will not be calculated (runtimecal not set)
2023-08-19T21:25:30.935688+07:00 PPL404I-112 blazer_usb[29224]: Battery information read in 1 tries
2023-08-19T21:25:32.402287+07:00 PPL404I-112 blazer_usb[29288]: Startup successful
2023-08-19T21:25:34.042656+07:00 PPL404I-112 upsd-usbd[5209]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2023-08-19T21:25:34.044317+07:00 PPL404I-112 blazer_usb[29288]: sock_connect: enabling asynchronous mode (auto)
2023-08-19T21:25:36.206533+07:00 PPL404I-112 dropbear[29325]: Child connection from 192.168.99.55:49683
2023-08-19T21:25:38.403024+07:00 PPL404I-112 dropbear[29325]: Password auth succeeded for 'admin' from 192.168.99.55:49683
2023-08-19T21:25:40.624404+07:00 PPL404I-112 CLI-admin[29325]: CLI
2023-08-19T21:25:42.160663+07:00 PPL404I-112 CLI-admin[29325]: CLI/config
2023-08-19T21:25:42.377245+07:00 PPL404I-112 u_main.pl: Uupsd:COMMUNICATION RESTORED
2023-08-19T21:26:14.005663+07:00 PPL404I-112 CLI-admin[29325]: CLI/status
2023-08-19T21:26:15.163897+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/log0_trace -n 205
2023-08-19T21:26:21.436329+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/ups_status
2023-08-19T21:26:31.493993+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/ups_cmd 127.0.0.1 1621 .1.3.6.1.2.1.33.1.1.27=1
2023-08-19T21:26:32.142258+07:00 PPL404I-112 u_main.pl: Uupsd:RECEIVED-Test-Battery-10s
2023-08-19T21:26:33.322691+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/log0_trace
2023-08-19T21:26:35.498872+07:00 PPL404I-112 u_main.pl: Uupsd:Current-BatteryMinuteRemaining=>Alert:224.0
2023-08-19T21:26:35.584027+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Test_Inprogress:Start=2023-08-19 21-26-35:End=:AC-Status=0:UPS-Status=OL CAL:Load=0:Battery-Charge=:Battery-Volt=40.50:Battery-Capacity=99.0:Battery-Remaining-Time=224.0
2023-08-19T21:26:46.111701+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Done:Start=2023-08-19 21-26-35:End=2023-08-19 21-26-46:AC-Status=0:UPS-Status=OL:Load=0:Battery-Charge=:Battery-Volt=41.04:Battery-Capacity=99.0:Battery-Remaining-Time=224.0
2023-08-19T21:27:19.057338+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/ups_cmd 127.0.0.1 1621 .1.3.6.1.2.1.33.1.1.28=1
2023-08-19T21:27:19.625464+07:00 PPL404I-112 u_main.pl: Uupsd:RECEIVED-Test-Battery-1m
2023-08-19T21:27:22.160146+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/log0_trace -n 250
2023-08-19T21:27:22.195590+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-1m=>Test_Inprogress:Start=2023-08-19 21-27-22:End=:AC-Status=0:UPS-Status=OL CAL:Load=0:Battery-Charge=:Battery-Volt=40.68:Battery-Capacity=99.0:Battery-Remaining-Time=224.0
2023-08-19T21:28:20.947795+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-1m=>Done:Start=2023-08-19 21-27-22:End=2023-08-19 21-28-20:AC-Status=0:UPS-Status=OL:Load=0:Battery-Charge=:Battery-Volt=42.30:Battery-Capacity=99.0:Battery-Remaining-Time=223.0
2023-08-19T21:31:40.749633+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/log0_trace -n 205
2023-08-19T21:33:14.519695+07:00 PPL404I-112 CLI-admin[29325]: CLI/status/log0_trace -n 205
2023-08-19T21:34:23.222159+07:00 PPL404I-112 dropbear[19645]: Child connection from 192.168.99.55:49754
2023-08-19T21:35:01.798571+07:00 PPL404I-112 dropbear[19645]: Password auth succeeded for 'root' from 192.168.99.55:49754
2023-08-19T21:47:00.760961+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2023-08-19T21:47:00.762006+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2023-08-19T21:47:01.718585+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2023-08-19T21:47:01.795975+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2023-08-19T21:47:01.796061+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2023-08-19T21:52:40.026307+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T21:52:40.027597+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T21:52:40.036298+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T21:52:40.036382+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T21:52:40.472840+07:00 PPL404I-112 dropbear[19645]: Exit (root) from <192.168.99.55:49754>: Error reading: Connection reset by peer
2023-08-19T21:52:40.474199+07:00 PPL404I-112 dropbear[29325]: Exit (admin) from <192.168.99.55:49683>: Error reading: Connection reset by peer
2023-08-19T21:52:42.461429+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN1 link up
2023-08-19T22:08:00.212969+07:00 PPL404I-112 crond[2639]: USER root pid 1385 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2023-08-19T22:54:12.479153+07:00 PPL404I-112 upsd-usbd[5209]: Data for UPS [pcmusb] is stale - check driver
2023-08-19T22:54:12.497589+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2023-08-19T22:54:12.529251+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2023-08-19T22:54:12.610160+07:00 PPL404I-112 upsd-usbd[5209]: Can't connect to UPS [pcmusb] (blazer_usb-pcmusb): Connection refused
2023-08-19T22:54:13.610227+07:00 PPL404I-112 blazer_usb[954]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2023-08-19T22:54:14.064004+07:00 PPL404I-112 blazer_usb[954]: Supported UPS detected with megatec protocol
2023-08-19T22:54:14.543567+07:00 PPL404I-112 blazer_usb[954]: Vendor information read in 1 tries
2023-08-19T22:54:14.759580+07:00 PPL404I-112 blazer_usb[954]: Warning information read in 1 tries
2023-08-19T22:54:15.087608+07:00 PPL404I-112 blazer_usb[954]: Faultinfo information read in 1 tries
2023-08-19T22:54:15.089050+07:00 PPL404I-112 blazer_usb[954]: No values provided for battery high/low voltages in ups.conf
2023-08-19T22:54:15.091042+07:00 PPL404I-112 blazer_usb[954]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2023-08-19T22:54:15.092547+07:00 PPL404I-112 blazer_usb[954]: Battery runtime will not be calculated (runtimecal not set)
2023-08-19T22:54:15.279684+07:00 PPL404I-112 blazer_usb[954]: Battery information read in 1 tries
2023-08-19T22:54:16.922480+07:00 PPL404I-112 blazer_usb[1005]: Startup successful
2023-08-19T22:54:18.615299+07:00 PPL404I-112 upsd-usbd[5209]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2023-08-19T22:54:18.616936+07:00 PPL404I-112 blazer_usb[1005]: sock_connect: enabling asynchronous mode (auto)
2023-08-19T23:07:11.000000+07:00 PPL404I-112 boot[905] ********************* PWR logger-Power Up(syslog) *******************
2023-08-19T23:07:42.623244+07:00 PPL404I-112 : [origin software="rsyslogd" swVersion="8.2110.0" x-pid="2546" x-info="https://www.rsyslog.com"] start
2023-08-19T23:07:46.879465+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/pre_zl502.sh
2023-08-19T23:07:51.634506+07:00 PPL404I-112 root: service QoS Stop ...
2023-08-19T23:07:52.152207+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2023-08-19T23:07:53.389016+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN4 link down
2023-08-19T23:07:53.693070+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN3 link down
2023-08-19T23:07:53.882456+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2023-08-19T23:07:54.010956+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN1 link down
2023-08-19T23:07:54.142391+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: wan link down
2023-08-19T23:07:55.667119+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/post_zl502.sh
2023-08-19T23:07:59.064655+07:00 PPL404I-112 root: service iptables Stop ...
2023-08-19T23:08:00.617947+07:00 PPL404I-112 crond[2683]: USER root pid 4080 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2023-08-19T23:08:02.300632+07:00 PPL404I-112 procd: - init complete -
2023-08-19T23:08:02.966390+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2023-08-19T23:08:03.303463+07:00 PPL404I-112 root: service QoS Stop ...
2023-08-19T23:08:07.753907+07:00 PPL404I-112 root: [usb_upsd]...Stopped
2023-08-19T23:08:09.312228+07:00 PPL404I-112 root: service iptables Stop ...
2023-08-19T23:08:10.880381+07:00 PPL404I-112 root: service iptables Starting ...
