[Nut-upsuser] Outlet switching on the MGE Pulsar 1500 using usbhid-ups on FreeBSD
Arjen de Korte
nut+users at de-korte.org
Mon Oct 29 07:39:31 UTC 2007
[...]
> I managed to set the low battery level OK though (and then shut my PC
> down by mistake :) so I can actually set values.. Is it just that
> usbhid-ups doesn't support outlet switching? (yet hopefully :)
Outlet switching is supported, only you need to use 'upscmd' for that (see
the man page). The output of
upscmd -l <upsname>
will tell you which commands are supported for your UPS. In newer NUT
versions, even a little description will be displayed (we forgot that when
these commands were added), but you can probably do without.
Best regards, Arjen
--