[Nut-upsuser] tripp lite SMART2200RMXL2U -- empty ups.status
(second test)
Charles Lepple
clepple at gmail.com
Fri Sep 22 16:22:20 UTC 2006
On 9/22/06, Jeff Knerr <knerr at cs.swarthmore.edu> wrote:
> On Mon, Sep 18, 2006 at 11:56:09PM -0400, Charles Lepple wrote:
> >> I added some more code to SVN trunk (rev 527). Let me know how it
> >> goes. You might not want to limit it to just ups.debug, as I tried to
> >> apply some old protocol notes to decoding the values that come back.
>
> Thanks, Charles. I ran another test using rev 527. It looks better (the
> status line now says OL), but I'm not sure about a few things. I put
> the debug output here: http://www.cs.swarthmore.edu/~knerr/ups.html
> Let me know if that's not the best format for you.
>
> Here are my observations from the debug data:
>
> - battery.test.status always says "Battery state unknown" (not sure if
> that's important or not)
Have you ever done a battery test on that unit? I think it's just
saying that there are no test results to report. I can change that
wording.
There are some "instant commands" defined for this UPS, including one
to start a battery test.
> - ups.status says OL even after I pull the plug. Should it say "on
> battery" or something?
Yes, it should.
Note that "ups.debug.S" stays the same when on battery - this is
different from the OMNIVS series.
> - ups.temperature looks ok until I pull the plug, then goes to -20.6
> (but I doubt I'll use this for anything)
Interesting. I might be off by a character on parsing that field.
> - once the battery light goes red, the ups.status changes to OL LB, so
> that seems to work!
>
> Let me know if you think there's more to fix here. And thanks again for
> helping with this.
No problem. I'll be out all weekend, but maybe I can play with the
code again next week. Thanks again for the feedback.
--
- Charles Lepple