2023-08-19T23:08:16.282288+07:00 PPL404I-112 root: [nut-server-usb]...Stopped
2023-08-19T23:08:16.374744+07:00 PPL404I-112 netifd: Interface 'lan' is enabled
2023-08-19T23:08:16.398426+07:00 PPL404I-112 netifd: Interface 'lan' is now up
2023-08-19T23:08:16.421558+07:00 PPL404I-112 root: [usb_upsd]...Started
2023-08-19T23:08:17.536234+07:00 PPL404I-112 netifd: Interface 'loopback' is enabled
2023-08-19T23:08:17.545228+07:00 PPL404I-112 netifd: Interface 'loopback' is now up
2023-08-19T23:08:17.655464+07:00 PPL404I-112 netifd: Interface 'loopback' has link connectivity
2023-08-19T23:08:28.025357+07:00 PPL404I-112 root: [nut-server-usb]...Stopped
2023-08-19T23:08:29.407728+07:00 PPL404I-112 blazer_usb[5368]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2023-08-19T23:08:29.641919+07:00 PPL404I-112 blazer_usb[5368]: Supported UPS detected with megatec protocol
2023-08-19T23:08:30.121427+07:00 PPL404I-112 blazer_usb[5368]: Vendor information read in 1 tries
2023-08-19T23:08:30.377411+07:00 PPL404I-112 blazer_usb[5368]: Warning information read in 1 tries
2023-08-19T23:08:30.697442+07:00 PPL404I-112 blazer_usb[5368]: Faultinfo information read in 1 tries
2023-08-19T23:08:30.699200+07:00 PPL404I-112 blazer_usb[5368]: No values provided for battery high/low voltages in ups.conf
2023-08-19T23:08:30.701180+07:00 PPL404I-112 blazer_usb[5368]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2023-08-19T23:08:30.703036+07:00 PPL404I-112 blazer_usb[5368]: Battery runtime will not be calculated (runtimecal not set)
2023-08-19T23:08:30.873508+07:00 PPL404I-112 blazer_usb[5368]: Battery information read in 1 tries
2023-08-19T23:08:32.481610+07:00 PPL404I-112 root: [nut-driver-usb]...Started
2023-08-19T23:08:32.483587+07:00 PPL404I-112 blazer_usb[5424]: Startup successful
2023-08-19T23:08:32.573124+07:00 PPL404I-112 upsd-usbd[5426]: listening on 127.0.0.1 port 6490
2023-08-19T23:08:32.578247+07:00 PPL404I-112 upsd-usbd[5426]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2023-08-19T23:08:32.697938+07:00 PPL404I-112 upsd-usbd[5427]: Startup successful
2023-08-19T23:08:32.702933+07:00 PPL404I-112 root: [nut-server-usb]...Started
2023-08-19T23:08:33.953648+07:00 PPL404I-112 blazer_usb[5424]: sock_connect: enabling asynchronous mode (auto)
2023-08-19T23:08:43.597805+07:00 PPL404I-112 u_main.pl: Uupsd:Current load='0' vs Threshold='50'
2023-08-19T23:08:43.602882+07:00 PPL404I-112 u_main.pl: Uupsd:Current Battery_MinuteRemaining='225.0' vs Threshold='252'
2023-08-19T23:08:43.605498+07:00 PPL404I-112 u_main.pl: Uupsd:Current temperature='22.7' vs Threshold='50'
2023-08-19T23:08:43.743973+07:00 PPL404I-112 u_main.pl: Uupsd:Start-Service:AC-Status=0:UPS-Status=OL:Manual-Shutdown=0:Beeper=enabled
2023-08-19T23:08:43.748783+07:00 PPL404I-112 u_main.pl: Uupsd:UPS-Beeper=>Enable
2023-08-19T23:08:44.652927+07:00 PPL404I-112 hu_sys.pl: Uupsd:Syslog_Interval=300
2023-08-19T23:14:55.340208+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T23:14:55.344164+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T23:14:55.355105+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T23:14:55.357089+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T23:14:55.808385+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN1 link up
2023-08-19T23:15:06.627976+07:00 PPL404I-112 dropbear[14923]: Child connection from 192.168.99.55:57585
2023-08-19T23:15:11.116001+07:00 PPL404I-112 dropbear[14923]: Password auth succeeded for 'admin' from 192.168.99.55:57585
2023-08-19T23:15:19.481369+07:00 PPL404I-112 CLI-admin[14923]: CLI
2023-08-19T23:15:20.651202+07:00 PPL404I-112 CLI-admin[14923]: CLI/status
2023-08-19T23:15:20.670610+07:00 PPL404I-112 CLI-admin[14923]: CLI/status/running_config | grep cli
2023-08-19T23:15:32.295414+07:00 PPL404I-112 CLI-admin[14923]: CLI/status/running_config | grep ups
2023-08-19T23:16:29.923717+07:00 PPL404I-112 CLI-admin[14923]: CLI/status/log0_trace
2023-08-19T23:16:34.622871+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2023-08-19T23:16:34.624423+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2023-08-19T23:16:35.025542+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN1 link down
2023-08-19T23:16:35.647960+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2023-08-19T23:16:35.648044+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2023-08-19T23:18:18.735563+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T23:18:18.742477+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T23:18:18.767934+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T23:18:18.768022+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T23:18:19.678730+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2023-08-19T23:18:19.970822+07:00 PPL404I-112 dropbear[14923]: Exit (admin) from <192.168.99.55:57585>: Error reading: Connection reset by peer
2023-08-19T23:18:21.149335+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2023-08-19T23:18:21.150391+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2023-08-19T23:18:22.207882+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2023-08-19T23:18:22.207969+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2023-08-19T23:18:22.939361+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2023-08-19T23:18:24.503606+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T23:18:24.504906+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T23:18:24.511181+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T23:18:24.511266+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T23:18:26.193644+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2023-08-19T23:19:01.519543+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2023-08-19T23:19:01.520593+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2023-08-19T23:19:01.930690+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2023-08-19T23:19:02.527841+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2023-08-19T23:19:02.527927+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2023-08-19T23:19:04.878474+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2023-08-19T23:19:04.879799+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2023-08-19T23:19:04.888037+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2023-08-19T23:19:04.888125+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2023-08-19T23:19:05.183832+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2023-08-19T23:20:19.446171+07:00 PPL404I-112 dropbear[22216]: Child connection from 192.168.99.55:61794
2023-08-19T23:20:23.090034+07:00 PPL404I-112 dropbear[22216]: Password auth succeeded for 'admin' from 192.168.99.55:61794
2023-08-19T23:20:25.688061+07:00 PPL404I-112 CLI-admin[22216]: CLI
2023-08-19T23:20:25.761441+07:00 PPL404I-112 CLI-admin[22216]: CLI/status
2023-08-19T23:20:27.883587+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/log0_trace -n 250
2023-08-19T23:24:36.554324+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/ups_status
2023-08-19T23:24:45.680728+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/log0_trace -n 2250 | grep driver
2023-08-19T23:24:53.580060+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/log0_trace -n 2250 | grep check
2023-08-19T23:25:15.780002+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/log0_trace -n 2500000 | grep stale
2023-08-19T23:25:22.076945+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/log0_trace
2023-08-19T23:29:25.079895+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/date -s '2025-01-24 14:10:00'
2025-01-24T14:10:23.062418+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T14:10:23.063468+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T14:10:24.091906+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T14:10:24.091991+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T14:10:25.652703+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T14:10:26.692384+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T14:10:26.693681+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T14:10:26.700455+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T14:10:26.700541+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T14:10:28.906529+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T14:10:31.909100+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T14:10:31.910151+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T14:10:32.159461+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T14:10:32.971967+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T14:10:32.972053+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T14:10:35.260568+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T14:10:35.263684+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T14:10:35.294359+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T14:10:35.294443+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T14:10:35.425932+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T14:10:35.551752+07:00 PPL404I-112 crond[2683]: time disparity of 754001 minutes detected
