Criggie wrote:
>
>
> Charles Lepple wrote:
> > On 5/1/06, Shlomo Dubrowin <shlomo at dubrowin.org> wrote:
> >> Does anyone know why, or how to check why, it is showing OB, when it
> >> should be showing OL?
> >
> > I am not familiar with the various genericups types, but you can use
> > statserial to show the status of the various serial port lines.
>
>
> Hi Charles - what does it suggest if statserial shows no change when the
> UPS switches to battery?
>
> Serial plugged in.... statserial /dev/ttyS0 -d
> 16742
>
> Unplugged returns 16390 Which shows I have the right serial port because
> unplugging the serial cable shows changes.
This could mean several things.
* perhaps your UPS does not report "on battery". Does it report "low
battery"? The latter is all that is technically needed to shut down
the computer.
* perhaps your UPS or cable is broken, or partially broken
* perhaps your UPS is not contact-closure. Maybe it expects proper
serial port communications, instead of setting individual pins?
In this case, you should use one of the serial drivers.
-- Peter