<div dir="ltr"><div>No, the Battery Temp does not change. It is always 25C.<br></div><div>I don't know why the ups.delay.start is that high.  Is that user configurable?<br></div><div>Yes, I have tested the automatic shutdown.  Works well.  <br></div><div>Yes, the instant commands work, at least those I feel comfortable testing.  Battery test work fine.<br></div><div>I have not enable the write to variables.  Did not know that it might be necessary.<br></div><div dir="ltr"><br>John Hart<br><br><br>----- Forwarded Message -----<br>  <font face="Arial" size="2"> <b><span style="font-weight:bold">From:</span></b> Charles Lepple <<a href="mailto:clepple@gmail.com" target="_blank">clepple@gmail.com</a>><br> <b><span style="font-weight:bold">To:</span></b> john hart <<a href="mailto:jsamcr@yahoo.com" target="_blank">jsamcr@yahoo.com</a>> <br><b><span style="font-weight:bold">Cc:</span></b> "<a href="mailto:nut-upsdev@lists.alioth.debian.org" target="_blank">nut-upsdev@lists.alioth.debian.org</a>" <<a href="mailto:nut-upsdev@lists.alioth.debian.org" target="_blank">nut-upsdev@lists.alioth.debian.org</a>> <br> <b><span style="font-weight:bold">Sent:</span></b> Sunday, September 20, 2015 2:52 PM<br> <b><span style="font-weight:bold">Subject:</span></b> Re: [Nut-upsdev] [HCL] Asium P700<br> </font> </div> <br>On Sep 19, 2015, at 10:08 AM, john hart <<a shape="rect" href="mailto:jsamcr@yahoo.com" target="_blank">jsamcr@yahoo.com</a>> wrote:<br clear="none">> <br clear="none">>
 I have been using the Asium P700 for about 4 months, running Debian 
Wheezy 7.9,  and would like to submit the UPS for inclusion in your list
 of supported devices.  <br clear="none">> ASIUM P700 (650VA/360W)<br clear="none">> <<a shape="rect" href="http://www.asiumpower.com/Asium-ASIUM-P700-650VA-360W/dp/B009SMEQ10" target="_blank">http://www.asiumpower.com/Asium-ASIUM-P700-650VA-360W/dp/B009SMEQ10</a>><br clear="none">[...]<br clear="none">> Not sure what the procedure might be but I am sending the dump from upsc :<br clear="none">> <br clear="none">> battery.charge: 100<br clear="none">> battery.voltage: 13.50<br clear="none">> battery.voltage.high: 13.00<br clear="none">> battery.voltage.low: 10.40<br clear="none">> battery.voltage.nominal: 12.0<br clear="none">> device.type: ups<br clear="none">> <a href="http://driver.name" target="_blank">driver.name</a>: blazer_usb<br clear="none">> driver.parameter.offdelay: 30<br clear="none">> driver.parameter.ondelay: 40<br clear="none">> driver.parameter.pollinterval: 2<br clear="none">> driver.parameter.port: auto<br clear="none">> driver.parameter.vendorid: 0665<br clear="none">> driver.version: 2.6.4<br clear="none">> driver.version.internal: 0.08<br clear="none">> input.current.nominal: 5.0<br clear="none">> input.frequency: 60.4<br clear="none">> input.frequency.nominal: 60<br clear="none">> input.voltage: 117.0<br clear="none">> input.voltage.fault: 117.0<br clear="none">> input.voltage.nominal: 120<br clear="none">> output.voltage: 117.0<br clear="none">> ups.beeper.status: enabled<br clear="none">> ups.delay.shutdown: 30<br clear="none">> ups.delay.start: 2400<br clear="none">> ups.load: 25<br clear="none">> ups.productid: 5161<br clear="none">> ups.status: OL<br clear="none">> ups.temperature: 25.0<br clear="none">> ups.type: offline / line interactive<br clear="none">> ups.vendorid: 0665<br clear="none">> <br clear="none">>
 I know that not all UPS devices can be tested and reviewed by your 
team, and not all devices can be included in the list.  Just thought I 
would give it a shot.<br clear="none"><br clear="none">Thanks for the 
info. The Hardware Compatibility List (HCL) and Device Dump Library 
(DDL) are both filled with user-submitted information, so we rely on 
reports like this.<br clear="none"><br clear="none">Before we add this, 
do all of the values from `upsc` look correct to you? In particular, 
does `ups.temperature` ever change from 25.0? Also, the value for 
ups.delay.start (2400) looks high for the requested value (40). Have you
 done any shutdown testing with this UPS? Do the read/write variables 
and instant commands (if any) work properly?<br clear="none"><br clear="none">Reference: <a shape="rect" href="http://www.networkupstools.org/stable-hcl.html#footnotes" target="_blank">http://www.networkupstools.org/stable-hcl.html#footnotes </a>and <a shape="rect" href="http://www.networkupstools.org/ddl/#report-a-bad-value" target="_blank">http://www.networkupstools.org/ddl/#report-a-bad-value</a><br clear="none"><br clear="none">Note
 that in later versions of NUT, the driver for your UPS will be 
nutdrv_qx (a superset of several Q*-protocol drivers, including 
blazer_usb).<br clear="none"><br clear="none">Another thing: we recently
 discovered that some Yahoo anti-spam measures result in mass 
unsubscription of non-Yahoo email users of these lists. Please consider 
submitting future information from a non-Yahoo email address, or create 
an issue on the NUT Github project: <a shape="rect" href="https://github.com/networkupstools/nut/issues" target="_blank">https://github.com/networkupstools/nut/issues</a><div class=""><div id=":69" class="" tabindex="0"><img class="" src="https://ssl.gstatic.com/ui/v1/icons/mail/images/cleardot.gif"></div></div></div>