2025-01-24T14:10:38.778666+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T14:10:38.779750+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T14:10:39.771941+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T14:10:39.772025+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T14:10:41.942538+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T14:10:42.105134+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T14:10:42.106450+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T14:10:42.114072+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T14:10:42.114158+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T14:10:45.195700+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T14:11:19.208603+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T14:11:19.209654+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T14:11:20.251901+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T14:11:20.251987+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T14:11:21.925625+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T14:11:22.559250+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T14:11:22.560556+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T14:11:22.567790+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T14:11:22.567874+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T14:11:25.185026+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T14:12:37.302994+07:00 PPL404I-112 dropbear[5851]: Child connection from 192.168.99.55:57536
2025-01-24T14:12:39.816396+07:00 PPL404I-112 dropbear[5851]: Password auth succeeded for 'admin' from 192.168.99.55:57536
2025-01-24T14:12:42.219700+07:00 PPL404I-112 CLI-admin[5851]: CLI
2025-01-24T14:12:50.599791+07:00 PPL404I-112 CLI-admin[5851]: CLI/status
2025-01-24T14:12:52.104420+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/log0_trace -n 205
2025-01-24T14:12:59.769230+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/ups_status
2025-01-24T14:13:03.989687+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/log0_trace
2025-01-24T14:15:00.415744+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/ups_cmd 127.0.0.1 1621 .1.3.6.1.2.1.33.1.1.27=1
2025-01-24T14:15:00.582456+07:00 PPL404I-112 dropbear[22216]: Exit (admin) from <192.168.99.55:61794>: Error reading: Connection reset by peer
2025-01-24T14:15:00.588976+07:00 PPL404I-112 CLI-admin[22216]: CLI/status/EOF
2025-01-24T14:15:01.054356+07:00 PPL404I-112 u_main.pl: Uupsd:RECEIVED-Test-Battery-10s
2025-01-24T14:15:01.456796+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/log0_trace
2025-01-24T14:15:02.492998+07:00 PPL404I-112 u_main.pl: Uupsd:Current-BatteryMinuteRemaining=>Alert:225.0
2025-01-24T14:15:02.606445+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Test_Inprogress:Start=2025-01-24 14-15-02:End=:AC-Status=0:UPS-Status=OL CAL:Load=0:Battery-Charge=100:Battery-Volt=40.68:Battery-Capacity=100.0:Battery-Remaining-Time=225.0
2025-01-24T14:15:11.194960+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T14:15:11.196017+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T14:15:12.252120+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T14:15:12.252205+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T14:15:12.554544+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T14:15:13.114149+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T14:15:13.115470+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T14:15:13.262660+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T14:15:13.262746+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T14:15:14.249757+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Done:Start=2025-01-24 14-15-02:End=2025-01-24 14-15-14:AC-Status=0:UPS-Status=OL:Load=0:Battery-Charge=100:Battery-Volt=41.04:Battery-Capacity=99.0:Battery-Remaining-Time=225.0
2025-01-24T14:15:16.556512+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T14:19:01.424100+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/ups_cmd 127.0.0.1 1622 .1.3.6.1.2.1.33.1.2.31=1
2025-01-24T14:20:17.924522+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/ups_cmd 127.0.0.1 1621 .1.3.6.1.2.1.33.1.1.27=1
2025-01-24T14:20:18.448100+07:00 PPL404I-112 u_main.pl: Uupsd:RECEIVED-Test-Battery-10s
2025-01-24T14:20:19.158021+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/log0_trace
2025-01-24T14:20:21.806342+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Test_Inprogress:Start=2025-01-24 14-20-21:End=:AC-Status=0:UPS-Status=OL CAL:Load=0:Battery-Charge=100:Battery-Volt=40.68:Battery-Capacity=99.0:Battery-Remaining-Time=225.0
2025-01-24T14:20:29.114539+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T14:20:29.115568+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T14:20:30.172037+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T14:20:30.172123+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T14:20:30.802475+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T14:20:31.094286+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T14:20:31.095545+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T14:20:31.103154+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T14:20:31.103239+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T14:20:31.530546+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Done:Start=2025-01-24 14-20-21:End=2025-01-24 14-20-31:AC-Status=0:UPS-Status=OL:Load=0:Battery-Charge=100:Battery-Volt=42.84:Battery-Capacity=99.0:Battery-Remaining-Time=225.0
2025-01-24T14:20:34.177267+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T14:21:02.462675+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/log0_trace
2025-01-24T14:22:34.876187+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/ups_status
2025-01-24T14:24:15.653258+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/ups_cmd 127.0.0.1 1621 .1.3.6.1.2.1.33.1.1.27=1
2025-01-24T14:24:16.069826+07:00 PPL404I-112 u_main.pl: Uupsd:RECEIVED-Test-Battery-10s
2025-01-24T14:24:17.027191+07:00 PPL404I-112 CLI-admin[5851]: CLI/status/log0_trace
2025-01-24T14:24:19.424980+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Test_Inprogress:Start=2025-01-24 14-24-19:End=:AC-Status=0:UPS-Status=OL CAL:Load=0:Battery-Charge=100:Battery-Volt=40.68:Battery-Capacity=99.0:Battery-Remaining-Time=225.0
2025-01-24T14:24:29.125694+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Done:Start=2025-01-24 14-24-19:End=2025-01-24 14-24-29:AC-Status=0:UPS-Status=OL:Load=0:Battery-Charge=100:Battery-Volt=42.66:Battery-Capacity=99.0:Battery-Remaining-Time=225.0
2025-01-24T14:27:19.468254+07:00 PPL404I-112 dropbear[7365]: Child connection from 192.168.99.55:61016
2025-01-24T14:27:20.081939+07:00 PPL404I-112 dropbear[5851]: Exit (admin) from <192.168.99.55:57536>: Error reading: Connection reset by peer
2025-01-24T14:27:22.358904+07:00 PPL404I-112 dropbear[7365]: Password auth succeeded for 'admin' from 192.168.99.55:61016
2025-01-24T14:27:24.339007+07:00 PPL404I-112 CLI-admin[7365]: CLI
2025-01-24T14:27:27.799421+07:00 PPL404I-112 CLI-admin[7365]: CLI/status
2025-01-24T14:27:29.204222+07:00 PPL404I-112 CLI-admin[7365]: CLI/status/log0_trace -n 205
2025-01-24T14:30:15.000632+07:00 PPL404I-112 upsd-usbd[5427]: Data for UPS [pcmusb] is stale - check driver
2025-01-24T14:30:18.184424+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-24T14:30:18.222641+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-24T14:30:18.304472+07:00 PPL404I-112 upsd-usbd[5427]: Can't connect to UPS [pcmusb] (blazer_usb-pcmusb): Connection refused
2025-01-24T14:30:19.306076+07:00 PPL404I-112 blazer_usb[11258]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2025-01-24T14:30:19.925885+07:00 PPL404I-112 blazer_usb[11258]: Supported UPS detected with megatec protocol
2025-01-24T14:30:20.269552+07:00 PPL404I-112 blazer_usb[11258]: Vendor information read in 1 tries
2025-01-24T14:30:20.461473+07:00 PPL404I-112 blazer_usb[11258]: Warning information read in 1 tries
2025-01-24T14:30:20.805648+07:00 PPL404I-112 blazer_usb[11258]: Faultinfo information read in 1 tries
2025-01-24T14:30:20.805748+07:00 PPL404I-112 blazer_usb[11258]: No values provided for battery high/low voltages in ups.conf
2025-01-24T14:30:20.805905+07:00 PPL404I-112 blazer_usb[11258]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2025-01-24T14:30:20.805979+07:00 PPL404I-112 blazer_usb[11258]: Battery runtime will not be calculated (runtimecal not set)
2025-01-24T14:30:21.117576+07:00 PPL404I-112 blazer_usb[11258]: Battery information read in 1 tries
2025-01-24T14:30:22.600186+07:00 PPL404I-112 blazer_usb[11296]: Startup successful
2025-01-24T14:30:24.311289+07:00 PPL404I-112 upsd-usbd[5427]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2025-01-24T14:30:24.311516+07:00 PPL404I-112 blazer_usb[11296]: sock_connect: enabling asynchronous mode (auto)
2025-01-24T15:01:07.296067+07:00 PPL404I-112 upsd-usbd[5427]: Data for UPS [pcmusb] is stale - check driver
2025-01-24T15:01:08.475687+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-24T15:01:08.505000+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-24T15:01:08.586705+07:00 PPL404I-112 upsd-usbd[5427]: Can't connect to UPS [pcmusb] (blazer_usb-pcmusb): Connection refused
2025-01-24T15:01:09.640941+07:00 PPL404I-112 blazer_usb[21454]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2025-01-24T15:01:09.894050+07:00 PPL404I-112 blazer_usb[21454]: Supported UPS detected with megatec protocol
2025-01-24T15:01:10.221681+07:00 PPL404I-112 blazer_usb[21454]: Vendor information read in 1 tries
2025-01-24T15:01:10.613702+07:00 PPL404I-112 blazer_usb[21454]: Warning information read in 1 tries
2025-01-24T15:01:10.957860+07:00 PPL404I-112 blazer_usb[21454]: Faultinfo information read in 1 tries
2025-01-24T15:01:10.957959+07:00 PPL404I-112 blazer_usb[21454]: No values provided for battery high/low voltages in ups.conf
2025-01-24T15:01:10.958123+07:00 PPL404I-112 blazer_usb[21454]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2025-01-24T15:01:10.958198+07:00 PPL404I-112 blazer_usb[21454]: Battery runtime will not be calculated (runtimecal not set)
2025-01-24T15:01:11.133679+07:00 PPL404I-112 blazer_usb[21454]: Battery information read in 1 tries
2025-01-24T15:01:12.616298+07:00 PPL404I-112 blazer_usb[21961]: Startup successful
2025-01-24T15:01:14.593588+07:00 PPL404I-112 upsd-usbd[5427]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2025-01-24T15:01:14.595218+07:00 PPL404I-112 blazer_usb[21961]: sock_connect: enabling asynchronous mode (auto)
