>> While plugged into the wall:
>> battery.charge: 100.0
>> battery.runtime: 64:41
>> driver.name: cpsups
>> driver.parameter.port: /dev/ttyS2
>> driver.version: 2.0.4
>> driver.version.internal: .04
>> input.frequency: 60
>> input.voltage: 122
>> output.voltage: 122
>> ups.load: 9
>> ups.mfr: CyberPower
>> ups.model: CPS1200VA 1.500
>> ups.power.nominal: 1200
>> ups.runtime: 70
>> ups.status: OL
>> ups.temperature: 28
>>
>> After power removed for ~5 minutes:
>> battery.charge: 65.0
>> battery.runtime: 46:29
>> driver.name: cpsups
>> driver.parameter.port: /dev/ttyS2
>> driver.version: 2.0.4
>> driver.version.internal: .04
>> input.frequency: 0
>> input.voltage: 0
>> output.voltage: 0
>> ups.load: 0
>> ups.mfr: CyberPower
>> ups.model: CPS1200VA 1.500
>> ups.power.nominal: 1200
>> ups.runtime: 70
>> ups.status: OB
>> ups.temperature: 42
> 
> Let me just clarify: was the lamp already off when you took this
> second reading? -- Peter

Yes.  When I took the second reading, the UPS had just shut off and the 
lamp was off.