[Nut-upsuser] tripp lite SMART2200RMXL2U -- empty ups.status
Charles Lepple
clepple at gmail.com
Mon Sep 18 17:00:48 UTC 2006
On 9/18/06, Jeff Knerr <knerr at cs.swarthmore.edu> wrote:
> On Mon, Sep 18, 2006 at 11:48:32AM -0400, Charles Lepple wrote:
> >> >Attached to Tripp Lite SMART2200RMXL2U
> >> >Unknown value for s[2]: 0x34
> >>
> >> That's the culprit.
> >>
> >> I have not had much testing time with the RM2U-style UPSes, so I was
> >> not able to map all of the status values to NUT ups.status lines.
> >>
> >> Would you have time to do some off-line testing with this UPS, or is
> >> it powering something mission-critical right now?
>
> Hi Charles. I'd love to help test this. It's just powering a monitor so
> far. What's the first step?
You might more of a load for this device - maybe an extra monitor or two.
Try the following test:
( while true; do
date
upsc tripplite at localhost |grep debug
sleep 30
done ) | tee logfile
and then unplug the UPS line power.
Note the times when the inputs or UPS front panel change state (power
pulled; low battery; load off; power re-applied, etc.)
--
- Charles Lepple