2025-01-24T15:04:30.467286+07:00 PPL404I-112 CLI-admin[7365]: CLI/status/log0_trace
2025-01-24T15:04:53.830371+07:00 PPL404I-112 CLI-admin[7365]: CLI/status/log0_trace -n 25000000 | grep stale | grep check
2025-01-24T15:04:59.904764+07:00 PPL404I-112 CLI-admin[7365]: CLI/status/log0_trace -n 25000000 | grep stale
2025-01-24T15:05:07.754590+07:00 PPL404I-112 CLI-admin[7365]: CLI/status/log0_trace -n 205
2025-01-24T15:08:00.598561+07:00 PPL404I-112 crond[2683]: USER root pid 31107 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-24T15:23:39.541509+07:00 PPL404I-112 dropbear[7365]: Exit (admin) from <192.168.99.55:61016>: Keepalive timeout
2025-01-24T15:31:07.351172+07:00 PPL404I-112 dropbear[30426]: Child connection from 192.168.99.55:64486
2025-01-24T15:31:10.120047+07:00 PPL404I-112 dropbear[30426]: Password auth succeeded for 'admin' from 192.168.99.55:64486
2025-01-24T15:31:12.415250+07:00 PPL404I-112 CLI-admin[30426]: CLI
2025-01-24T15:31:12.501331+07:00 PPL404I-112 CLI-admin[30426]: CLI/status
2025-01-24T15:31:14.582880+07:00 PPL404I-112 CLI-admin[30426]: CLI/status/log0_trace -n 2500
2025-01-24T15:38:34.924819+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T15:38:34.925831+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T15:38:35.931891+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T15:38:35.931978+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T15:38:37.604198+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T15:38:38.278417+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T15:38:38.279257+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T15:38:38.286308+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T15:38:38.286390+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T15:38:39.941397+07:00 PPL404I-112 dropbear[30426]: Exit (admin) from <192.168.99.55:64486>: Error reading: Connection reset by peer
2025-01-24T15:38:40.968390+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T15:38:57.321025+07:00 PPL404I-112 dropbear[9062]: Child connection from 192.168.99.55:64148
2025-01-24T15:38:59.860847+07:00 PPL404I-112 dropbear[9062]: Password auth succeeded for 'admin' from 192.168.99.55:64148
2025-01-24T15:39:02.483823+07:00 PPL404I-112 CLI-admin[9062]: CLI
2025-01-24T15:39:02.558417+07:00 PPL404I-112 CLI-admin[9062]: CLI/status
2025-01-24T15:39:02.573926+07:00 PPL404I-112 CLI-admin[9062]: CLI/status/log0_trace -n 205
2025-01-24T15:44:44.993185+07:00 PPL404I-112 dropbear[16935]: Child connection from 192.168.99.55:65021
2025-01-24T15:44:46.446129+07:00 PPL404I-112 dropbear[16935]: Password auth succeeded for 'root' from 192.168.99.55:65021
2025-01-24T16:05:48.642813+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is down
2025-01-24T16:05:48.643454+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is down
2025-01-24T16:05:49.316328+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-24T16:05:49.691809+07:00 PPL404I-112 netifd: bridge 'br-lan' link is down
2025-01-24T16:05:49.691891+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity loss
2025-01-24T16:05:50.647867+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-24T16:05:50.648737+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-24T16:05:50.655749+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-24T16:05:50.655831+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-24T16:05:52.569708+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-24T16:08:00.648079+07:00 PPL404I-112 crond[2683]: USER root pid 16926 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-24T16:14:13.488978+07:00 PPL404I-112 upsd-usbd[5427]: Data for UPS [pcmusb] is stale - check driver
2025-01-24T16:14:14.670026+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-24T16:14:14.699493+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-24T16:14:14.781976+07:00 PPL404I-112 upsd-usbd[5427]: Can't connect to UPS [pcmusb] (blazer_usb-pcmusb): Connection refused
2025-01-24T16:14:15.785517+07:00 PPL404I-112 blazer_usb[25528]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2025-01-24T16:14:15.997890+07:00 PPL404I-112 blazer_usb[25528]: Supported UPS detected with megatec protocol
2025-01-24T16:14:16.341499+07:00 PPL404I-112 blazer_usb[25528]: Vendor information read in 1 tries
2025-01-24T16:14:16.693473+07:00 PPL404I-112 blazer_usb[25528]: Warning information read in 1 tries
2025-01-24T16:14:17.037702+07:00 PPL404I-112 blazer_usb[25528]: Faultinfo information read in 1 tries
2025-01-24T16:14:17.037800+07:00 PPL404I-112 blazer_usb[25528]: No values provided for battery high/low voltages in ups.conf
2025-01-24T16:14:17.037957+07:00 PPL404I-112 blazer_usb[25528]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2025-01-24T16:14:17.038033+07:00 PPL404I-112 blazer_usb[25528]: Battery runtime will not be calculated (runtimecal not set)
2025-01-24T16:14:17.213581+07:00 PPL404I-112 blazer_usb[25528]: Battery information read in 1 tries
2025-01-24T16:14:18.776386+07:00 PPL404I-112 blazer_usb[25579]: Startup successful
2025-01-24T16:14:18.786024+07:00 PPL404I-112 upsd-usbd[5427]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2025-01-24T16:14:20.405533+07:00 PPL404I-112 blazer_usb[25579]: sock_connect: enabling asynchronous mode (auto)
2025-01-24T16:44:28.538618+07:00 PPL404I-112 CLI-admin[9062]: CLI/status/log0_trace -n 2500 | grep check
2025-01-24T16:55:42.094001+07:00 PPL404I-112 dropbear[17756]: Child connection from 192.168.99.55:52702
2025-01-24T16:55:42.642396+07:00 PPL404I-112 dropbear[17756]: Password auth succeeded for 'root' from 192.168.99.55:52702
2025-01-24T16:56:17.480966+07:00 PPL404I-112 dropbear[4402]: Exit (root) from <192.168.99.55:49224>: Error reading: Connection reset by peer
2025-01-24T16:56:22.858238+07:00 PPL404I-112 dropbear[18705]: Child connection from 192.168.99.55:52728
2025-01-24T16:56:25.368052+07:00 PPL404I-112 dropbear[18705]: Password auth succeeded for 'admin' from 192.168.99.55:52728
2025-01-24T16:56:27.972648+07:00 PPL404I-112 CLI-admin[18705]: CLI
2025-01-24T16:56:30.226945+07:00 PPL404I-112 dropbear[18866]: Child connection from 192.168.99.55:52730
2025-01-24T16:56:32.977096+07:00 PPL404I-112 dropbear[18866]: Password auth succeeded for 'root' from 192.168.99.55:52730
2025-01-24T17:00:16.618293+07:00 PPL404I-112 upsd-usbd[5427]: Data for UPS [pcmusb] is stale - check driver
2025-01-24T17:00:17.887306+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-24T17:00:17.909707+07:00 PPL404I-112 dropbear[17255]: Exit (root) from <192.168.99.55:52686>: Error reading: Connection reset by peer
2025-01-24T17:00:17.951576+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-24T17:00:18.058066+07:00 PPL404I-112 upsd-usbd[5427]: Can't connect to UPS [pcmusb] (blazer_usb-pcmusb): Connection refused
2025-01-24T17:00:19.056079+07:00 PPL404I-112 blazer_usb[24325]: Please note that this driver is deprecated and will not receive#012new development. If it works for managing your devices - fine,#012but if you are running it to try setting up a new device, please#012consider the newer nutdrv_qx instead, which should handle all 'Qx'#012protocol variants for NUT. (Please also report if your device works#012with this driver, but nutdrv_qx would not actually support it with#012any subdriver!)
2025-01-24T17:00:19.493815+07:00 PPL404I-112 blazer_usb[24325]: Supported UPS detected with megatec protocol
2025-01-24T17:00:19.965476+07:00 PPL404I-112 blazer_usb[24325]: Vendor information read in 1 tries
2025-01-24T17:00:20.173477+07:00 PPL404I-112 blazer_usb[24325]: Warning information read in 1 tries
2025-01-24T17:00:20.519541+07:00 PPL404I-112 blazer_usb[24325]: Faultinfo information read in 1 tries
2025-01-24T17:00:20.519638+07:00 PPL404I-112 blazer_usb[24325]: No values provided for battery high/low voltages in ups.conf
2025-01-24T17:00:20.519797+07:00 PPL404I-112 blazer_usb[24325]: Using 'guestimation' (low: 31.200000, high: 39.000000)!
2025-01-24T17:00:20.519876+07:00 PPL404I-112 blazer_usb[24325]: Battery runtime will not be calculated (runtimecal not set)
2025-01-24T17:00:20.829567+07:00 PPL404I-112 blazer_usb[24325]: Battery information read in 1 tries
2025-01-24T17:00:22.296338+07:00 PPL404I-112 blazer_usb[24376]: Startup successful
2025-01-24T17:00:24.063642+07:00 PPL404I-112 upsd-usbd[5427]: Connected to UPS [pcmusb]: blazer_usb-pcmusb
2025-01-24T17:00:24.065283+07:00 PPL404I-112 blazer_usb[24376]: sock_connect: enabling asynchronous mode (auto)
2025-01-24T17:08:00.699430+07:00 PPL404I-112 crond[2683]: USER root pid 2544 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-24T17:10:35.862769+07:00 PPL404I-112 CLI-admin[18705]: CLI/status
2025-01-24T17:10:37.382695+07:00 PPL404I-112 CLI-admin[18705]: CLI/status/log0_trace -n 205
2025-01-24T17:17:27.323280+07:00 PPL404I-112 CLI-admin[18705]: CLI/status/log0_trace -n 205
2025-01-24T17:18:25.177001+07:00 PPL404I-112 dropbear[17756]: Exit (root) from <192.168.99.55:52702>: Exited normally
2025-01-24T17:18:31.355819+07:00 PPL404I-112 dropbear[17291]: Child connection from 192.168.99.55:63690
2025-01-24T17:18:31.715204+07:00 PPL404I-112 dropbear[17291]: Password auth succeeded for 'root' from 192.168.99.55:63690
-------------- next part --------------
2025-01-29T16:56:32.000000+07:00 PPL404I-112 boot[904] ********************* PWR logger-Power Up(syslog) *******************
2025-01-29T16:57:01.629623+07:00 PPL404I-112 : [origin software="rsyslogd" swVersion="8.2110.0" x-pid="2343" x-info="https://www.rsyslog.com"] start
2025-01-29T16:57:05.917969+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/pre_zl502.sh
2025-01-29T16:57:10.177990+07:00 PPL404I-112 root: service QoS Stop ...
