[Nut-upsuser] HP/Compaq Rackmount UPS Support? [SOLVED]
Denny Fox
dennyf at microtimeinc.com
Tue Nov 15 15:26:25 UTC 2005
Hi Kjell,
Downloaded the Development tag from CVS, and now it's working! Great!
[root at encoda02 root]# /usr/local/ups/bin/upsc hpr5500 at localhost
ambient.temperature: 26.5
battery.charge: 99.3
battery.runtime: 1153
battery.voltage: 256.8
driver.name: bcmxcp
driver.parameter.baud_rate: 19200
driver.parameter.port: /dev/ttyS0
driver.version: 2.1.0
driver.version.internal: 0.10
input.frequency: 59.8
input.voltage: 199.7
output.current: 11.5
output.frequency: 60.0
output.voltage: 197.0
ups.firmware: 01.03
ups.load: 45.6
ups.model: R5500 XR 5000VA
ups.power.nominal: 5000
ups.serial: Y1K6MHZ12H
ups.status: OL
ups.voltage.nominal: 204
Thanks for all your help!
Now onward to the rest of the configuration...
Denny
-----Original Message-----
From: nut-upsuser-bounces at lists.alioth.debian.org
[mailto:nut-upsuser-bounces at lists.alioth.debian.org] On Behalf Of Kjell
Claesson
Sent: Sunday, November 13, 2005 3:03 PM
To: Denny Fox
Cc: nut-upsuser at lists.alioth.debian.org
Subject: RE: [Nut-upsuser] HP/Compaq Rackmount UPS Support?
Hi Denny.
You have to use the code from the cvs. You can use
the Development or Testing tag.
cvs -d:pserver:anonymous at cvs.alioth.debian.org:/cvsroot/nut login
[Press ENTER when prompted for a password]
cvs -z3 -d:pserver:anonymous at cvs.alioth.debian.org:/cvsroot/nut co -r
Development nut
If you want the code for next release change Development to Testing
in the last line.
The driver you use is the version 0.08 and it does not contain the
fix for the baud-hunting and the param baud_rate.
I send you a mail of list for more info.
Regards
Kjell
More information about the Nut-upsuser
mailing list