> Thanks for your reply. I tried to update nut to 2.0.2, but upsc print
> out the same informations:
>
> # upsc Smart-UPS at localhost
> driver.name: apcsmart
> driver.version: 2.0.2
> driver.version.internal: 1.99.7
> ups.mfr: APC
> ups.status: OL
Two things you might check:
1) What cable are you using?
2) What does the driver mention upon startup?
Note that the info you currently get from upsc, may be all that you will
ever see. Older APC models will not support more than that. I can't tell
from the information you provided so far if your UPS is among these
models.
Regards,
Arjen