2025-01-29T16:57:10.569591+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2025-01-29T16:57:11.435186+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN4 link up
2025-01-29T16:57:11.705109+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN3 link down
2025-01-29T16:57:11.837841+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-29T16:57:11.968921+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN1 link down
2025-01-29T16:57:12.088005+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: wan link up
2025-01-29T16:57:14.287972+07:00 PPL404I-112 root: /opt/pp/CLI/sbin/post_zl502.sh
2025-01-29T16:57:14.786295+07:00 PPL404I-112 netifd: Interface 'lan' is enabled
2025-01-29T16:57:14.806437+07:00 PPL404I-112 netifd: Interface 'lan' is now up
2025-01-29T16:57:14.812078+07:00 PPL404I-112 netifd: bridge 'br-lan' link is up
2025-01-29T16:57:14.832910+07:00 PPL404I-112 netifd: Interface 'lan' has link connectivity
2025-01-29T16:57:15.518085+07:00 PPL404I-112 root: service iptables Stop ...
2025-01-29T16:57:21.384669+07:00 PPL404I-112 procd: - init complete -
2025-01-29T16:57:22.599863+07:00 PPL404I-112 root: service QoS Stop ...
2025-01-29T16:57:23.030891+07:00 PPL404I-112 root: [serial_upsd]...Stopped
2025-01-29T16:57:27.767963+07:00 PPL404I-112 root: [usb_upsd]...Stopped
2025-01-29T16:57:28.028640+07:00 PPL404I-112 root: service iptables Stop ...
2025-01-29T16:57:29.608181+07:00 PPL404I-112 root: service iptables Starting ...
2025-01-29T16:57:38.498806+07:00 PPL404I-112 netifd: VLAN 'eth0.1' link is up
2025-01-29T16:57:38.619843+07:00 PPL404I-112 netifd: Interface 'loopback' is enabled
2025-01-29T16:57:38.705448+07:00 PPL404I-112 netifd: Interface 'loopback' is now up
2025-01-29T16:57:38.730212+07:00 PPL404I-112 netifd: Interface 'wan' is enabled
2025-01-29T16:57:38.744839+07:00 PPL404I-112 netifd: Interface 'wan' is now up
2025-01-29T16:57:39.115236+07:00 PPL404I-112 netifd: Interface 'loopback' has link connectivity
2025-01-29T16:57:39.119386+07:00 PPL404I-112 netifd: VLAN 'eth0.2' link is up
2025-01-29T16:57:39.183022+07:00 PPL404I-112 netifd: Interface 'wan' has link connectivity
2025-01-29T16:57:39.221158+07:00 PPL404I-112 root: [nut-server-usb]...Stopped
2025-01-29T16:57:39.358038+07:00 PPL404I-112 root: [usb_upsd]...Started
2025-01-29T16:57:45.827626+07:00 PPL404I-112 dropbear[4943]: Child connection from 172.31.1.55:49918
2025-01-29T16:57:50.826266+07:00 PPL404I-112 dnsmasq[5076]: started, version 2.89 cachesize 150
2025-01-29T16:57:50.832993+07:00 PPL404I-112 dnsmasq[5076]: DNS service limited to local subnets
2025-01-29T16:57:50.838236+07:00 PPL404I-112 dnsmasq[5076]: UBus support enabled: connected to system bus
2025-01-29T16:57:50.840174+07:00 PPL404I-112 dnsmasq-dhcp[5076]: DHCP, IP range 192.168.99.200 -- 192.168.99.249, lease time 12h
2025-01-29T16:57:50.842287+07:00 PPL404I-112 dnsmasq[5076]: using nameserver 1.1.1.1#53
2025-01-29T16:57:50.846608+07:00 PPL404I-112 dnsmasq[5076]: using nameserver 8.8.8.8#53
2025-01-29T16:57:50.871622+07:00 PPL404I-112 dnsmasq[5076]: read /etc/hosts - 12 names
2025-01-29T16:57:50.873657+07:00 PPL404I-112 dnsmasq[5076]: read /tmp/hosts/dhcp.cfg01411c - 2 names
2025-01-29T16:57:51.309040+07:00 PPL404I-112 dnsmasq-dhcp[5076]: read /etc/ethers - 0 addresses
2025-01-29T16:57:54.178483+07:00 PPL404I-112 hostapd: ACS: Automatic channel selection started, this may take a bit
2025-01-29T16:57:54.197505+07:00 PPL404I-112 hostapd: wlan0: interface state UNINITIALIZED->ACS
2025-01-29T16:57:54.200482+07:00 PPL404I-112 hostapd: wlan0: ACS-STARTED
2025-01-29T16:57:55.790047+07:00 PPL404I-112 netifd: Wireless device 'radio0' is now up
2025-01-29T16:57:56.224521+07:00 PPL404I-112 hostapd: wlan0: ACS-COMPLETED freq=2437 channel=6
2025-01-29T16:57:59.055982+07:00 PPL404I-112 dropbear[4943]: Password auth succeeded for 'admin' from 172.31.1.55:49918
2025-01-29T16:57:59.987649+07:00 PPL404I-112 hostapd: wlan0: interface state ACS->ENABLED
2025-01-29T16:57:59.989133+07:00 PPL404I-112 hostapd: wlan0: AP-ENABLED
2025-01-29T16:58:01.485111+07:00 PPL404I-112 dropbear[5400]: Child connection from 192.168.99.55:50572
2025-01-29T16:58:03.085291+07:00 PPL404I-112 root: [nut-server-usb]...Stopped
2025-01-29T16:58:06.683281+07:00 PPL404I-112 nutdrv_qx[5434]: device.serial: UPS reported a non-significant serial [0000000000000000]
2025-01-29T16:58:39.990101+07:00 PPL404I-112 ntpdate[5052]: step time server 202.28.116.236 offset +32.624395 sec
2025-01-29T16:58:40.555852+07:00 PPL404I-112 nutdrv_qx[5434]: battery_number: 3
2025-01-29T16:58:40.555958+07:00 PPL404I-112 nutdrv_qx[5434]: battery_number, settable range: 1..9
2025-01-29T16:58:40.886013+07:00 PPL404I-112 dropbear[5400]: Password auth succeeded for 'admin' from 192.168.99.55:50572
2025-01-29T16:58:41.308906+07:00 PPL404I-112 nutdrv_qx[5434]: bypass_alarm: enabled
2025-01-29T16:58:41.310345+07:00 PPL404I-112 nutdrv_qx[5434]: battery_alarm: enabled
2025-01-29T16:58:41.311708+07:00 PPL404I-112 nutdrv_qx[5434]: bypass_when_off: enabled
2025-01-29T16:58:41.313463+07:00 PPL404I-112 nutdrv_qx[5434]: alarm_control: enabled
2025-01-29T16:58:41.313869+07:00 PPL404I-112 nutdrv_qx[5434]: converter_mode: disabled
2025-01-29T16:58:41.316781+07:00 PPL404I-112 nutdrv_qx[5434]: eco_mode: enabled
2025-01-29T16:58:41.319161+07:00 PPL404I-112 nutdrv_qx[5434]: bypass_forbidding: disabled
2025-01-29T16:58:41.319661+07:00 PPL404I-112 nutdrv_qx[5434]: site_fault_detection: disabled
2025-01-29T16:58:41.875732+07:00 PPL404I-112 nutdrv_qx[5434]: max_bypass_volt: 264
2025-01-29T16:58:41.875916+07:00 PPL404I-112 nutdrv_qx[5434]: max_bypass_volt, settable range: 230..264
2025-01-29T16:58:41.876059+07:00 PPL404I-112 nutdrv_qx[5434]: min_bypass_volt: 170
2025-01-29T16:58:41.876236+07:00 PPL404I-112 nutdrv_qx[5434]: min_bypass_volt, settable range: 170..220
2025-01-29T16:58:42.019747+07:00 PPL404I-112 nutdrv_qx[5434]: max_bypass_freq: 53.0
2025-01-29T16:58:42.019892+07:00 PPL404I-112 nutdrv_qx[5434]: max_bypass_freq, settable range: 51.0..60.0
2025-01-29T16:58:42.020065+07:00 PPL404I-112 nutdrv_qx[5434]: min_bypass_freq: 47.0
2025-01-29T16:58:42.020183+07:00 PPL404I-112 nutdrv_qx[5434]: min_bypass_freq, settable range: 40.0..49.0
2025-01-29T16:58:42.772368+07:00 PPL404I-112 root: [nut-driver-usb]...Started
2025-01-29T16:58:42.774061+07:00 PPL404I-112 nutdrv_qx[5561]: Startup successful
2025-01-29T16:58:42.927967+07:00 PPL404I-112 upsd-usbd[5563]: listening on 127.0.0.1 port 6490
2025-01-29T16:58:42.934666+07:00 PPL404I-112 upsd-usbd[5563]: Connected to UPS [pcmusb]: nutdrv_qx-pcmusb
2025-01-29T16:58:43.227964+07:00 PPL404I-112 nutdrv_qx[5561]: sock_connect: enabling asynchronous mode (auto)
2025-01-29T16:58:43.274554+07:00 PPL404I-112 root: [nut-server-usb]...Started
2025-01-29T16:58:43.276208+07:00 PPL404I-112 upsd-usbd[5564]: Startup successful
2025-01-29T16:58:45.296251+07:00 PPL404I-112 CLI-admin[4943]: CLI
2025-01-29T16:58:46.495327+07:00 PPL404I-112 CLI-admin[5400]: CLI
2025-01-29T16:58:54.471281+07:00 PPL404I-112 u_main.pl: Uupsd:Current load='0' vs Threshold='50'
2025-01-29T16:58:54.476052+07:00 PPL404I-112 u_main.pl: Uupsd:Current Battery_MinuteRemaining='2' vs Threshold='252'
2025-01-29T16:58:54.486509+07:00 PPL404I-112 u_main.pl: Uupsd:Current temperature='22.2' vs Threshold='50'
2025-01-29T16:58:54.632381+07:00 PPL404I-112 u_main.pl: Uupsd:Start-Service:AC-Status=0:UPS-Status=OL:Manual-Shutdown=0:Beeper=enabled
2025-01-29T16:58:54.647789+07:00 PPL404I-112 u_main.pl: Uupsd:UPS-Beeper=>Enable
2025-01-29T16:58:55.539950+07:00 PPL404I-112 hu_sys.pl: Uupsd:Syslog_Interval=300
2025-01-29T17:02:22.922171+07:00 PPL404I-112 CLI-admin[7813]: CLI/status/ups_cmd 127.0.0.1 1621 .1.3.6.1.2.1.33.1.1.27=1
2025-01-29T17:02:23.233300+07:00 PPL404I-112 u_main.pl: Uupsd:RECEIVED-Test-Battery-10s
2025-01-29T17:02:23.419863+07:00 PPL404I-112 nutdrv_qx[5561]: instcmd(test.battery.start.quick, [NULL])
2025-01-29T17:02:23.491675+07:00 PPL404I-112 nutdrv_qx[5561]: instcmd: SUCCEED
2025-01-29T17:02:26.163747+07:00 PPL404I-112 nutdrv_qx[5561]: battery_number: 3
2025-01-29T17:02:26.924224+07:00 PPL404I-112 nutdrv_qx[5561]: bypass_alarm: enabled
2025-01-29T17:02:26.924356+07:00 PPL404I-112 nutdrv_qx[5561]: battery_alarm: enabled
2025-01-29T17:02:26.924465+07:00 PPL404I-112 nutdrv_qx[5561]: bypass_when_off: enabled
2025-01-29T17:02:26.924748+07:00 PPL404I-112 nutdrv_qx[5561]: alarm_control: enabled
2025-01-29T17:02:26.924863+07:00 PPL404I-112 nutdrv_qx[5561]: converter_mode: disabled
2025-01-29T17:02:26.925295+07:00 PPL404I-112 nutdrv_qx[5561]: eco_mode: enabled
2025-01-29T17:02:26.925455+07:00 PPL404I-112 nutdrv_qx[5561]: bypass_forbidding: disabled
2025-01-29T17:02:26.925574+07:00 PPL404I-112 nutdrv_qx[5561]: site_fault_detection: disabled
2025-01-29T17:02:27.515590+07:00 PPL404I-112 nutdrv_qx[5561]: max_bypass_volt: 264
2025-01-29T17:02:27.517010+07:00 PPL404I-112 nutdrv_qx[5561]: min_bypass_volt: 170
2025-01-29T17:02:27.651641+07:00 PPL404I-112 nutdrv_qx[5561]: max_bypass_freq: 53.0
2025-01-29T17:02:27.653076+07:00 PPL404I-112 nutdrv_qx[5561]: min_bypass_freq: 47.0
2025-01-29T17:02:29.667908+07:00 PPL404I-112 u_main.pl: Uupsd:Current-BatteryMinuteRemaining=>Alert:2
2025-01-29T17:02:29.759342+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Test_Inprogress:Start=2025-01-29 17-02-29:End=:AC-Status=0:UPS-Status=OL CAL:Load=0:Battery-Charge=100:Battery-Volt=40.60:Battery-Capacity=99:Battery-Remaining-Time=2
2025-01-29T17:02:36.636909+07:00 PPL404I-112 u_main.pl: Uupsd:Test-Battery-10s=>Done:Start=2025-01-29 17-02-29:End=2025-01-29 17-02-36:AC-Status=0:UPS-Status=OL:Load=0:Battery-Charge=100:Battery-Volt=40.60:Battery-Capacity=99:Battery-Remaining-Time=2
2025-01-29T17:04:51.487783+07:00 PPL404I-112 CLI-admin[5400]: CLI/status/running_config | grep ups
2025-01-29T17:05:16.600257+07:00 PPL404I-112 CLI-admin[5400]: CLI/status/log0_trace -n 205
2025-01-29T17:05:48.131897+07:00 PPL404I-112 dropbear[24070]: Child connection from 192.168.99.55:64729
2025-01-29T17:05:50.926744+07:00 PPL404I-112 dropbear[24070]: Password auth succeeded for 'root' from 192.168.99.55:64729
2025-01-29T17:07:30.054760+07:00 PPL404I-112 CLI-admin[5400]: CLI/status/log0_trace -n 250
2025-01-29T17:08:00.718143+07:00 PPL404I-112 crond[2480]: USER root pid 26740 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-29T18:08:00.770033+07:00 PPL404I-112 crond[2480]: USER root pid 7558 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-29T19:08:00.819400+07:00 PPL404I-112 crond[2480]: USER root pid 20554 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-29T20:08:00.868970+07:00 PPL404I-112 crond[2480]: USER root pid 880 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-29T21:08:00.919810+07:00 PPL404I-112 crond[2480]: USER root pid 12389 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-29T22:08:00.969307+07:00 PPL404I-112 crond[2480]: USER root pid 23754 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-29T23:08:00.015795+07:00 PPL404I-112 crond[2480]: USER root pid 2184 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T00:08:00.061887+07:00 PPL404I-112 crond[2480]: USER root pid 12687 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T00:08:16.038500+07:00 PPL404I-112 ntpdate[12742]: step time server 202.28.116.236 offset +0.145794 sec
2025-01-30T01:08:00.253699+07:00 PPL404I-112 crond[2480]: USER root pid 23383 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T01:19:10.921187+07:00 PPL404I-112 upsd-usbd[5564]: Data for UPS [pcmusb] is stale - check driver
2025-01-30T01:19:12.378439+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-30T01:19:12.481222+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-30T01:19:12.634689+07:00 PPL404I-112 upsd-usbd[5564]: Can't connect to UPS [pcmusb] (nutdrv_qx-pcmusb): Connection refused
2025-01-30T01:19:15.405366+07:00 PPL404I-112 nutdrv_qx[5649]: device.serial: UPS reported a non-significant serial [0000000000000000]
2025-01-30T01:19:16.597616+07:00 PPL404I-112 nutdrv_qx[5649]: battery_number: 3
2025-01-30T01:19:16.599142+07:00 PPL404I-112 nutdrv_qx[5649]: battery_number, settable range: 1..9
2025-01-30T01:19:17.230718+07:00 PPL404I-112 nutdrv_qx[5649]: bypass_alarm: enabled
2025-01-30T01:19:17.232143+07:00 PPL404I-112 nutdrv_qx[5649]: battery_alarm: enabled
2025-01-30T01:19:17.233595+07:00 PPL404I-112 nutdrv_qx[5649]: bypass_when_off: enabled
2025-01-30T01:19:17.235349+07:00 PPL404I-112 nutdrv_qx[5649]: alarm_control: enabled
2025-01-30T01:19:17.236752+07:00 PPL404I-112 nutdrv_qx[5649]: converter_mode: disabled
2025-01-30T01:19:17.238724+07:00 PPL404I-112 nutdrv_qx[5649]: eco_mode: enabled
2025-01-30T01:19:17.240222+07:00 PPL404I-112 nutdrv_qx[5649]: bypass_forbidding: disabled
2025-01-30T01:19:17.240608+07:00 PPL404I-112 nutdrv_qx[5649]: site_fault_detection: disabled
2025-01-30T01:19:17.821395+07:00 PPL404I-112 nutdrv_qx[5649]: max_bypass_volt: 264
2025-01-30T01:19:17.822850+07:00 PPL404I-112 nutdrv_qx[5649]: max_bypass_volt, settable range: 230..264
2025-01-30T01:19:17.824401+07:00 PPL404I-112 nutdrv_qx[5649]: min_bypass_volt: 170
2025-01-30T01:19:17.825808+07:00 PPL404I-112 nutdrv_qx[5649]: min_bypass_volt, settable range: 170..220
2025-01-30T01:19:17.957421+07:00 PPL404I-112 nutdrv_qx[5649]: max_bypass_freq: 53.0
2025-01-30T01:19:17.957952+07:00 PPL404I-112 nutdrv_qx[5649]: max_bypass_freq, settable range: 51.0..60.0
2025-01-30T01:19:17.960475+07:00 PPL404I-112 nutdrv_qx[5649]: min_bypass_freq: 47.0
2025-01-30T01:19:17.960869+07:00 PPL404I-112 nutdrv_qx[5649]: min_bypass_freq, settable range: 40.0..49.0
2025-01-30T01:19:18.848576+07:00 PPL404I-112 nutdrv_qx[5687]: Startup successful
2025-01-30T01:19:20.643220+07:00 PPL404I-112 upsd-usbd[5564]: Connected to UPS [pcmusb]: nutdrv_qx-pcmusb
2025-01-30T01:19:20.643474+07:00 PPL404I-112 nutdrv_qx[5687]: sock_connect: enabling asynchronous mode (auto)
2025-01-30T01:30:13.583793+07:00 PPL404I-112 upsd-usbd[5564]: Data for UPS [pcmusb] is stale - check driver
2025-01-30T01:30:13.602950+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-30T01:30:13.633245+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-30T01:30:13.717263+07:00 PPL404I-112 upsd-usbd[5564]: Can't connect to UPS [pcmusb] (nutdrv_qx-pcmusb): Connection refused
2025-01-30T01:30:16.533400+07:00 PPL404I-112 nutdrv_qx[19405]: device.serial: UPS reported a non-significant serial [0000000000000000]
2025-01-30T01:30:17.150642+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN4 link up
2025-01-30T01:30:17.813613+07:00 PPL404I-112 nutdrv_qx[19405]: battery_number: 3
2025-01-30T01:30:17.814981+07:00 PPL404I-112 nutdrv_qx[19405]: battery_number, settable range: 1..9
2025-01-30T01:30:18.430711+07:00 PPL404I-112 nutdrv_qx[19405]: bypass_alarm: enabled
2025-01-30T01:30:18.432148+07:00 PPL404I-112 nutdrv_qx[19405]: battery_alarm: enabled
2025-01-30T01:30:18.433713+07:00 PPL404I-112 nutdrv_qx[19405]: bypass_when_off: enabled
2025-01-30T01:30:18.435483+07:00 PPL404I-112 nutdrv_qx[19405]: alarm_control: enabled
2025-01-30T01:30:18.437022+07:00 PPL404I-112 nutdrv_qx[19405]: converter_mode: disabled
2025-01-30T01:30:18.438942+07:00 PPL404I-112 nutdrv_qx[19405]: eco_mode: enabled
2025-01-30T01:30:18.439442+07:00 PPL404I-112 nutdrv_qx[19405]: bypass_forbidding: disabled
2025-01-30T01:30:18.441856+07:00 PPL404I-112 nutdrv_qx[19405]: site_fault_detection: disabled
2025-01-30T01:30:19.005439+07:00 PPL404I-112 nutdrv_qx[19405]: max_bypass_volt: 264
2025-01-30T01:30:19.006899+07:00 PPL404I-112 nutdrv_qx[19405]: max_bypass_volt, settable range: 230..264
2025-01-30T01:30:19.008357+07:00 PPL404I-112 nutdrv_qx[19405]: min_bypass_volt: 170
2025-01-30T01:30:19.009776+07:00 PPL404I-112 nutdrv_qx[19405]: min_bypass_volt, settable range: 170..220
2025-01-30T01:30:19.141486+07:00 PPL404I-112 nutdrv_qx[19405]: max_bypass_freq: 53.0
2025-01-30T01:30:19.141629+07:00 PPL404I-112 nutdrv_qx[19405]: max_bypass_freq, settable range: 51.0..60.0
2025-01-30T01:30:19.141803+07:00 PPL404I-112 nutdrv_qx[19405]: min_bypass_freq: 47.0
2025-01-30T01:30:19.141920+07:00 PPL404I-112 nutdrv_qx[19405]: min_bypass_freq, settable range: 40.0..49.0
2025-01-30T01:30:19.952580+07:00 PPL404I-112 nutdrv_qx[19446]: Startup successful
2025-01-30T01:30:21.725439+07:00 PPL404I-112 upsd-usbd[5564]: Connected to UPS [pcmusb]: nutdrv_qx-pcmusb
2025-01-30T01:30:21.725692+07:00 PPL404I-112 nutdrv_qx[19446]: sock_connect: enabling asynchronous mode (auto)
2025-01-30T01:54:18.753041+07:00 PPL404I-112 upsd-usbd[5564]: Data for UPS [pcmusb] is stale - check driver
2025-01-30T01:54:20.190499+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-30T01:54:20.252101+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-30T01:54:20.388372+07:00 PPL404I-112 upsd-usbd[5564]: Can't connect to UPS [pcmusb] (nutdrv_qx-pcmusb): Connection refused
2025-01-30T01:54:23.333384+07:00 PPL404I-112 nutdrv_qx[17716]: device.serial: UPS reported a non-significant serial [0000000000000000]
2025-01-30T01:54:24.509598+07:00 PPL404I-112 nutdrv_qx[17716]: battery_number: 3
2025-01-30T01:54:24.510943+07:00 PPL404I-112 nutdrv_qx[17716]: battery_number, settable range: 1..9
2025-01-30T01:54:25.278698+07:00 PPL404I-112 nutdrv_qx[17716]: bypass_alarm: enabled
2025-01-30T01:54:25.280109+07:00 PPL404I-112 nutdrv_qx[17716]: battery_alarm: enabled
2025-01-30T01:54:25.281461+07:00 PPL404I-112 nutdrv_qx[17716]: bypass_when_off: enabled
2025-01-30T01:54:25.283254+07:00 PPL404I-112 nutdrv_qx[17716]: alarm_control: enabled
2025-01-30T01:54:25.284652+07:00 PPL404I-112 nutdrv_qx[17716]: converter_mode: disabled
2025-01-30T01:54:25.286940+07:00 PPL404I-112 nutdrv_qx[17716]: eco_mode: enabled
2025-01-30T01:54:25.288525+07:00 PPL404I-112 nutdrv_qx[17716]: bypass_forbidding: disabled
2025-01-30T01:54:25.288897+07:00 PPL404I-112 nutdrv_qx[17716]: site_fault_detection: disabled
2025-01-30T01:54:25.709431+07:00 PPL404I-112 nutdrv_qx[17716]: max_bypass_volt: 264
2025-01-30T01:54:25.710861+07:00 PPL404I-112 nutdrv_qx[17716]: max_bypass_volt, settable range: 230..264
2025-01-30T01:54:25.712361+07:00 PPL404I-112 nutdrv_qx[17716]: min_bypass_volt: 170
2025-01-30T01:54:25.713857+07:00 PPL404I-112 nutdrv_qx[17716]: min_bypass_volt, settable range: 170..220
2025-01-30T01:54:25.989422+07:00 PPL404I-112 nutdrv_qx[17716]: max_bypass_freq: 53.0
2025-01-30T01:54:25.989803+07:00 PPL404I-112 nutdrv_qx[17716]: max_bypass_freq, settable range: 51.0..60.0
2025-01-30T01:54:25.990284+07:00 PPL404I-112 nutdrv_qx[17716]: min_bypass_freq: 47.0
2025-01-30T01:54:25.993525+07:00 PPL404I-112 nutdrv_qx[17716]: min_bypass_freq, settable range: 40.0..49.0
2025-01-30T01:54:26.700544+07:00 PPL404I-112 nutdrv_qx[17754]: Startup successful
2025-01-30T01:54:28.395427+07:00 PPL404I-112 upsd-usbd[5564]: Connected to UPS [pcmusb]: nutdrv_qx-pcmusb
2025-01-30T01:54:28.397038+07:00 PPL404I-112 nutdrv_qx[17754]: sock_connect: enabling asynchronous mode (auto)
2025-01-30T02:01:00.297648+07:00 PPL404I-112 crond[2480]: USER root pid 25919 cmd run-parts /opt/pp/CLI/sbin/etc/cron.daily
2025-01-30T02:05:03.093080+07:00 PPL404I-112 : [origin software="rsyslogd" swVersion="8.2110.0" x-pid="2343" x-info="https://www.rsyslog.com"] rsyslogd was HUPed
2025-01-30T02:08:00.304456+07:00 PPL404I-112 crond[2480]: USER root pid 2283 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T03:08:00.350284+07:00 PPL404I-112 crond[2480]: USER root pid 13312 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T04:08:00.395500+07:00 PPL404I-112 crond[2480]: USER root pid 24215 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T04:43:41.028658+07:00 PPL404I-112 upsd-usbd[5564]: Data for UPS [pcmusb] is stale - check driver
2025-01-30T04:43:41.075539+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-30T04:43:41.144944+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-30T04:43:41.283605+07:00 PPL404I-112 upsd-usbd[5564]: Can't connect to UPS [pcmusb] (nutdrv_qx-pcmusb): Connection refused
2025-01-30T04:43:44.277374+07:00 PPL404I-112 nutdrv_qx[4699]: device.serial: UPS reported a non-significant serial [0000000000000000]
2025-01-30T04:43:45.453611+07:00 PPL404I-112 nutdrv_qx[4699]: battery_number: 3
2025-01-30T04:43:45.454973+07:00 PPL404I-112 nutdrv_qx[4699]: battery_number, settable range: 1..9
2025-01-30T04:43:46.214688+07:00 PPL404I-112 nutdrv_qx[4699]: bypass_alarm: enabled
2025-01-30T04:43:46.216116+07:00 PPL404I-112 nutdrv_qx[4699]: battery_alarm: enabled
2025-01-30T04:43:46.217471+07:00 PPL404I-112 nutdrv_qx[4699]: bypass_when_off: enabled
2025-01-30T04:43:46.219211+07:00 PPL404I-112 nutdrv_qx[4699]: alarm_control: enabled
2025-01-30T04:43:46.220618+07:00 PPL404I-112 nutdrv_qx[4699]: converter_mode: disabled
2025-01-30T04:43:46.222514+07:00 PPL404I-112 nutdrv_qx[4699]: eco_mode: enabled
2025-01-30T04:43:46.224090+07:00 PPL404I-112 nutdrv_qx[4699]: bypass_forbidding: disabled
2025-01-30T04:43:46.224472+07:00 PPL404I-112 nutdrv_qx[4699]: site_fault_detection: disabled
2025-01-30T04:43:46.773409+07:00 PPL404I-112 nutdrv_qx[4699]: max_bypass_volt: 264
2025-01-30T04:43:46.773587+07:00 PPL404I-112 nutdrv_qx[4699]: max_bypass_volt, settable range: 230..264
2025-01-30T04:43:46.773722+07:00 PPL404I-112 nutdrv_qx[4699]: min_bypass_volt: 170
2025-01-30T04:43:46.773894+07:00 PPL404I-112 nutdrv_qx[4699]: min_bypass_volt, settable range: 170..220
2025-01-30T04:43:46.909420+07:00 PPL404I-112 nutdrv_qx[4699]: max_bypass_freq: 53.0
2025-01-30T04:43:46.909821+07:00 PPL404I-112 nutdrv_qx[4699]: max_bypass_freq, settable range: 51.0..60.0
2025-01-30T04:43:46.910316+07:00 PPL404I-112 nutdrv_qx[4699]: min_bypass_freq: 47.0
2025-01-30T04:43:46.910654+07:00 PPL404I-112 nutdrv_qx[4699]: min_bypass_freq, settable range: 40.0..49.0
2025-01-30T04:43:47.628649+07:00 PPL404I-112 nutdrv_qx[4748]: Startup successful
2025-01-30T04:43:49.292661+07:00 PPL404I-112 upsd-usbd[5564]: Connected to UPS [pcmusb]: nutdrv_qx-pcmusb
2025-01-30T04:43:49.292955+07:00 PPL404I-112 nutdrv_qx[4748]: sock_connect: enabling asynchronous mode (auto)
2025-01-30T05:08:00.441559+07:00 PPL404I-112 crond[2480]: USER root pid 3063 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T06:08:00.491364+07:00 PPL404I-112 crond[2480]: USER root pid 14514 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T07:08:00.536049+07:00 PPL404I-112 crond[2480]: USER root pid 26753 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T08:08:00.584456+07:00 PPL404I-112 crond[2480]: USER root pid 6113 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
2025-01-30T08:43:17.965297+07:00 PPL404I-112 upsd-usbd[5564]: Data for UPS [pcmusb] is stale - check driver
2025-01-30T08:43:19.359901+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-30T08:43:19.422231+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-30T08:43:19.564271+07:00 PPL404I-112 upsd-usbd[5564]: Can't connect to UPS [pcmusb] (nutdrv_qx-pcmusb): Connection refused
2025-01-30T08:43:22.557374+07:00 PPL404I-112 nutdrv_qx[19246]: device.serial: UPS reported a non-significant serial [0000000000000000]
2025-01-30T08:43:23.765612+07:00 PPL404I-112 nutdrv_qx[19246]: battery_number: 3
2025-01-30T08:43:23.766978+07:00 PPL404I-112 nutdrv_qx[19246]: battery_number, settable range: 1..9
2025-01-30T08:43:24.543252+07:00 PPL404I-112 nutdrv_qx[19246]: bypass_alarm: enabled
2025-01-30T08:43:24.544674+07:00 PPL404I-112 nutdrv_qx[19246]: battery_alarm: enabled
2025-01-30T08:43:24.546035+07:00 PPL404I-112 nutdrv_qx[19246]: bypass_when_off: enabled
2025-01-30T08:43:24.547799+07:00 PPL404I-112 nutdrv_qx[19246]: alarm_control: enabled
2025-01-30T08:43:24.549196+07:00 PPL404I-112 nutdrv_qx[19246]: converter_mode: disabled
2025-01-30T08:43:24.551103+07:00 PPL404I-112 nutdrv_qx[19246]: eco_mode: enabled
2025-01-30T08:43:24.552596+07:00 PPL404I-112 nutdrv_qx[19246]: bypass_forbidding: disabled
2025-01-30T08:43:24.553053+07:00 PPL404I-112 nutdrv_qx[19246]: site_fault_detection: disabled
2025-01-30T08:43:25.125411+07:00 PPL404I-112 nutdrv_qx[19246]: max_bypass_volt: 264
2025-01-30T08:43:25.126868+07:00 PPL404I-112 nutdrv_qx[19246]: max_bypass_volt, settable range: 230..264
2025-01-30T08:43:25.128329+07:00 PPL404I-112 nutdrv_qx[19246]: min_bypass_volt: 170
2025-01-30T08:43:25.129740+07:00 PPL404I-112 nutdrv_qx[19246]: min_bypass_volt, settable range: 170..220
2025-01-30T08:43:25.285444+07:00 PPL404I-112 nutdrv_qx[19246]: max_bypass_freq: 53.0
2025-01-30T08:43:25.286864+07:00 PPL404I-112 nutdrv_qx[19246]: max_bypass_freq, settable range: 51.0..60.0
2025-01-30T08:43:25.287303+07:00 PPL404I-112 nutdrv_qx[19246]: min_bypass_freq: 47.0
2025-01-30T08:43:25.287744+07:00 PPL404I-112 nutdrv_qx[19246]: min_bypass_freq, settable range: 40.0..49.0
2025-01-30T08:43:26.013652+07:00 PPL404I-112 nutdrv_qx[19316]: Startup successful
2025-01-30T08:43:27.572294+07:00 PPL404I-112 upsd-usbd[5564]: Connected to UPS [pcmusb]: nutdrv_qx-pcmusb
2025-01-30T08:43:27.572522+07:00 PPL404I-112 nutdrv_qx[19316]: sock_connect: enabling asynchronous mode (auto)
2025-01-30T08:43:58.363133+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-30T08:50:16.427930+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-30T08:56:57.509560+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-30T08:57:00.918761+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-30T08:57:04.340224+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-30T08:57:07.776708+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-30T08:57:11.240717+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-30T08:57:48.760184+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link down
2025-01-30T08:57:52.214808+07:00 PPL404I-112 root: rt3050-esw 10110000.esw: link changed: LAN2 link up
2025-01-30T09:00:21.250190+07:00 PPL404I-112 upsd-usbd[5564]: Data for UPS [pcmusb] is stale - check driver
2025-01-30T09:00:21.302316+07:00 PPL404I-112 u_main.pl: Uupsd: cannot get data from ups retry:1/3
2025-01-30T09:00:21.372934+07:00 PPL404I-112 u_main.pl: Uupsd: Defined UPS's USBVIDPID has been found:restore connection
2025-01-30T09:00:21.515464+07:00 PPL404I-112 upsd-usbd[5564]: Can't connect to UPS [pcmusb] (nutdrv_qx-pcmusb): Connection refused
2025-01-30T09:00:24.213375+07:00 PPL404I-112 nutdrv_qx[8257]: device.serial: UPS reported a non-significant serial [0000000000000000]
2025-01-30T09:00:25.373642+07:00 PPL404I-112 nutdrv_qx[8257]: battery_number: 3
2025-01-30T09:00:25.374988+07:00 PPL404I-112 nutdrv_qx[8257]: battery_number, settable range: 1..9
2025-01-30T09:00:25.998721+07:00 PPL404I-112 nutdrv_qx[8257]: bypass_alarm: enabled
2025-01-30T09:00:26.000129+07:00 PPL404I-112 nutdrv_qx[8257]: battery_alarm: enabled
2025-01-30T09:00:26.001464+07:00 PPL404I-112 nutdrv_qx[8257]: bypass_when_off: enabled
2025-01-30T09:00:26.003245+07:00 PPL404I-112 nutdrv_qx[8257]: alarm_control: enabled
2025-01-30T09:00:26.004640+07:00 PPL404I-112 nutdrv_qx[8257]: converter_mode: disabled
2025-01-30T09:00:26.006533+07:00 PPL404I-112 nutdrv_qx[8257]: eco_mode: enabled
2025-01-30T09:00:26.008002+07:00 PPL404I-112 nutdrv_qx[8257]: bypass_forbidding: disabled
2025-01-30T09:00:26.008371+07:00 PPL404I-112 nutdrv_qx[8257]: site_fault_detection: disabled
2025-01-30T09:00:26.549411+07:00 PPL404I-112 nutdrv_qx[8257]: max_bypass_volt: 264
2025-01-30T09:00:26.550831+07:00 PPL404I-112 nutdrv_qx[8257]: max_bypass_volt, settable range: 230..264
2025-01-30T09:00:26.552269+07:00 PPL404I-112 nutdrv_qx[8257]: min_bypass_volt: 170
2025-01-30T09:00:26.553747+07:00 PPL404I-112 nutdrv_qx[8257]: min_bypass_volt, settable range: 170..220
2025-01-30T09:00:26.685511+07:00 PPL404I-112 nutdrv_qx[8257]: max_bypass_freq: 53.0
2025-01-30T09:00:26.685894+07:00 PPL404I-112 nutdrv_qx[8257]: max_bypass_freq, settable range: 51.0..60.0
2025-01-30T09:00:26.686376+07:00 PPL404I-112 nutdrv_qx[8257]: min_bypass_freq: 47.0
2025-01-30T09:00:26.686700+07:00 PPL404I-112 nutdrv_qx[8257]: min_bypass_freq, settable range: 40.0..49.0
2025-01-30T09:00:27.513701+07:00 PPL404I-112 nutdrv_qx[8295]: Startup successful
2025-01-30T09:00:27.522277+07:00 PPL404I-112 upsd-usbd[5564]: Connected to UPS [pcmusb]: nutdrv_qx-pcmusb
2025-01-30T09:00:27.829782+07:00 PPL404I-112 nutdrv_qx[8295]: sock_connect: enabling asynchronous mode (auto)
2025-01-30T09:08:00.631083+07:00 PPL404I-112 crond[2480]: USER root pid 18057 cmd run-parts /opt/pp/CLI/sbin/etc/cron.hourly
More information about the Nut-upsdev